Hello,
I am building a new garage. It will be 230' from my main panel (200A) at my house. I am going to run 2/0 Aluminum Direct Bury Cable to the new panel (125A panel).
Subpanel at Garage Question #1: Attached is a pic of the new box (w/o wiring) at the garage. The breaker installed is going to be used as the main breaker in the panel - electrician at local supply store said this is acceptable. Can someone verify this is acceptable as far as the incoming 'main' breaker?
Subpanel Question #2: I studied voltage drop & my calcs matched calculator on Southwire website. i.e. 230', 2/0 alum direct bury, 120V is good for 60 amps at 3.75% voltage drop. My loads will be a small mig welder (220), small compressor, lights. Should I be using a 100A breaker or a smaller breaker? (There will obviously be a main breaker at the house). The 2/0 just fits in the 100A breaker. (I will be providing shading for the direct bury cables)
Attachment of Neutral Question #3: Attached is a pic of my neutral lugs on my main. Any ideas as to how to expand to accept the 2/0 aluminum to my neutral?
View media item 32163
Attachment of Ground to main panel Question #4: For my ground, in my main, is a bare copper wire that is attached to the neutral at the main. Attached is a pic of the recommended direct bury alum. ground cable. As can be seen in the main panel pic, the top bare copper is the ground. Can I simply insert the new alum ground with the copper ground and tighten the terminal? Or should I simply swage it to the bare copper ground? Or should I attach to a new terminal as mentioned in #3 above? It seems odd that I am attaching a new ground for subpanel to the neutral at the main, but ground is ground.
Thanks so much...this forum is great. I'm new to home wiring but work on wind turbines...much different animals...
I am building a new garage. It will be 230' from my main panel (200A) at my house. I am going to run 2/0 Aluminum Direct Bury Cable to the new panel (125A panel).
Subpanel at Garage Question #1: Attached is a pic of the new box (w/o wiring) at the garage. The breaker installed is going to be used as the main breaker in the panel - electrician at local supply store said this is acceptable. Can someone verify this is acceptable as far as the incoming 'main' breaker?
Subpanel Question #2: I studied voltage drop & my calcs matched calculator on Southwire website. i.e. 230', 2/0 alum direct bury, 120V is good for 60 amps at 3.75% voltage drop. My loads will be a small mig welder (220), small compressor, lights. Should I be using a 100A breaker or a smaller breaker? (There will obviously be a main breaker at the house). The 2/0 just fits in the 100A breaker. (I will be providing shading for the direct bury cables)
Attachment of Neutral Question #3: Attached is a pic of my neutral lugs on my main. Any ideas as to how to expand to accept the 2/0 aluminum to my neutral?
View media item 32163
Attachment of Ground to main panel Question #4: For my ground, in my main, is a bare copper wire that is attached to the neutral at the main. Attached is a pic of the recommended direct bury alum. ground cable. As can be seen in the main panel pic, the top bare copper is the ground. Can I simply insert the new alum ground with the copper ground and tighten the terminal? Or should I simply swage it to the bare copper ground? Or should I attach to a new terminal as mentioned in #3 above? It seems odd that I am attaching a new ground for subpanel to the neutral at the main, but ground is ground.
Thanks so much...this forum is great. I'm new to home wiring but work on wind turbines...much different animals...