Should I use 6/2 or 6/3 wire?
T tom-ky Well-known member Joined Mar 11, 2017 Messages 512 Location Morgantown, Ky Apr 22, 2017 #1 Should I use 6/2 or 6/3 wire?
C CNGsaves Well-known member Joined Sep 26, 2012 Messages 13,233 Location KS and OK Apr 22, 2017 #2 Too little information . . . . . . . a) what welder ?? . . . . b) distance from subpanel ??
OP T tom-ky Well-known member Joined Mar 11, 2017 Messages 512 Location Morgantown, Ky Apr 22, 2017 #3 CNGsaves said: Too little information . . . . . . . a) what welder ?? . . . . b) distance from subpanel ?? Click to expand... Welder says 50 amp Lincoln 225. About 40 feet from breaker box.
CNGsaves said: Too little information . . . . . . . a) what welder ?? . . . . b) distance from subpanel ?? Click to expand... Welder says 50 amp Lincoln 225. About 40 feet from breaker box.
S sberry Banned Joined Jun 18, 2005 Messages 35,747 Location Brethren, Michigan Apr 22, 2017 #4 It requires 2 conductor plus ground. That machine needs 12 or better if single circuit in pipe, 10 cable or better. 50A breaker.
It requires 2 conductor plus ground. That machine needs 12 or better if single circuit in pipe, 10 cable or better. 50A breaker.
W wyliesdiesels Well-known member Joined Aug 14, 2012 Messages 20,021 Location Modesto, CA Apr 22, 2017 #5 Unless u plan on using the wire for something else down the road that needs a neutral, all u need is NM-b 6/2...
Unless u plan on using the wire for something else down the road that needs a neutral, all u need is NM-b 6/2...