Look at the name plate on the back of unit sometimes near the power cord.
It should list:
1 name of manufacturer
2 frequency
3 number of phases
4 primary voltage
5 I max and I eff or rated primary current
6 max. open- circuit voltage
7 rated secondary current
8 basis of rating, such as duty cycle
The ampacity of supply conductors shall not be smaller than I eff
The over current device (breaker/fuse) shall be rated at not more than 200% of I max
if I max is not given use rated primary current
Above taken from NEC Art. 630
Wire size: type thwn, thhn, thw ,rhw, use, xhhw
Not more than three current carrying conductors in raceway,cable or directly buried in earth. Ground wire is not considered a current carrying cond. Neutral wire is.
#14awg copper 15 amp max
#12 " 20 "
#10 " 30 "
#8 " 50 "
#6 " 65 "
#4 " 85 "
#2 " 115 "