would this run on 220 or 110?

No. You'd have to totally redesign the control panel to change it from three phase to single phase, plus it would draw too many amps at the lower voltage.

As an aside, many years ago I interviewed for a job at BGK - they're in Blaine, MN on the north side of the Minneapolis-St. Paul metro area.
 
To avoid these ads, REGISTER NOW!

Steve in Mi

Well-known member
Joined
Mar 13, 2007
Messages
1,042
Location
Mid Michigan
The device in the auction is an infared heater, not a motor.

The VFD can be looked at as a 3ph power supply. Just as you can plug in a motor or radio or welder of the single phase variety into the appropriate voltage single phase power supply the VFD isn't limited to 3ph motor operation.
 

StaggeringGoat

Well-known member
Joined
Jul 1, 2011
Messages
758
Location
Oregon
*IF* you could run that thing on 240 volts (no such thing as 110 or 220) it would draw more than 145 amps.
 

lametec

Well-known member
Joined
May 5, 2008
Messages
2,099
Location
Michigan
That's 145A on 3-phase 240V. If you ran it off a VFD on single phase it would draw over 250A.
 