New panel is installed. Just waiting on GFCI breakers ordered online to have GFCI for everything that needs it, should have them installed next weekend. I thought there were ground rods at the garage, however there are none.
There is a generator at the garage that is wired through conduit back to a transfer switch in the house at the main panel. This generator has a ground rod. Can I, and should I, use this ground rod for the garage and drive an additional ground rod 6' away to have two ground rods for the garage subpanel? Or should I drive two new ground rods for the garage subpanel (new ground rods would end up both within 6' of the existing rod for the generator)? 6 gauge solid copper from ground rods to panel?
In the 3/4" conduit to the shed are 3x 10ga copper stranded and 2x 12ga copper stranded. Looking at wire, at the end of the day cost is what it is but trying to optimize. I'm looking at a 60' run estimated through conduit and to where I'd place the panel in the shed, 65' to be safe if buying wire by the foot. With my 3/4 conduit I can put 4x 6 gauge conductors in it, so I may as well go with that if I'm spending the time to do it.
It would be nice to have different colors, but I can get a spool of 500' for less than it would cost for 195' by the foot (65' each to be safe), let alone 260' (4x 65' lengths). Is it still acceptable to tape the neutral to identify it? If so I'll just get a 500' spool of 6ga THHN and use that for the run from garage subpanel to shed subpanel.
Ground conductor sizing. As per table 250.122, 10 gauge copper is good for 60 amps. Am I looking at the right table for ground conductor sizing for a subpanel? Is the existing 10ga THHN ground from garage to shed acceptable as a ground conductor with 6 gauge feeding the panel? If not I will run a new 6ga THHN ground.
Load in the shed is a 3HP compressor, refrigerator, a couple lights, and outlets. Occasional tool use only one at a time (parts washer, sand blaster, saw, drill). Might eventually go to a 5 HP 2 stage compressor. I will likely run 4 circuits in the shed: 240v 20a 10/2 compressor, 120v 15a 14/2 lights, 120v 20a 12/2 refrigerator, 120v 20a 12/2 outlets. Is the existing 10ga THHN ground adequate for this (two new ground rods for shed subpanel, 6ga copper from rods to panel)? What size breaker should I use in the garage subpanel to feed the shed subpanel?