Maybe this is what happened link below.
http://terrylove.com/forums/index.php?threads/imploding-water-heater.23656/
Why do you need a heater for your hot water?
![]()
Why do you need a heater for your hot water?
![]()
Because it's much more efficient to heat the 50 gallons of hot water in the tank than letting it get cold and reheating it.
I think the point is - that it is a "water heater", not a "hot water heater". Hot water heater is redundant.
Eight year old Bradford White 50 gallon...
I just shut it down as I didn't like the look of this....
Why are the pipes bent inward like that???
But it is a hot water heater. The tank is full of hot water. You turn the hot water tap on, causing some hot water in the tank to be replaced with cold water causing the tank temperature to drop. When the tank cools to a preset temp (still hot though), the thermostat turns the heat source on and.......wait for it......wait for it.....heats the hot water even hotter.
It's some neat stuff.
Did this happen suddenly or did it happen over time? While that expansion tank looks heavy, I would tend to think that if it was lack of support on the pipes it would tend to lean towards the outside of the water heater. I've never seen anything like that.
A friend of mine has installed hundreds of water heaters, I'll see if I can get in touch with him.
Why do we continually argue about this? We all know what the opening poster is talking about so why can't we just move on?
I think the canister is not installed correctly, has nothing to do with the cockeyed water pipe on the water heater. But might consider plumbing that thing with the air valve up.
I don't care one way or the other just saying..
I agree with you in principle, but for the pipes to bend that far inward it would mean the internal tank would have to bend outward pretty darn far. I doubt it would be possible for the internal tank to bend outward far enough to make the pipes bend inward that much without the internal tank bursting wide open. I mean, I am assuming the tank is glass lined steel and if that is indeed the case, just how far can it stretch without breaking and flooding the basement?Gents, sorry to disagree, not a vacuum....excess pressure. A vacuum would draw the middle of the heater jacket inward forcing the ******* outward (think of squeezing a beer can). Thermal expansion or excess pressure forces the middle of the heater outward which forces the ******* inward.
Not really enough data given to give a absolute answer. If the outlet ******* are faced inward as depicted in the picture, it's likely that thermal expansion is to blame.
A few things to check:
Need to find out what the incoming water pressure is. If over 80psi, a pressure reducing valve is needed before going on to the following steps.
T & P Valve - Insure one is installed. I think I see it in the lower right-hand portion of the picture.
T & P Valve - Has it been seeping? IF not, check to insure that it is rated to NO MORE than 150 psi. Many people try to solve a seeping T & P issue by installing a T & P valve with a rating greater than 150 psi. If this has been done, shut down the water heater until you can get the proper T & P valve installed. This is a very dangerous situation.
If T & P has been seeping - Expansion tank has gone bad or is not properly charged. Expansion tank should be charged to incoming water pressure BEFORE it is installed (air can be compressed, water can't....at least not on earth).
Take the following steps:
1) Check T & P for proper rating (150 psi)
2) Check to see if you have a closed plumbing system. Check valve in the water meter, a pressure reducing valve, or a backflow preventer all close the system.
3) Check water pressure for 24 hours using a gauge with a lazy arm (cheap at Home Depot - link below).
4) If water pressure exceeds 80 psi you have found part of your problem.
5) Check expansion tank. Open the Schroeder valve (looks like the valve stem on a tire) for a second, if water comes out, expansion tank is bad.
6) If water does not come out, remove expansion tank and check air pressure. Expansion tank should be charged to incoming water pressure BEFORE installing it in the system. It is extremely common for tanks to be improperly charged as most do not know to charge before installation.
7) Reinstall properly charged expansion tank.
9) Use pressure gauge with lazy arm to check pressure for 24 hours. I think you'll find that unless you have a water hammer problem, the gauge will read within a pound or two of your original incoming water pressure (which should/must be under 80 psi).
A link to the gauge I use is below:
http://www.homedepot.com/p/3-4-in-Plastic-Water-Pressure-Test-Gauge-DP-IWTG/100175467?MERCH=REC-_-SearchPLPHorizontal1_rr-_-NA-_-100175467-_-N
There could be a bit more to what's going on, but the above is a good place to start.
Reflex
Gents, sorry to disagree, not a vacuum....excess pressure. A vacuum would draw the middle of the heater jacket inward forcing the ******* outward (think of squeezing a beer can). Thermal expansion or excess pressure forces the middle of the heater outward which forces the ******
......
Reflex
I would like to see a disection of this after you get it swapped out...
Either the top collapsed in, or the sides expanded out... But like you said, "why" is the question here...
It's probably for a whole house humidifier.A little off topic but is that an ice maker tap on the "hot" pipe?
The bending is indeed a WTF I agree
This is probably an opportune time to replace it with an on demand AKA tank less water heater.