WTF? My hot water heater

ratdoggy

Well-known member
Joined
Mar 27, 2009
Messages
11,977
Location
Akron-Canton area OH
Eight year old Bradford White 50 gallon...
I just shut it down as I didn't like the look of this....:headscrat
Why are the pipes bent inward like that???
 

Attachments

  • P2250177.jpg
    P2250177.jpg
    139.9 KB · Views: 735
To avoid these ads, REGISTER NOW!

coldh2o

Well-known member
Joined
May 21, 2013
Messages
1,440
Location
Ontario, Canada
Why do you need a heater for your hot water?


:p

Because it's much more efficient to heat the 50 gallons of hot water in the tank than letting it get cold and reheating it. Unless it's the first fill, or you have a lot of showering teenagers, the unit is always bouncing a few degrees around the thermostat set point and heating hot (or warm) water.

Back on topic, I also have an 8 year old BW unit so am very interested in knowing the cause.

I'm also wondering what is written on the vent pipe...
 

pepi

Well-known member
Joined
Mar 27, 2013
Messages
2,883
Location
Woodstock, GA
I think the canister is not installed correctly, has nothing to do with the cockeyed water pipe on the water heater. But might consider plumbing that thing with the air valve up.

I don't care one way or the other just saying..
 

toyotadriver

Well-known member
Joined
Dec 30, 2010
Messages
1,586
I think the point is - that it is a "water heater", not a "hot water heater". Hot water heater is redundant.




But it is a hot water heater. The tank is full of hot water. You turn the hot water tap on, causing some hot water in the tank to be replaced with cold water causing the tank temperature to drop. When the tank cools to a preset temp (still hot though), the thermostat turns the heat source on and.......wait for it......wait for it.....heats the hot water even hotter.

It's some neat stuff.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
I think OP is running some sort of science experiment ..... something like the one that crush the 50 Gallon drums with a bucket of cold water....in physics class

were you trying to do this experiment?

I would check your cold water down mix tube makes sure it is still there.... and not disintegrate. It usually feeds the cold water to the bottom of the "Hot Water Heater". I think they are common to disintegrate over time, it's just some sort of PVC. Cheap part. Especially noticeable if your water is luke warm most of the time. If it have any chance of spraying cold water to the top of the tank like that 50 Gallon drum experiment, it could cause a mini rapid implosion from the rapid cooling of the top.... The inside of those tanks are at least 1/8 steel.... no rust would easily bend them.... I still have and old one in the back that I cut up.... Cheap American Water Heater brand, builder's quality one.
 
Last edited:

onewheat

Well-known member
Joined
Feb 19, 2012
Messages
1,286
Location
Knoxville, TN
But it is a hot water heater. The tank is full of hot water. You turn the hot water tap on, causing some hot water in the tank to be replaced with cold water causing the tank temperature to drop. When the tank cools to a preset temp (still hot though), the thermostat turns the heat source on and.......wait for it......wait for it.....heats the hot water even hotter.

It's some neat stuff.

But it also heats cold water, luke-warm water, warm water, tepid water and almost-hot water, so it heats water and the temperature is irrelevant. It is a "water heater". Look on any box - they are labeled as "Water Heaters" on all of them - not "Hot Water Heaters".
 

Super Mech

Well-known member
Joined
Feb 19, 2011
Messages
1,806
Location
Bronx,NY
Did this happen suddenly or did it happen over time? While that expansion tank looks heavy, I would tend to think that if it was lack of support on the pipes it would tend to lean towards the outside of the water heater. I've never seen anything like that.
A friend of mine has installed hundreds of water heaters, I'll see if I can get in touch with him.
 
OP
R

ratdoggy

Well-known member
Joined
Mar 27, 2009
Messages
11,977
Location
Akron-Canton area OH
I manage a scrap yard and see all kinds of water heaters come in and I have never seen one do this...
As far as the expansion tank it's been there for 8 years and why would the othre pipe bend inward?
Builder quality or not I've never ever seen this before and based on some of the answers that are reasonable not too many have either.
Of course I shut it down and will get it replaced but I want a real reason why it did that
 
OP
R

ratdoggy

Well-known member
Joined
Mar 27, 2009
Messages
11,977
Location
Akron-Canton area OH
Did this happen suddenly or did it happen over time? While that expansion tank looks heavy, I would tend to think that if it was lack of support on the pipes it would tend to lean towards the outside of the water heater. I've never seen anything like that.
A friend of mine has installed hundreds of water heaters, I'll see if I can get in touch with him.

Basically over night it happened...I do have a water softener and wonder if it might have rusted internally
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Why do we continually argue about this? We all know what the opening poster is talking about so why can't we just move on?

I have no idea why either... it's like just some stubborn old dog loves peeing on the hot water heaters.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,657
Location
Long Island
I think the canister is not installed correctly, has nothing to do with the cockeyed water pipe on the water heater. But might consider plumbing that thing with the air valve up.

I don't care one way or the other just saying..

Extrol tanks are designed to work in any orientation. But if you want to get all of the air out of the water side of the tank (more of a consideration for closed loop systems), then you should install it with the air valve DOWN, not up.

The OP's issue however is something else. From the way that both inlet pipes bent in the same way inwards, it is clear to me that a vacuum was drawn on the tank.

The Extrol tank is there to compensate for increases in pressure that can occur as water heats up and expands, and has nowhere to go when the path to the water system is blocked by a check valve.

The same water will contract as it cools. But the check valve will allow cold water to re-enter the tank before you get any vacuum.

I can think of two scenarios that could cause this.
1) The hot tank had the cold water supply shut off, and was then allowed to cool.
2) A firetruck on a nearby street pulled vacuum on the water main.

Vacuum arresters are required devices on things that can allow contaminants to enter a water system. In the case of vacuum being pulled from the system, they allow clean air in, rather than allowing contaminated water to enter. If the OP had a PVB, rather than a check valve on his water service, then scenario 2 would be impossible (if it worked as it should).
 

Reflex

Well-known member
Joined
May 19, 2015
Messages
49
Gents, sorry to disagree, not a vacuum....excess pressure. A vacuum would draw the middle of the heater jacket inward forcing the ******* outward (think of squeezing a beer can). Thermal expansion or excess pressure forces the middle of the heater outward which forces the ******* inward.

Not really enough data given to give a absolute answer. If the outlet ******* are faced inward as depicted in the picture, it's likely that thermal expansion is to blame.

A few things to check:

Need to find out what the incoming water pressure is. If over 80psi, a pressure reducing valve is needed before going on to the following steps.

T & P Valve - Insure one is installed. I think I see it in the lower right-hand portion of the picture.

T & P Valve - Has it been seeping? IF not, check to insure that it is rated to NO MORE than 150 psi. Many people try to solve a seeping T & P issue by installing a T & P valve with a rating greater than 150 psi. If this has been done, shut down the water heater until you can get the proper T & P valve installed. This is a very dangerous situation.

If T & P has been seeping - Expansion tank has gone bad or is not properly charged. Expansion tank should be charged to incoming water pressure BEFORE it is installed (air can be compressed, water can't....at least not on earth). :D

Take the following steps:

1) Check T & P for proper rating (150 psi)

2) Check to see if you have a closed plumbing system. Check valve in the water meter, a pressure reducing valve, or a backflow preventer all close the system.

3) Check water pressure for 24 hours using a gauge with a lazy arm (cheap at Home Depot - link below).

4) If water pressure exceeds 80 psi you have found part of your problem.

5) Check expansion tank. Open the Schroeder valve (looks like the valve stem on a tire) for a second, if water comes out, expansion tank is bad.

6) If water does not come out, remove expansion tank and check air pressure. Expansion tank should be charged to incoming water pressure BEFORE installing it in the system. It is extremely common for tanks to be improperly charged as most do not know to charge before installation.

7) Reinstall properly charged expansion tank.

9) Use pressure gauge with lazy arm to check pressure for 24 hours. I think you'll find that unless you have a water hammer problem, the gauge will read within a pound or two of your original incoming water pressure (which should/must be under 80 psi).

A link to the gauge I use is below:

http://www.homedepot.com/p/3-4-in-Plastic-Water-Pressure-Test-Gauge-DP-IWTG/100175467?MERCH=REC-_-SearchPLPHorizontal1_rr-_-NA-_-100175467-_-N

There could be a bit more to what's going on, but the above is a good place to start.

Reflex
 
Last edited:
To avoid these ads, REGISTER NOW!

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
Gents, sorry to disagree, not a vacuum....excess pressure. A vacuum would draw the middle of the heater jacket inward forcing the ******* outward (think of squeezing a beer can). Thermal expansion or excess pressure forces the middle of the heater outward which forces the ******* inward.

Not really enough data given to give a absolute answer. If the outlet ******* are faced inward as depicted in the picture, it's likely that thermal expansion is to blame.

A few things to check:

Need to find out what the incoming water pressure is. If over 80psi, a pressure reducing valve is needed before going on to the following steps.

T & P Valve - Insure one is installed. I think I see it in the lower right-hand portion of the picture.

T & P Valve - Has it been seeping? IF not, check to insure that it is rated to NO MORE than 150 psi. Many people try to solve a seeping T & P issue by installing a T & P valve with a rating greater than 150 psi. If this has been done, shut down the water heater until you can get the proper T & P valve installed. This is a very dangerous situation.

If T & P has been seeping - Expansion tank has gone bad or is not properly charged. Expansion tank should be charged to incoming water pressure BEFORE it is installed (air can be compressed, water can't....at least not on earth). :D

Take the following steps:

1) Check T & P for proper rating (150 psi)

2) Check to see if you have a closed plumbing system. Check valve in the water meter, a pressure reducing valve, or a backflow preventer all close the system.

3) Check water pressure for 24 hours using a gauge with a lazy arm (cheap at Home Depot - link below).

4) If water pressure exceeds 80 psi you have found part of your problem.

5) Check expansion tank. Open the Schroeder valve (looks like the valve stem on a tire) for a second, if water comes out, expansion tank is bad.

6) If water does not come out, remove expansion tank and check air pressure. Expansion tank should be charged to incoming water pressure BEFORE installing it in the system. It is extremely common for tanks to be improperly charged as most do not know to charge before installation.

7) Reinstall properly charged expansion tank.

9) Use pressure gauge with lazy arm to check pressure for 24 hours. I think you'll find that unless you have a water hammer problem, the gauge will read within a pound or two of your original incoming water pressure (which should/must be under 80 psi).

A link to the gauge I use is below:

http://www.homedepot.com/p/3-4-in-Plastic-Water-Pressure-Test-Gauge-DP-IWTG/100175467?MERCH=REC-_-SearchPLPHorizontal1_rr-_-NA-_-100175467-_-N

There could be a bit more to what's going on, but the above is a good place to start.

Reflex
I agree with you in principle, but for the pipes to bend that far inward it would mean the internal tank would have to bend outward pretty darn far. I doubt it would be possible for the internal tank to bend outward far enough to make the pipes bend inward that much without the internal tank bursting wide open. I mean, I am assuming the tank is glass lined steel and if that is indeed the case, just how far can it stretch without breaking and flooding the basement?
 

EOC_Jason

Well-known member
Joined
Jun 25, 2012
Messages
11,388
Location
Bentonville, AR
I would like to see a disection of this after you get it swapped out...

Either the top collapsed in, or the sides expanded out... But like you said, "why" is the question here...
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Gents, sorry to disagree, not a vacuum....excess pressure. A vacuum would draw the middle of the heater jacket inward forcing the ******* outward (think of squeezing a beer can). Thermal expansion or excess pressure forces the middle of the heater outward which forces the ******
......
Reflex

The top and bottom of the inside tank normally is build with, the top is convex (domed) outwards and the bottom is concave inwards..... if it is excess pressure the top would have expand outward further. I would think..... only a vacuum implosion would have cause a convex surface dent inwards. . like that 50 gallon drum experiment.... the OP must have created certain unique conditions that cause this. .... such as some how rapid cooling the convex top.... Most of those heaters have a 10 year warranty especially on the tank why not claim the warranty :) maybe the rapid cooling is caused by that draft inducing fan ?
 
Last edited:

Reflex

Well-known member
Joined
May 19, 2015
Messages
49
Dogdog,

Excellent logic....and your are correct, the top and bottom portions of the tank are manufactured with the same basic shape (not exactly the same). The bottom of the tank is manufactured so that we get greater surface area for improved heat transfer. The top of the tank is shaped this way for strength. These parts are formed with a 60 ton press out of a flat sheet and are critical to the proper performance of the unit.

That being said, the weakest point of the tank is the middle of the vertical portion of the tank. In addition, the top and bottom of the tank are welded to the flue, this gives the top of the tank additional strength. What I didn't mention in my post (it was too long) was the fact that the original poster might also check for a collapsed flue. It is common for the flue to "give" in this situation. It's a little tough to check on a power vent.

Although in a vacuum or excessive pressure situation the pressure is equal on all sides, the long sides have the tank have a greater moment and therefore less rigidity. The top and bottom may collapse, but deformation of the sides occurs first. This causes the ******* to bow out when a vacuum occurs as the top of the heater is much stronger than the sides due to it's limited moment and it's curvature. We've all seen/done the paint can or gas can experiment in which the can is heated with the cap off and then taken off the burner and the cap put on. The can collapses as depicted in the picture below.

air-pressure-crushed-can_thumb.jpg


You point on vacuum is well taken, but I'll stick with high pressure. Enjoyed reading your post.

Thanks,

Reflex
 
OP
R

ratdoggy

Well-known member
Joined
Mar 27, 2009
Messages
11,977
Location
Akron-Canton area OH
I would like to see a disection of this after you get it swapped out...

Either the top collapsed in, or the sides expanded out... But like you said, "why" is the question here...

I definitely want to see that too....
As I've mentioned; house was built in 2009 and we have never had any kind of problem with the unit before. I'll drain sediment out every now and then. No odd problems and I'm on city water
 
OP
R

ratdoggy

Well-known member
Joined
Mar 27, 2009
Messages
11,977
Location
Akron-Canton area OH
And I will be contacting Bradford-White to see what's up with this

I just emailed them so I should know more Monday
 
Last edited:

mires

Well-known member
Joined
Jan 12, 2014
Messages
600
Location
Columbia, MO
Definitely thermal expansion. If your expansion tank is like 80% of them I see in my area it was never charged with the correct pressure when it was installed rendering it useless. Definitely check your water pressure.
 

Lassen Forge

Well-known member
Joined
Apr 26, 2014
Messages
15,391
Location
The romantic hills of central Umbria, Italy,
I would think the top of the water tank caved in. Subjected to a hard vacuum, add internal rust, and whang, just like the Pepsi cans above. If the warranty is still good on the tank, then you may be OK. but yeah, I'd replace that thing either way.

I'm wondering, tho, if it did rust internally why it rusted - there's supposed to be a sacrificial anode (or 3) in the tank to prevent that from happening... maybe it's shot, or worse, forgot to be installed when they built the thing...

It'll be interesting to see what that tank looks like once the sheet metal is removed, and what the tank looks like cut open.
 
OP
R

ratdoggy

Well-known member
Joined
Mar 27, 2009
Messages
11,977
Location
Akron-Canton area OH
This is probably an opportune time to replace it with an on demand AKA tank less water heater.

I don't think it pays as I have Natural Gas I saw where yearly savings would be about $100...

Not worth it..
Cost to heat the house is one reason I wanted NG at the house..
You wouldn't believe how cheap my bill is for what I get..
 
Last edited:

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
14,082
Location
Lebanon, TN
I'm curious to see what the failure mode is. In a gas water heater the flue is welded into the bottom and top tank ends, essentially forming a column within the tank. In theory, the area where the inlet and outlet bungs are welded to the top tank end (where yours appears to have buckled) should be one of the strongest parts of the tank. Failure from pressure or vacuum should effect the walls of the tank LONG before the ends.

This is truly an odd one.
 
Last edited:

Super Mech

Well-known member
Joined
Feb 19, 2011
Messages
1,806
Location
Bronx,NY
I got in contact with a friend of mine who has installed literally hundreds of water heaters in his lifetime. He said that he has never seen anything like that. His theory is that if there is tension on the pex lines and the top of the tank weakend they could have pushed the pipes together. He doubts that's the problem. He had no other answer but would like me to tell him if an autopsy is done on the tank.
 