Xhhn-w or USE and conduit bends?

jekquist

Well-known member
Joined
Apr 6, 2016
Messages
65
Location
Pinckney, MI
My local county inspector said I can use xhhn-w or USE #2 wire for a 100 A sub in my pole barn. Run is total of 145feet 65 feet of that being across the basement. PVC is cheap enough, and I have to run conduit on the inside run so I figured why not do the whole run. I am upsizing to #1 because of threads I have read on here stating #2 AL is only good for 90A. Unless you guys can give me a reason not to.


My other question is about max number of bends. From what I have read the maximum number of bends has to be less that 360 degrees. Is this only for the outside/once it goes underground? The reason I ask is, I need 270degrees to make it look clean and run neatly along the joists. I plan on exiting from the main panel on the side, but can move to the top if needed. Man is that NEC book confusing.


Thanks guys. I would have asked the inspector again but I bet he is sick of my questions.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
USE-2 only is not allowed to be installed inside, outside only. Use the XHHW or RHH/RHW-2/USE-2.

360deg between pull points.
 
Last edited:
OP
J

jekquist

Well-known member
Joined
Apr 6, 2016
Messages
65
Location
Pinckney, MI
I might have answered my own questions as a conduit body is considered a pull point. So I should be fine having 270 degrees on the inside to a conduit body then 180 degrees to the next conduit body.
 

metlmunchr

Well-known member
Joined
Sep 10, 2011
Messages
1,278
An LB would give you a pull point so it would not be included in the 360 degrees.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Also a LB can not be used for a transition point (splice point) because the volume/size is too small to meet code. You'll need at least a 8X8X4 junction box for the splices using #2 wire.
 

bjcouche

Well-known member
Joined
Sep 11, 2010
Messages
509
Location
Ohio
Yes, 360 degrees between pull points, and an LB is considered a pull point. What you will find is that you cannot pull wire through an LB without pulling the wire out of the LB, then shoving it back in the other side. An LB is too tight of a radius to pull wire through.

Also if you are looking at wire types, the advice thus far is good. If you are going to an electrical distributor (not big box stores) you might inquire about what other wire types they have. Around here you can get THHN/THWN in ALUMINUM, and the wire is pre lubed. Might be able to compare pricing between the THWN and the RHH/RHW-2/USE-2. That's what I used for my shop feed.

Brian
 
To avoid these ads, REGISTER NOW!

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
Also a LB can not be used for a transition point (splice point) because the volume/size is too small to meet code. You'll need at least a 8X8X4 junction box for the splices using #2 wire.

Debateable. If it's sized accordingly it can be used as a junction.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,217
Location
SE MI
I am upsizing to #1 because of threads I have read on here stating #2 AL is only good for 90A. Unless you guys can give me a reason not to.

Sure $$$ !!! You will never miss those 10A !

2-2-2-4 MHF cable is usually the best "bang for the buck". It must be run in a conduit when indoors.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Debateable. If it's sized accordingly it can be used as a junction.

Well yeah if you use conduit that is way over sized for the wire and have a huge LB. Otherwise you'll be hard pressed to meet the dimension requirements of the box to the conduit size for the splice and have the needed lengths of tails to meet code for the splices and be able to shove it in the LB. Also the LB has to be stamped with a volume to be used for splices.
 
Last edited:
OP
J

jekquist

Well-known member
Joined
Apr 6, 2016
Messages
65
Location
Pinckney, MI
Sure $$$ !!! You will never miss those 10A !



2-2-2-4 MHF cable is usually the best "bang for the buck". It must be run in a conduit when indoors.



I was quoted #1al xhhw-2 for 30 cents a foot. That is well within my budget. Running a welder, plasma cutter and a big compressor I might need those extra 10A.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I was quoted #1al xhhw-2 for 30 cents a foot. That is well within my budget. Running a welder, plasma cutter and a big compressor I might need those extra 10A.

You'll find that buying the individual wires are cheaper than the assembled MHF cable. Another thing is MHF doesn't come in #1, it's #2 or #2/0 or #4/0.
 