farphle
Well-known member
I just inherited a 60 gal compressor (CH VT627505AJ) and need to know what's required to wire it up. Label says 240V/15A/60Hz/1PH. I believe it has a 3.2 HP motor.
Basic volts x amps=watts 240v x15amp=3600watt div by 746 watt per hp=4.825 HP
So what size breaker am I looking at needing and do I need to hardwire this to a disconnect or can I put a plug on it and use a receptacle?
I don't believe you are allowed to oversize the breaker on a cord and plug circuit for motor operated equipment.
It's not and never has been.
The only time it's allowed is to use 15A devices on a 20A circuit, but even then using a single 15A receptacle on a 20A circuit is forbidden
I'm very well aware of that.
I don't believe you are allowed to oversize the breaker on a cord and plug circuit for motor operated equipment. It will need to be hardwired to use a 30A breaker on #12. Use #10Cu wire with a 30A breaker and a 6-50 outlet & plug. The 6-50 is 3HP rated.
The 6-50 is required to get the 3HP. However, if using that size P/R, a 50A ckt - (conductors and ocp) must be provided not 30A. NEC 430.42(C) and 210.21(B) govern this since the receptacle does not provide for a dedicated motor ckt. Anyone can plug anything into it.
You have to go by the NEC tables for both wire and breaker sizes.
3HP is listed @ 17A, which when multiplied by 1.25 (also required) comes out to 21.25A.
So a 20A breaker is undersized for the circuit.
In this case wouldn't you use the amp rating on the motor? The motor plate doesn't claim 3hp. That comes from the marketing material. I'm asking because I don't know. Not an issue for me now but if we move to a new house/build a larger garage it might.