Yet another wire size question

Planenutz

Well-known member
Joined
Mar 6, 2014
Messages
50
Location
Central Minnesota
I found previous garage owner wired a 220 20a outlet with 14 ga NM wire. It's about 30' from breaker to outlet. Here's the tag on the compressor. Seems to be OK at 15 amps for that distance according to the online wire size calculators.
Would you agree it's ok? I'd rather not have to pull new wire through the walls.
Thanks
 

Attachments

  • 92696968_2569895289964644_4084700836947558400_n.jpg
    92696968_2569895289964644_4084700836947558400_n.jpg
    119.6 KB · Views: 53
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
20a outlet with #14 NM is not ok.

Wire for motor circuits is sized by HP rating. Since the motor is SPL you have to compare the FLA rating to the NEC FLC chart.

That motor is about 3HP so it needs #10 NM-b or #12 THWN in pipe.

17a x 1.25 = 21.25a
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,494
Location
East Bay SFO
Have you considered a surface mounted conduit installation?

By pulling a few more wires, you could use the new conduit run to not only solve your wire gauge problem for the 240V but add another 120V receptacle if you need another one somewhere in that 30 feet. A new dedicated circuit 20A duplex receptacle might be a welcomed addition.

To me, a well done conduit run in a working garage does not look out of place.
 
Last edited:

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,925
Location
Coronado, CA
Have you considered a surface mounted conduit installation?

By pulling a few more wires, you could use the new conduit run to not only solve your wire gauge problem for the 240V but add another 120V receptacle if you need another one somewhere in that 30 feet. A new dedicated circuit 20A duplex receptacle might be a welcomed addition.

To me, a well done conduit run in a working garage does not look out of place.

What he said.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,106
Location
SE MI
Change the breaker to 15A.

If the motor trips the breaker, then pull new wire and go back to the 20A breaker.
 
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,584
Location
BC
The wire can technically handle the 15A load being asked of it. After all, a compressor that charges up a tank is not a continuous load.

But for peace of mind, and to match the 20A breaker and receptacle being used, best to upgrade to #12. Code wants #12 too.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,417
Location
Richmond, VA
20a outlet with #14 NM is not ok.

Wire for motor circuits is sized by HP rating. Since the motor is SPL you have to compare the FLA rating to the NEC FLC chart.

That motor is about 3HP so it needs #10 NM-b or #12 THWN in pipe.

17a x 1.25 = 21.25a