Well-known member
So my buddy recently had a dual-head LG system installed (well, 4 head condensing unit, but only two heads hooked up). They said they were having some issues, so I was taking a look at it. It seemed to be working okay, maybe. The outdoor unit's compressor seemed to be working pretty hard with only one head on and a ~45 degree ambient. At least compared to other minisplits I've worked with.
That made me think maybe some charge had leaked out.
So we started looking over some stuff. The documentation the installer provided said "Pressure tested @ 150 PSI for 10 minutes". So right off the bat that's a red flag.
I then grabbed some soapy bubbles and headed out to the ODU, was pretty shocked to see them using zoomlock/other press fittings on the outdoor unit. They were these pre-made flare-to-crimp connections. I looked them up, and they cost anywhere from $30-60 depending on size! I can maybe understand it on a conventional system where you'd have to braze, but on a minisplit? It literally takes less than a minute to flare a line set. They probably spent more time futzing around with the crimp tool and getting things cleaned, deburred and lined up than they would have just flaring the line directly.
But anyways, that's besides the point. I looked up the specs on the crimp fittings they used, and they said "Maximum Working Pressure: 700 PSI, Max Temperature: 250°F".
The LG documentation requests that you pressure test at 550 PSI for many hours, and that the compressor discharge temperature can hit near 170-180°F. I've read that minisplit R410a systems can hit 600+ PSI in normal operation. That seems to be cutting it really close, no? Seems kind of sketchy to me.
Are people really pressing minisplits together these days?
That made me think maybe some charge had leaked out.
So we started looking over some stuff. The documentation the installer provided said "Pressure tested @ 150 PSI for 10 minutes". So right off the bat that's a red flag.
I then grabbed some soapy bubbles and headed out to the ODU, was pretty shocked to see them using zoomlock/other press fittings on the outdoor unit. They were these pre-made flare-to-crimp connections. I looked them up, and they cost anywhere from $30-60 depending on size! I can maybe understand it on a conventional system where you'd have to braze, but on a minisplit? It literally takes less than a minute to flare a line set. They probably spent more time futzing around with the crimp tool and getting things cleaned, deburred and lined up than they would have just flaring the line directly.
But anyways, that's besides the point. I looked up the specs on the crimp fittings they used, and they said "Maximum Working Pressure: 700 PSI, Max Temperature: 250°F".
The LG documentation requests that you pressure test at 550 PSI for many hours, and that the compressor discharge temperature can hit near 170-180°F. I've read that minisplit R410a systems can hit 600+ PSI in normal operation. That seems to be cutting it really close, no? Seems kind of sketchy to me.
Are people really pressing minisplits together these days?