Splicing Inside Sub-Panel?

dwall174

Well-known member
Joined
Jun 1, 2012
Messages
453
Location
Southeast Michigan
Can you install a power distribution block like this inside of a sub-panel to split the power from a 40-amp breaker into 2-circuits?
MPDB63162_main-1.jpg

Doug
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,014
Location
NJ
Why not use a quad breaker instead of adding this distribution block that doesn't belong in a small panel? Much cleaner, less space, probably less cost.

Is each circuit 40A ?
 
OP
D

dwall174

Well-known member
Joined
Jun 1, 2012
Messages
453
Location
Southeast Michigan
Why not use a quad breaker instead of adding this distribution block that doesn't belong in a small panel?
Because as far as I know they don't make a quad breaker for the QO series Square D sub-panel I installed a few years ago.
Sub Panel 1 .jpg
The QO series double pole breakers are rated for dual wire terminations, but only up to 30-amps.
Is each circuit 40A ?
Yeah, I have a 5hp. RPC that's wired to a 40-amp breaker & I would like to also run (not at the same time) a 5hp. VFD off that same circuit.

Doug
 

kaymccampbell

Well-known member
Joined
Feb 27, 2015
Messages
29,588
Location
Upstate New York
I was in your predicament, and instead, ran from my single 240 breaker to an Eaton sub box with an Eaton BQC240240 40A Quad Circuit Breaker in it, so I could split my 240 line into my lathe and dust collector, in a small form factor. It looks a touch weird, but it works.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,773
Location
Richmond, VA
Because as far as I know they don't make a quad breaker for the QO series Square D sub-panel I installed a few years ago.
Sub Panel 1 .jpg
The QO series double pole breakers are rated for dual wire terminations, but only up to 30-amps.

Yeah, I have a 5hp. RPC that's wired to a 40-amp breaker & I would like to also run (not at the same time) a 5hp. VFD off that same circuit.

Doug
Finally, an application where homeline is better! :)

Thanks for the details. Blue wire nuts will do dual #6 and it would cost about 5 bucks

 
Last edited:

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,773
Location
Richmond, VA

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,014
Location
NJ
Now with more details, I understand your predicament.
Before you go further, ask yourself, how many more ckts will my shop need in the future? Will I keep running into the same problem?

Is now the time to bite the bullet for a larger panel? Or hold off for now and just use a few blue wire nuts as a temp for the interim?
 
OP
D

dwall174

Well-known member
Joined
Jun 1, 2012
Messages
453
Location
Southeast Michigan
Now with more details, I understand your predicament.
Just to aggravate me a little more, the cover actually has 4-more spaces in it. :headscrat
Panel Cover .jpg
Before you go further, ask yourself, how many more ckts will my shop need in the future? Will I keep running into the same problem?
I've thought about that! :rolleyes:
However, I'm pretty much out of room for anymore equipment in the garage.

Doug
 

toplessHO

Well-known member
Joined
Oct 20, 2014
Messages
14,067
Location
central florida
Whats the can made for?
if it lists one with a larger breaker count,gut the breakers,install the new
interior and add your breakers
 

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,819
Why don't you do like most people and stick a junction box outside the panel somewhere to branch off to the different loads?
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,219
Location
SE MI
Because as far as I know they don't make a quad breaker for the QO series Square D sub-panel I installed a few years ago.
Older (25+) used different tandems. If you can find single pole (120V) tandems, you can shuffle the single pole breakers around and fit another two pole breaker in.
 
OP
D

dwall174

Well-known member
Joined
Jun 1, 2012
Messages
453
Location
Southeast Michigan
Whats the can made for?
If you're referring to the electrical box behind the cover?
The original panel is a 125-Amp panel with 12 spaces/12 circuits. QO112L125PG
if it lists one with a larger breaker count,gut the breakers,install the new
interior and add your breakers
The only panel I found with the same size box is a 100-Amp panel with 16 spaces/24 circuits. QO116M100P

Looking on the Schneider / Square D Website even though the boxes are the same size, the box numbers are different.
Swapping the guts may work, but it would probably involve modifying the mounting holes/slots.

Doug
 

toplessHO

Well-known member
Joined
Oct 20, 2014
Messages
14,067
Location
central florida
If you're referring to the electrical box behind the cover?
The original panel is a 125-Amp panel with 12 spaces/12 circuits. QO112L125PG

The only panel I found with the same size box is a 100-Amp panel with 16 spaces/24 circuits. QO116M100P

Looking on the Schneider / Square D Website even though the boxes are the same size, the box numbers are different.
Swapping the guts may work, but it would probably involve modifying the mounting holes/slots.

Doug
Check on the guts swap if the box is same size the only difference may be the label.
There is a company thats doing panel upgrades and makes the guts and covers for
many obsolete panels. So its UL approved for them to swap guts and provide a new cover
with the old can. That saves a lot of time and expense. In this case you have the cover.
The guts most likely are all screws or slot on bottom screws up top.
I bet the bottom mount is same on yours vs the 16 circuit,just need to drill and tap a couple holes up higher.
 
To avoid these ads, REGISTER NOW!

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,272
Location
Coastal NJ
I think he's referring to placing two single -space tandem breakers next to each other & tying the center two together to basically make a quad setup.

The problem with that, is my panel isn't designed for tandem single breakers.
The problem with that is the two center breakers would feed a 240V circuit without common trip. No bueno.
They sell the setup you are referring to. But it’s not for 240 circuits.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,219
Location
SE MI
How? He has only 2 single pole breakers in the already full box.
Unless my eyes are bad (and they are) there is an empty spot on the top right. Only 2 of the 3 single pole breakers are in use. One tandem would cover that.

I do know that some load centers restrict the number of tandems and their locations. Not sure if there is a restriction on the number of 2 pole breakers on that load center.

I also know just because Square D no longer manufacturers a tandem 2 pole, does NOT mean they are no longer available !
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,219
Location
SE MI
The problem with that, is my panel isn't designed for tandem single breakers.
Are you sure about that ?

I was told the same thing by Square D, but I found out that there was a discontinued tandem, that was still available. 4 of those NOS tandems saved me from replacing the load center or adding a sub
 
OP
D

dwall174

Well-known member
Joined
Jun 1, 2012
Messages
453
Location
Southeast Michigan
Check on the guts swap if the box is same size the only difference may be the label.
Ok you talked me into it! :unsure:
I was able to find a box (no cover) with the 16-space guts! The box is the same width, but about 4" longer.
I bet the bottom mount is same on yours vs the 16 circuit, just need to drill and tap a couple holes up higher.
That's what I'm hoping on. :beer:
just ordered it today from ZORO! They usually ship pretty fast, so hopefully I get it next week.
New & Old Panel .jpg

Doug
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,051
Location
Modesto, CA
Unless my eyes are bad (and they are) there is an empty spot on the top right. Only 2 of the 3 single pole breakers are in use. One tandem would cover that.

I do know that some load centers restrict the number of tandems and their locations. Not sure if there is a restriction on the number of 2 pole breakers on that load center.

I also know just because Square D no longer manufacturers a tandem 2 pole, does NOT mean they are no longer available !
youre looking at the wrong pic (the deadfront cover in #4). you need to look at the pic in #1. notice the ground wires go right over the spot where the deadfront has 2 twist out covers? theres no space there. no buss bars for another breaker.
 
OP
D

dwall174

Well-known member
Joined
Jun 1, 2012
Messages
453
Location
Southeast Michigan
OP
D

dwall174

Well-known member
Joined
Jun 1, 2012
Messages
453
Location
Southeast Michigan
Curious. What was the price vs a whole new box ?
I couldn't find a 16-space full box/cover anywhere! Zoro sells the boxes & covers separately, I paid $66.00 for the box & 16-space buss/guts.

If I wanted to replace the complete box I could have gotten a 24-space box with cover in a value package with a few breakers for $135 at Lowes.

Doug
 