Doubled33

Well-known member
Joined
Dec 29, 2021
Messages
179
Location
CA/HI
I have a 3/4 run of FMC about 65’ long. The run is pretty straight and flat with only a few gentle bends in it.

It runs through an attic that is not really accessible.

There is an EMT 90 at each end with a FMC to EMT compression fitting.

I have an Ideal Fish Tape that is 125’ with a factory bent end on it that looks like half of an arrow head.

I tried both ends, but can’t get the tape through the pipe. It stops somewhere around the 50’ to 60’ mark.

Is there a better fish tape set up I can use?

Thanks
 
To avoid these ads, REGISTER NOW!

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
I have a 3/4 run of FMC about 65’ long. The run is pretty straight and flat with only a few gentle bends in it.

It runs through an attic that is not really accessible.

There is an EMT 90 at each end with a FMC to EMT compression fitting.

I have an Ideal Fish Tape that is 125’ with a factory bent end on it that looks like half of an arrow head.

I tried both ends, but can’t get the tape through the pipe. It stops somewhere around the 50’ to 60’ mark.

Is there a better fish tape set up I can use?

Thanks
Picture?
Are you talking about greenfield/flex?
 

Dig Doug

Well-known member
Joined
Apr 16, 2018
Messages
1,124
You can **** it like said above or blow it w/ air compressor

vac / **** works best, tie a plastic bag on a string - the bag needs to not plug the pipe and yet big enough to grab onto the suction…
 
OP
D

Doubled33

Well-known member
Joined
Dec 29, 2021
Messages
179
Location
CA/HI
Picture?
Are you talking about greenfield/flex?
Grabbed some Internet pics as I am away from the house.

I should add that I have 2 parallel runs and both have the same issue. This why I am thinking a tool issue over an Install issue.
 

Attachments

  • IMG_8895.png
    IMG_8895.png
    2.9 MB · Views: 8
  • IMG_8896.png
    IMG_8896.png
    1.8 MB · Views: 8

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Can you disconnect the greenfield from conduit,then fish it through there separately?
Then reconnect once the wire is through the greenfield?
 
OP
D

Doubled33

Well-known member
Joined
Dec 29, 2021
Messages
179
Location
CA/HI
You can **** it like said above or blow it w/ air compressor

vac / **** works best, tie a plastic bag on a string - the bag needs to not plug the pipe and yet big enough to grab onto the suction…

Will try this one. Did not think of sucking and good info on bag size.

Thanks
 
OP
D

Doubled33

Well-known member
Joined
Dec 29, 2021
Messages
179
Location
CA/HI
Can you disconnect the greenfield from conduit,then fish it through there separately?
Then reconnect once the wire is through the greenfield?
Possibly on one end. I will also give this a try.

The other end is connected to a 3’ long gutter that was installed with all 90’s stubbed out first so that end will not disconnect easily.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Ok,then put a bunch of pull boxes in line with the green field if it makes you happy. Hahaha.
If it passes a rough in inspection and a final that's all that matters,some times you have to do what you've got to do to get things done.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
Make sure your flex is pulled halfway tight. 65' of flex isn't going to be great no matter what. If you get it most of the way push another fish tape from the other end, hook the first one and finish pulling it through.

I wouldn't hold my breath on trying to **** a string. Flex is just a spiral of metal, not going to hold air.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,999
Location
Central Iowa
Flex in lengths over 50 or so feet can be a *******. I've done the take it apart and put it back together after the wire is in, I know it's a code violation, but there are times when I don't give a flyin' eff. If you have help, the easiest I've found is to have someone shake it while pushing on the fish tape.

This probably won't help with this, more in the future, but cut the end off of the fish tape. About 1-1/2" from the end, heat it up cherry red and bend a new loop in it. Dip it in water to cool it down and tape the gap shut.
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Flex in lengths over 50 or so feet can be a *******. I've done the take it apart and put it back together after the wire is in, I know it's a code violation, but there are times when I don't give a flyin' eff. If you have help, the easiest I've found is to have someone shake it while pushing on the fish tape.

This probably won't help with this, more in the future, but cut the end off of the fish tape. About 1-1/2" from the end, heat it up cherry red and bend a new loop in it. Dip it in water to cool it down and tape the gap shut.
The difficulty of fishing flex is why I do not like ENT "smurf tube" either, but vacuum fishing is what got some wire pulled in some Greenfield that a fish tape would not go through.
 
OP
D

Doubled33

Well-known member
Joined
Dec 29, 2021
Messages
179
Location
CA/HI
Flex in lengths over 50 or so feet can be a *******. I've done the take it apart and put it back together after the wire is in, I know it's a code violation, but there are times when I don't give a flyin' eff. If you have help, the easiest I've found is to have someone shake it while pushing on the fish tape.

This probably won't help with this, more in the future, but cut the end off of the fish tape. About 1-1/2" from the end, heat it up cherry red and bend a new loop in it. Dip it in water to cool it down and tape the gap shut.

Thanks. After dealing with this I can only imagine what pulling through maxcell innerduct is like. No thanks.
 
To avoid these ads, REGISTER NOW!

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
Flex which is not stretched tight and strapped down while tight is a bear to push the fishtape through. Reason being is that the flex wants to move with the head of the fishtape. Sucking or blowing a baggie tied to mason's twine is the way to go.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,592
Location
Fullerton, CA
There's code, and then there's reality. How would you fish some greenfield with two 90º connectors on it box-to-box.
It depends on the type of 90s they are.
One type has removable covers and is made of cast zinc (slang name is a "Jake fitting"). The other has a sheet metal cover that holds the conduit in.
 
Last edited:

rabidsquirrel

Well-known member
Joined
Jul 17, 2010
Messages
397
Location
SE Pennsylvania
It depends on the type of 90s they are.
One type has removable covers and is made of cast zinc. The other has a sheet metal cover that holds the conduit in.

I'm aware of that. My counter-argument is that fully assembled raceway of 90-flex-90 is impossible or nearly impossible to fish and pull wire in, in compliance with the code that was quoted.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,037
Location
Coronado, CA
Back in the day before retirement I had a very flexible tape that was like a "Golden Worm". If I recall correctly, it was sold by Ideal.
 

rabidsquirrel

Well-known member
Joined
Jul 17, 2010
Messages
397
Location
SE Pennsylvania
The ones with the removable covers leave the conduit run complete from box to box.
Can you provide an example of the ones you are talking about? Every flex 90 I've seen has a removable cover. The larger sizes have an additional clamp that holds the flex separately, but I doubt there is a single person on the planet that can leave 3.5" flex clamped and then fold the 500s into 90.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,592
Location
Fullerton, CA
I doubt there is a single person on the planet that can leave 3.5" flex clamped and then fold the 500s into 90.
Those I linked to are only available up to 1".
A 3-1/2" 90 degree flex connector has the bending radius required for 500s
Have you heard of a "Mogul LB"?
 
Last edited:

rabidsquirrel

Well-known member
Joined
Jul 17, 2010
Messages
397
Location
SE Pennsylvania
I've never seen 1 of those,but Walmart of all places lists them? Hahaha

Ditto. I'd expect that fitting to be about $5 each, not about $1.

Those I linked to are only available up to 1".
A 3-1/2" 90 degree flex connector has the bending radius required for 500s
Have you heard of a "Mogul LB"?

Yes, I understand that the connector is rated for that radius. I'm saying that with the 90 on whatever piece of equipment and the flex securely clamped onto the 90, zero, or nearly zero people will be able to get all the conductors in without undoing the flex.

Yes, I've seen a Mogul LB. Usually much more expensive.
 

mark flucke

Active member
Joined
Feb 14, 2016
Messages
33
Use a fiberglass fish tape- I used one for years on Target store remodels on 3rd shift- also about your only hope with smurf tube- , sometimes folding over a zip tie and creating a loop in front of the fish tape head (wrap the ends of the zip tie to the fish tape end with 33-DO NOT pull the wire in with the zip tie leader! -my apprentice did this once-Bad Spencer!- he learned
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,592
Location
Fullerton, CA
I had a 50' "Slippery Snake" (no longer made) it was made of 1/4" nylon, with a 6" spring leader on one end and an eye on the other. It was the best thing I ever used for flex (but couldn't be used for a 65' pull like the OP has).
 

BreeStephany

ALLIANCE MEMBER
Joined
May 19, 2012
Messages
854
Location
Oregon
As general practice, for FMC, it is easiest to put the conductors into the conduit and then install the conduit, but generally only do this for short runs. When long runs are necessary, I just generally try to avoid FMC and stick to EMT for runs of any kind significant of length because fishing wire in can be a huge pain once the conduit is installed and secured.

Given your installation, I would suggest what others have suggested with sucking in a string line with a baggy (a corner of a grocery bag work GREAT!) and then use the string line to pull your conductors.

Running metal fishtapes can be a huge pain as the leader tends to bind up inside of the FMC. I have had some luck with a fiberglass fishtape, but most of the time look at is pure luck type success.

As a bit of a tip, once you do get a fishtape or pull string through, pull in a spare pull string with your conductors just in case you need to pull any additional conductors into the conduit in the future.

Just my two cents!
 