NEMA 6-50 wiring oven

newpain01

Well-known member
Joined
Nov 3, 2023
Messages
111
Location
Eastern NC
Hey everyone!

I have an old oven on the garage that I plan to use for baking powder coated parts and need to wire a plug. The oven is 240V and has 4 wires (black, red, white and a bare ground wire) and I have NEMA 6-50R receptacle that only has 3 wires. I wired the black (left side), red (right side) and ground wire (top side) and put a wire nut on the white wire, but the oven doesn't power up, so the question is, what should I do with the white wire?

Appreciate any help!
 
To avoid these ads, REGISTER NOW!
OP
N

newpain01

Well-known member
Joined
Nov 3, 2023
Messages
111
Location
Eastern NC
It does have some features (I have not looked at them though), so I am sure there is a light inside and most likely a timer. I just want to wire it to turn on/off and maybe adjust temperature. It previously had a NEMA 10-30 plug and the white and ground wires were wired together on the neutral pin, if that helps. I don't have a NEMA 10-30 outlet in the garage, so need to rewire it now.
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,975
Location
East Cobb County, Georgia
Controls likely need 120 V so a neutral is needed. 10-30 used 2 lines plus the neutral with the ground tied to the neutral. You should not tie the neutral to a bare ground.
 
OP
N

newpain01

Well-known member
Joined
Nov 3, 2023
Messages
111
Location
Eastern NC
I have a 30a breaker, but don't need to run 50amps, I'll be using this for a 15amp air compressor and this 15-20 amp oven.

If I replace the cable how can I wire the 4 wires to the plug pictured above, or would you wire ground only on the metal part of the receptacle (my boxes are plastic)?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,941
Location
Richmond, VA
I have a 30a breaker, but don't need to run 50amps, I'll be using this for a 15amp air compressor and this 15-20 amp oven.

If I replace the cable how can I wire the 4 wires to the plug pictured above?
You can't. You need a 4 wire receptacle.

All the three wire stuff is not of use for the oven.

What's the HP rating on the compressor?
 
OP
N

newpain01

Well-known member
Joined
Nov 3, 2023
Messages
111
Location
Eastern NC
Ah, got it, so I can't use this oven with the existing receptacle.
The air compressor is rated at 3.7HP and the info plate on the motor says 15amp max.
 
OP
N

newpain01

Well-known member
Joined
Nov 3, 2023
Messages
111
Location
Eastern NC
Which receptacle would I need to use? The air compressor has a 6-50 plug already and only has 3 wires, works fine with the current receptacle. Do I have any other options to use this oven in the garage without rewiring the whole thing?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,018
Location
Central Iowa
You need a 14-50. You will be fine running 8/3 and using a 40 amp breaker. I do it all the time because I hate trying to stuff #6 in the box.

The oven needs two hots, a neutral because the controls and the light are 120 volt, and a ground. The compressor is two hots and a ground because it doesn't need a neutral. The oven didn't fire up because it doesn't have a neutral for the control circuit.

 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,941
Location
Richmond, VA
Which receptacle would I need to use? The air compressor has a 6-50 plug already and only has 3 wires, works fine with the current receptacle. Do I have any other options to use this oven in the garage without rewiring the whole thing?
The compressor doesn't need a neutral since it doesn't have any 120v controls like the oven.

Can you leave the current circuit for the compressor and run a new one for the oven?
 
OP
N

newpain01

Well-known member
Joined
Nov 3, 2023
Messages
111
Location
Eastern NC
I don't have any more empty spots for a new breaker in the breaker box. There are 2 of these 6-50 receptacles and I was planning to use one for the compressor and the other for the oven.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,941
Location
Richmond, VA
I don't have any more empty spots for a new breaker in the breaker box. There are 2 of these 6-50 receptacles and I was planning to use one for the compressor and the other for the oven.
You may be able to use tandems, but either way, you need a different oven or need to rewire.

If you are already full, I'd consider a small sub panel.
 
To avoid these ads, REGISTER NOW!
OP
N

newpain01

Well-known member
Joined
Nov 3, 2023
Messages
111
Location
Eastern NC
Let's say if I have someone rewire and replace both receptacles with 14-50, I could still keep the 6-50 plug on the compressor and use it with the 14-50 receptacle, right?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,018
Location
Central Iowa
How about posting a picture of the panel along with the model number. Usually, if can take tandems, it's part of the #. IE 1224, 1624, 2040, etc
 
OP
N

newpain01

Well-known member
Joined
Nov 3, 2023
Messages
111
Location
Eastern NC
Not sure where to find the model number, but here are some pictures. Looking at the breaker now, it’s a 20 amp, not 30 like I thought.

IMG_0616.jpegIMG_0617.jpeg
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,018
Location
Central Iowa
The label on the cover is for four different panels, but the key part is the 3040 in every number. 30 spaces, 40 circuits. It's twinnable, and though I'm not an expert on Siemens panels, I'd be willing to bet the five spaces on each side at the bottom are where the tandems can go.

EDIT: Since it's bottom fed, it will be the five spaces at the top on each side.

You'll have to do a little rearranging to make it work, but it's doable. The breaker for the compressor will have to move down and out of the tandem territory.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,053
Location
NJ
Why hasnt anyone suggested using a 3 wire cord from the stove to the existing recept?

New stoves today are providing the option of using 3 or 4 wire cords by simply changing the bonding jumper in the appliance. Why cant OP do that with the old stove?

Am I missing a stated detail?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
Why hasnt anyone suggested using a 3 wire cord from the stove to the existing recept?

New stoves today are providing the option of using 3 or 4 wire cords by simply changing the bonding jumper in the appliance. Why cant OP do that with the old stove?

Am I missing a stated detail?
A huge detail, you can't use a bare EGC as a neutral, & 3-wire is not allowed in new installs only existing.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
Since the panel is bottom fed, the notched bus stabs will be at the top of the panel, I see one way to free some space, get two 15-15 twins and install one in place of the single pole for the garbage disposal, then take the microwave circuit & move it to the same spot, then if the two 15A circuits are not a multiwire circuit, use the other twin to handle the other 2- 15A circuits above where the microwave circuit was, leaving 2 open spaces for a 2 pole breaker. Posting a photo of the panel interior will be helpful to see if the above idea will work.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,074
Location
Modesto, CA
Why hasnt anyone suggested using a 3 wire cord from the stove to the existing recept?

New stoves today are providing the option of using 3 or 4 wire cords by simply changing the bonding jumper in the appliance. Why cant OP do that with the old stove?

Am I missing a stated detail?
he has a n6-50r. thats the wrong receptacle for a stove. he would need a 10-50r (not allowed for new circuits) for a stove plus the 6-50r receptacle is fed w/ 2 hots & a bare ground in NM. thats not kosher either.
 