dwall174
Well-known member
I have a 100-amp Square-D QO series sub panel in my garage with only 2-spaces left.
It's currently only set-up as a 60-amp panel with 6ga. wire & a 60-amp main breaker due to a limited main house service entrance line.

I just picked up a Heat Storm 6000-watt heater for the garage.

The heater is 240-Volts & it draws 25-amps at full power & the owner's manual states to wire it to a 30-amp breaker.
The heater is a 3-wire connection no neutral so, it would be a pretty straight forward normal install. 2 - 10ga. wires, black/red & a 10ga. ground wire in 1/2" EMT conduit.
Being I only have two spaces left; I was wondering if I could run a 40-amp breaker with two 8ga. wires black & red with a 10ga. ground wire & a 10ga. white neutral wire through 1/2" EMT to another 70-amp sub panel like this one.


It would have one tandem 30-amp breaker for the heater, and two 15-amp 120-Volt breakers for a couple of extra 120v outlets.
It's currently only set-up as a 60-amp panel with 6ga. wire & a 60-amp main breaker due to a limited main house service entrance line.

I just picked up a Heat Storm 6000-watt heater for the garage.

The heater is 240-Volts & it draws 25-amps at full power & the owner's manual states to wire it to a 30-amp breaker.
The heater is a 3-wire connection no neutral so, it would be a pretty straight forward normal install. 2 - 10ga. wires, black/red & a 10ga. ground wire in 1/2" EMT conduit.
Being I only have two spaces left; I was wondering if I could run a 40-amp breaker with two 8ga. wires black & red with a 10ga. ground wire & a 10ga. white neutral wire through 1/2" EMT to another 70-amp sub panel like this one.


It would have one tandem 30-amp breaker for the heater, and two 15-amp 120-Volt breakers for a couple of extra 120v outlets.