Any concerns over this main panel?
earl84
Colona, CO
We're buying two rental properties, and am hoping to tap into a quick bit of knowledge from experts. Curious if there is any issues with this panel. It's in a 20 year old house.20240329_101238.jpg20240329_101248.jpg20240329_101233.jpg
mm08822
Nothing that will burn the place down.
This is a main panel correct?
cgrutt
Not an electrician so take this for what it's worth but I don't see any things I'd be really concerned about. Several double taps on the ground bus but looks like you have room to correct that if you want to. I'm not sure if that's a GFCI or ARC Fault breaker but shouldn't the neutral be running to the neutral bus?
LXCam
Looks fine except for where they connected the grounds to the neutral buss. I'd suggest you move it over to the ground buss but even as is, as long as everything else is properly grounded / bonded its not a hazard.
MovingAlong
Not sure stuffing every piece of Romex through one hole at the top would pass a current inspection, no sizing spec on that fitting, no strain relief, etc.. Not an electrician myself but I'd ask one about that. :dunno:
sparky 1971
Central Iowa
I don't see anything that would cause reason for concern as long as it's a main panel. Is there a main breaker feeding it from outside or is it a meter only?
I'm sure someone will chime in about the lack of a bushing on the feeder conduit, but it's really not that big of a deal.
PCustoms
VT
Grounds can be doubled if the bar is rated for it (square D I have are)
Main panel should be bonded, so this is not an isolated neutral buss and the ground can be landed there.
Only things I saw "wrong" are the missing bushing and I question if the top right breaker is a square D.
LXCam
Main panel should be bonded, so there is no "neutral" buss.
So you're commenting on something for absolutely no real reason. Ok lets go there. Was it confirmed this was the main service panel or possibly a sub panel. And if it is the main service panel (which I'm pretty certain it is) I know I can't see the neutral bonding screw.
PCustoms
VT
Excuse me? Not really sure where your attitude comes from, but as you say, let's got there.
I'm commenting on your comment explaining why that's not a isolated neutral buss and therefore not a problem.
The OP stated, in the title, that this is a main panel, so I am going with that premise.
If you have a concern that this isn't a main panel, or that's it's not bonded, then that would have been a great question/observation. Stating that the ground shouldn't be on the neutral buss is not
wyliesdiesels
Modesto, CA
Doubled up ground wires are fine on majority of panels.
E
earl84
Colona, CO
Thanks everyone for your expert input. I think I can rest easy knowing it's not going to start a fire the day we take possession.