Several double taps on the ground bus but looks like you have room to correct that if you want to. I'm not sure if that's a GFCI or ARC Fault breaker but shouldn't the neutral be running to the neutral bus?
Looks fine except for where they connected the grounds to the neutral buss. I'd suggest you move it over to the ground buss but even as is, as long as everything else is properly grounded / bonded its not a hazard.
I don't see anything that would cause reason for concern as long as it's a main panel. Is there a main breaker feeding it from outside or is it a meter only?
I'm sure someone will chime in about the lack of a bushing on the feeder conduit, but it's really not that big of a deal.
So you're commenting on something for absolutely no real reason. Ok lets go there. Was it confirmed this was the main service panel or possibly a sub panel. And if it is the main service panel (which I'm pretty certain it is) I know I can't see the neutral bonding screw.Main panel should be bonded, so there is no "neutral" buss.
Excuse me? Not really sure where your attitude comes from, but as you say, let's got there.So you're commenting on something for absolutely no real reason. Ok lets go there. Was it confirmed this was the main service panel or possibly a sub panel. And if it is the main service panel (which I'm pretty certain it is) I know I can't see the neutral bonding screw.
Doubled up ground wires are fine on majority of panels.Not an electrician so take this for what it's worth but I don't see any things I'd be really concerned about. Several double taps on the ground bus but looks like you have room to correct that if you want to. I'm not sure if that's a GFCI or ARC Fault breaker but shouldn't the neutral be running to the neutral bus?
This is incorrect. There is a neutral buss in main panels.Main panel should be bonded, so there is no "neutral" buss.
Thanks, I clarified my wordingThis is incorrect. There is a neutral buss in main panels.