Another plumbing question

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,391
Location
Texas
I’m finalizing my plans to plumb in the toilet at my place. At the end of the day, it’s going to be a 4” flange on the second floor located almost directly above the 4 inch stub for the septic coming out of the floor 12 feet below. There’s about an 18” horizontal offset between the flange and the septic stub.

I’ve convinced myself that there’s no problem using a couple of 45s to get it directly over the septic stub. With a 4”x4”x 2” 1/8 combo wye leading to the vent through the roof.

That’s it. The rest of the water will be going out of gray water vented system.

I’m continuously learning that I know nothing about plumbing. I’d wanted to check in to see if this layout would work.

Many thanks.
 
To avoid these ads, REGISTER NOW!

CraigStu

Well-known member
Joined
May 22, 2014
Messages
4,089
Location
Blacksburg, Va
You could also search for 'Plumbing for Dummies' or 'simplified plumbing' or 'beginning plumbing' or similar. Some L or HD stores have a book section and I have to think there is something there for you.
 
To avoid these ads, REGISTER NOW!

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
14,823
Location
Lebanon, TN
I think your plan for the 45's sounds solid if I understand it correctly. I think you are not supposed to use a combo-y in a drain stack, see image below. It's supposed to be a sanitary tee. I think you can use a sanitary tee in your layout in place of the comb-y, just need the right adapters / reducers.
efdd41ed4f19878.png
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,771
Location
Long Island
I think your plan for the 45's sounds solid if I understand it correctly. I think you are not supposed to use a combo-y in a drain stack, see image below. It's supposed to be a sanitary tee. I think you can use a sanitary tee in your layout in place of the comb-y, just need the right adapters / reducers.
I know a combo-y is designed for it to be laying down with the branch facing up. Not running vertically with the branch coming in the side. That's exactly what a sanitary tee is made for. In this situation though, with the side being a dry vent and not a wet stack, I don't know if it matters.
 