Gree Mini Split not Heating

alexrm78

New member
Joined
Nov 7, 2024
Messages
3
I had a 1.5 tonne / 18000 Btu mini split installed about 2.5 years ago and it has been fantastic. We don't run it a while lot, our garage is our home gym so in the summers we work out early enough that we don't need to cool it but in the winters, we do use the heat pump. We turned it on for the first time since last winter yesterday and everything seemed normal. The icon lit up on the air handler showing heating mode and the set temperature the fins partially opened and the outside unit spun up as it got ready to heat. After a couple of minutes the fins fully opened and the air handler started blowing air, again, as normal only the air was not hot. It was blowing room temperature air. I checked the filters and they are clean, I turned the breaker off for about an hour to reset the unit but nether of these have solved the issue. There are no error codes, everything else seems to be functioning perfectly normally, just no heat. Is there anything else I can check before I schedule an HVAC technician to come and diagnose?
 
To avoid these ads, REGISTER NOW!

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
It could be low on refrigerant and having a hard time warming up the indoor coil.

Did you try running it in cooling mode for a while ? If the charge is really low, it'll eventually throw a code : F0.

What's the model number ?

Just out of curiosity, where are you from ?
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,707
Location
Fargo, ND
My first guess would be low on charge.

When I worked as an HVAC tech, my first action to a poorly performing mini split was to check for leaks, then reclaim all the refrigerant and weigh in the proper amount. Before recharging it I would check the flares and give them a little snuggie. That would fix most of them.
 
OP
A

alexrm78

New member
Joined
Nov 7, 2024
Messages
3
It could be low on refrigerant and having a hard time warming up the indoor coil.

Did you try running it in cooling mode for a while ? If the charge is really low, it'll eventually throw a code : F0.

What's the model number ?

Just out of curiosity, where are you from ?
Thank you for taking the time to reply. I ran it for a few minutes in cooling mode and it felt like the air was not cooling either (although it was about 60° in the garage at the time). I will try running it in cooling mode for longer today and see if that error pops up.

The model number is:- LIVV18HP230V1AH

I am in Southern California.
 
To avoid these ads, REGISTER NOW!
OP
A

alexrm78

New member
Joined
Nov 7, 2024
Messages
3
My first guess would be low on charge.

When I worked as an HVAC tech, my first action to a poorly performing mini split was to check for leaks, then reclaim all the refrigerant and weigh in the proper amount. Before recharging it I would check the flares and give them a little snuggie. That would fix most of them.
Thank you for taking the time to respond, I'll schedule an appointment with an HVAC technician to come out and diagnose.
 

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
Thank you for taking the time to reply. I ran it for a few minutes in cooling mode and it felt like the air was not cooling either (although it was about 60° in the garage at the time). I will try running it in cooling mode for longer today and see if that error pops up.

The model number is:- LIVV18HP230V1AH

I am in Southern California.

You can also check the smaller copper line coming out of the outside unit. Frost on it when the unit is running in A/C could be another indication of a low charge.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,992
Location
Peace Valley,mo
There is a reversing valve that is energized i heating and de energized in cooling and defrost. Difference between the two modes defrost turns the outside fan off. If the unit cools and doesn't heat the reversing valve might be moving but not all the way. In heat turn thermostat way up 80° wait 5 minutes they go outside turn power off to unit should here a sushing sound when unit shuts down unit reversing valve goes back to cooling.
 