Arc & fire
Copymutt
Colorado
Headed to a buddy’s shop tomorrow.
He lost a dedicated 20A circuit to the garage. Plugged in the compressor and the GFCI outlet went up in flames as well the breaker. I saw the outlet was back stabbed & thought perhaps the starting surge from the compressor caused the minimal physical contact to arc. Doesn't explain the breaker though. He Replaced both and it did the same thing.
I’ll ohm the run for a dead short and check the voltage and polarity at both the breaker and the outlet feed.
What could I be missing?I’m leaning toward a bad starting cap on the compressor.
rlitman
Long Island
...the GFCI outlet went up in flames as well the breaker. I saw the outlet was back stabbed...
GFCI outlets are never back stabbed. They use back wire clamps, which are superior to side wire clamps in just about every way.
Bad caps are supposed to fail open, but they can fail short. Could also be a failed coil in the motor, or something more innocuous, but you're right in that there's got to be a dead short in there somewhere.
BrandonV
Arizona
Did the breaker actually trip? I assume not. Imagine if a dead short didn't trip a breaker... you'd have some scary stuff on your hands.
Call me paranoid but that's why I like British style of wall plug.
rlitman
Long Island
You're missing the point of Kirchoff's law. Adding a fuse at the plug doesn't change the short-circuit current seen at the panel, or anywhere else in the circuit for that matter. In fact, on a British ring circuit, there's usually quite a bit more energy available at a typical plug than there would be at a residential American 20A outlet. However, the short-circuit current is NOT limited by the breaker or fuse size. It's limited by the impedance of the circuit, and at a 20A outlet that's physically close to a large commercial panel, the impedance could be very low, leading to the potential for enormous currents.
BrandonV
Arizona
My point was that it's more important to have an overcurrent device that actually functions, rather than a breaker just sitting there doing nothing. Fuses tend to always work (like the ones in almost every BS 1363), whereas breakers don't always perform as expected.
rlitman
Long Island
I guess. But my personal experience with thermo-magnetic breakers has been very good (barring typical coordination issues). To be fair, I have no personal experience with FPE. I've also seen the results of the wrong fuse being used, and it may not be so pretty, but yes, the correct fuse should be safe.
I was watching a video by Big Clive the other day about a failed breaker given to him, and it had me floored that the UK would allow a breaker to be made of thermoplastic, and have windows that allowed a flashover to travel from one breaker to it's two neighbors and trash three breakers with a single fault. None of that would fly on this side of the pond.
BrandonV
Arizona
So I think circuit breakers have a good track record indoors... my experience with bad circuit breakers has been those exposed to the elements for decades.
Thank whoever thought putting them outside in Arizona was a good idea...
wyliesdiesels
Modesto, CA
HP rating of compressor as listed on motor nameplate?
and the GFCI outlet went up in flames as well as the breaker.
literally 🔥 ??
GFCIs do not have backstab terminals....so unless the screws were loose, this is unlikely culprit
where on the breaker did the flames come from?
no such thing as polarity on AC. even if hot and neutral were reversed it would still work and not cause the issue you described.
even a dead short should just cause the breaker to insta-trip due to its magnetic trip mechanism.... ive caused dead shorts on circuits and the breaker simply trips...
wyliesdiesels
Modesto, CA
unless the breaker is a shitsco (zinsco) or Fire Pacific Electric (FPE), or very worn out EOL breaker, its unlikely the breaker wouldnt have tripped. and catching on fire is even more unheard of... theres nothing in a breaker that would cause it to erupt in flames especially considering they are made of bakelite. Ive literally seen melted breakers that never had flames erupt from them....
wyliesdiesels
Modesto, CA
strange we dont have that issue here in california where the majority of houses and even commercial buildings have meter mains... very rare to find a track home with a subpanel inside.
BrandonV
Arizona
Usually the issue is slow tripping not fires.
I assume its because of the dust storms here over decades of exposure. Last breaker I cut open was legitimately filled with sand.
KenC
oklahoma
Back in the 80s I had a zinsco 2pole 40a fail spectacularly. It was hooked to my welder circuit in the shop. I struck an arc and the breaker blew a hole thru both halves! Huge hole through the body of the breaker. Huge arc flash, but mostly hidden in the panel and lots of smoke but no after fire. I was working 12-15 ft from the panel and it sounds like a bomb went off.
My guess is that the contacts were bad/high resistance, it did'nt trip from heat or load but created enough to physically damage the case.
C
Copymutt
Colorado
Findings,
Yes the GFCI had a back stab connection.
total disregard for basic wiring. Compressor pulls 15amp. Also connected was a 1500 watt heater. GFCI and breakers were 20 amp, but wire was 14 ga. 🙀. In the process of repair a black hot separate black wire was wire nutted to ground🫣. Lots of other wiring issues in the shop. So much for his neighbors knowledge as he wired the shop. Wired it correctly, tested it & advised to get some 12 ga. & I’d install that.
dscheidt
Im guessing youre mixing up push-wire terminals aka back stab, with backwire.
I have never seen a GFCI receptacle with back stab terminals
Post a pic of the GFCI
they were common in the 80s. The ones I took out of my basement were backstab only, no screw pressure terminals at all. I forget who made them, but it was one of the biggies. I suspect the UL listing requirements changed, and it's no longer allowed. probably about the same time the nec started limiting stab connections to 14 awg only.
PCustoms
VT
That would immediately trip.
You need to post pictures, or just close the thread. Further discussion it's pointless.
wyliesdiesels
Modesto, CA
If a GFCI lasted close to 40yrs that would be really surprising.
It wouldnt be the NEC limiting the connections. Thats entirely up to the manufacturer and NRTL listing.
BrandonV
Arizona
Well you're expecting people to test them weekly right? ;)
Never seen one that accepted backstab connections and I have a weird quirk of collecting vintage GFCIs. Oldest I ever saw was a 3M (yes 3M branded) one from the 1970s that was in use until a year or two ago. Worked great except for the tripping part!
I'd be interested to see or acquire a GFCI which accepts backstabbed connections for my collection. Considering people are still selling recalled GFCIs on eBay 20+ years later... I'd believe anything.