Is there some reason for not running a second circuit? Especially since it is that close. If further away I'd recommend a sub panel and separate circuits from there.
Ease of just using one (not at the same time) circuit not 2. The range and compressor wont be used at the same time, ever. And the compressor isnt going to be used non stop.
The sub panel is in the garage. The run from the house to garage(shop) panel is about 75ish feet. At least they did the run in the correct wire size.
If it comes down to it, I can just get a less hp motor that draws less power that spins the same rmp needed to run the pump. Which is 3450 rpm, which are available for relatively cheap.
The more I look in the black box on the compressor, the more I wonder how this guy had this wired. Only 1 lug has been touched to hook this up. I can tell by the screw driver marks. One of the lugs is brand new, hasn't been touched. So bizarre.
Anyways, I understand what you guys are saying about the receptacle, and just hard wire it. That would mean I would need 2 more additional 50 amp dual pole breakers and I don't have enough room in the panel for that, with the other circuits in the panel. That would mean I'd have 3-50 amp cb's in the panel along with everything else. As it is, I have to swap over the plasma cutter and welder when I need the other one. At most id be running compressor and plasma at the same time. Not compressor and range, or compressor and welder.