WOW WOW WOW :eek::wtf::shocking:

forget the oven/micro combo appliance

your panels need some major work.... where do I begin?

the shitsco main needs to go....

That subpanel just needs to be ripped out and start over....
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,006
Location
Modesto, CA
oops. Deleted duplicate.

And edited previous post.

Here’s the sub panel.

IMG_5336.jpeg
this subpanel is a major hazard

get rid of this panel and get a new one

uninsulated neutral cloth wrapped SEU needs to go

the top 20a breaker has #14... the bottom 30a has #12.... not kosher...

then theres that hack job of neutral splices with a split bolt....

no way was the guy that did this a chief electrical inspector.... way too many issues here...

is this subpanel on a detached building?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,006
Location
Modesto, CA
Got it. Thanks.

I don’t see any red stripe on either black cable.

I’m guessing if I pull a permit, I’m opening up a whole can of worms with a city inspection. As in the possibility of having to rewire the entire house.

Am I thinking correctly?

Is there an opportunity to pull split phase from one of those spares in the subpanel?


Or just abandon ship? Pretty sure I can sell this microwave/convection oven and I picked up a Restore for a profit.



IMG_5323.jpeg
that wire is way too large for that GFCI.... its another SER feeder. im guessing someone "trimmed" the strands to make it fit.... this needs to be fixed as well...
 
To avoid these ads, REGISTER NOW!
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,282
Location
Texas
this subpanel is a major hazard

get rid of this panel and get a new one

uninsulated neutral cloth wrapped SEU needs to go

the top 20a breaker has #14... the bottom 30a has #12.... not kosher...

then theres that hack job of neutral splices with a split bolt....

no way was the guy that did this a chief electrical inspector.... way too many issues here...

is this subpanel on a detached building?

I’m pretty sure the top wire is 12 AWG. But I’ll double check. The guy who replaced this panel said he had to replace the previous panel because it was dangerous. All of this used to be feeding a pool and hot tub and pool heater. All that stuff is gone.

Edit to add – it’s on the same building.
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,282
Location
Texas
that wire is way too large for that GFCI.... its another SER feeder. im guessing someone "trimmed" the strands to make it fit.... this needs to be fixed as well...

I’m just going to cap the wires and put a cover plate back on it. Maybe pull it back up into the attic and put in a junction box and stick it in there.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,006
Location
Modesto, CA
I’m pretty sure the top wire is 12 AWG. But I’ll double check. The guy who replaced this panel said he had to replace the previous panel because it was dangerous. All of this used to be feeding a pool and hot tub and pool heater. All that stuff is gone.

Edit to add – it’s on the same building.
yeah looks like 14 on the jacket but i could be wrong...
 