Breaker feeding Disconnect for HVAC

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
I'm getting a new heat pump system, and the air handler in the attic wants 240v 15amps. Space is at a premium in my main panel so I need to use a triplex breaker, but I'm having trouble finding a 20-15/15-20 Siemens breaker. I can find a 20-20/20-20 triplex breaker no problem.
A 30 amp (two 15 amp fuses) quick disconnect is required at the air handler, can i use the 20 2 pole breaker to feed the 15/15 amp disconnect since the air handler is protected by the fuses?

My other thought is (let me know if this is crazy in some way! Just seems like a lot parts to go from 20 to 15 amps?!?) put a sub panel in the attic next to the quick disconnect, fed it off of the 20a 2 pole triplex breaker in the main panel. Than i can put a 15a 2 pole in the sub panel to feed the quick disconnect. This also has a benefit of i can also put a single pole breaker in the sub panel to power to the attic lights

Little background on current system-
20 amp 1 pole breaker feeding air handler/lights in attic
40 amp double pole breaker feeding condenser unit outside (breaker is a triplex 20-40/40-20). I plan to reuse this circuit for heat pump mounted outside
 
Last edited:
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,084
Location
Modesto, CA
I'm getting a new heat pump system, and the air handler in the attic wants 240v 15amps. Space is at a premium in my main panel so I need to use a triplex breaker, but I'm having trouble finding a 20-15/15-20 Siemens breaker. I can find a 20-20/20-20 triplex breaker no problem.
A 30 amp (two 15 amp fuses) quick disconnect is required at the air handler, can i use the 20 2 pole breaker to feed the 15/15 amp disconnect since the air handler is protected by the fuses?

you dont add up the poles to get 30a. 240v 15a is a 15a circuit.

As far as using a 30a disco fed by a 20a 240v breaker, it depends on the wire size and MCA listed on the air handler. Have a screenshot?

My other thought is (let me know if this is crazy in some way! Just seems like a lot parts to go from 20 to 15 amps?!?) put a sub panel in the attic next to the quick disconnect, fed it off of the 20a 2 pole triplex breaker in the main panel. Than i can put a 15a 2 pole in the sub panel to feed the quick disconnect. This also has a benefit of i can also put a single pole breaker in the sub panel to power to the attic lights

you dont want a subpanel in an attic.

Little background on current system-
20 amp 1 pole breaker feeding air handler/lights in attic
40 amp double pole breaker feeding condenser unit outside (breaker is a triplex 20-40/40-20). I plan to reuse this circuit for heat pump mounted outside

I wouldnt want the air handler on the same circuit as the lights but to each their own. Regardless, you wont be able to keep feeding the lights when you convert this air handler circuit to 240v unless they ran 3-wire (2 hots neutral and ground). So you will have to run a new circuit for the AH...
 
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
Here is the spec sheet. I guess the quick discount would be two 15 amp fuses, not 30. I can keep the lights on a different circuit, the attic lights are only two 24" Leds
 

Attachments

  • specs.png
    specs.png
    249.3 KB · Views: 8

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,319
Location
SE MI
A 30 amp (two 15 amp fuses) quick disconnect is required at the air handler, can i use the 20 2 pole breaker to feed the 15/15 amp disconnect since the air handler is protected by the fuses?
Yes. You can always install a smaller breaker/fuse "downstream". The feed to the disconnect will still have to be 12/2.

Around here, a NEMA 5-15R "convivence" outlet is also required near the compressor.
 
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
Thanks everyone. The system plan has been changed up to a Diakin DFVE60, which is 120v, wanting a 20 amp breaker.
Any suggestions on what to use for disconnect in the attic? Is it as simple as using a single pole light switch mounted by the unit? Or use a cord to a receptacle?
 

Attachments

  • Screenshot 2025-09-03 at 2.14.45 PM.png
    Screenshot 2025-09-03 at 2.14.45 PM.png
    216.6 KB · Views: 8

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,855
You can get motor rated switches for stuff like that. It looks like a light switch but more heavy duty. Usually see them near furnaces or on small under counter hot water tank.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,543
Location
VT
Thanks everyone. The system plan has been changed up to a Diakin DFVE60, which is 120v, wanting a 20 amp breaker.
Any suggestions on what to use for disconnect in the attic? Is it as simple as using a single pole light switch mounted by the unit? Or use a cord to a receptacle?

Get a non-fused AC disconnect
 
To avoid these ads, REGISTER NOW!
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
I think i like the non fused disconnect over the switch since I can see the actual air gap, or not accidentally bump the switch on without realizing it. I found this one on HD:

Since it's 120v, do I only connect the load supply to the disconnect and wire nut the neutrals? Or connect the load and neutral to each leg of the disconnect so they both get disconnected when the lever is pulled out?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,084
Location
Modesto, CA
I think i like the non fused disconnect over the switch since I can see the actual air gap, or not accidentally bump the switch on without realizing it. I found this one on HD:

Since it's 120v, do I only connect the load supply to the disconnect and wire nut the neutrals? Or connect the load and neutral to each leg of the disconnect so they both get disconnected when the lever is pulled out?
dont need to disconnect the neutral. just wire nut them
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,836
Location
Southern Oregon
I think i like the non fused disconnect over the switch since I can see the actual air gap, or not accidentally bump the switch on without realizing it. I found this one on HD:
I like the Square D disconnects. QOTR200TRCP
simple switch, no pullout to fumble with.
About $21 at Home Depot.
 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,726
Location
S.E. TEXAS
Stick with a 240v system. Do it right
They do make a 230/208 in that same model op Posted
Diakin DFVE60
I too would go with a 240 volt model. Not sure if that makes it right but I like 240 to keep loads balanced on each leg easier.
 