I'm getting a new heat pump system, and the air handler in the attic wants 240v 15amps. Space is at a premium in my main panel so I need to use a triplex breaker, but I'm having trouble finding a 20-15/15-20 Siemens breaker. I can find a 20-20/20-20 triplex breaker no problem.
A 30 amp (two 15 amp fuses) quick disconnect is required at the air handler, can i use the 20 2 pole breaker to feed the 15/15 amp disconnect since the air handler is protected by the fuses?
My other thought is (let me know if this is crazy in some way! Just seems like a lot parts to go from 20 to 15 amps?!?) put a sub panel in the attic next to the quick disconnect, fed it off of the 20a 2 pole triplex breaker in the main panel. Than i can put a 15a 2 pole in the sub panel to feed the quick disconnect. This also has a benefit of i can also put a single pole breaker in the sub panel to power to the attic lights
Little background on current system-
20 amp 1 pole breaker feeding air handler/lights in attic
40 amp double pole breaker feeding condenser unit outside (breaker is a triplex 20-40/40-20). I plan to reuse this circuit for heat pump mounted outside
A 30 amp (two 15 amp fuses) quick disconnect is required at the air handler, can i use the 20 2 pole breaker to feed the 15/15 amp disconnect since the air handler is protected by the fuses?
My other thought is (let me know if this is crazy in some way! Just seems like a lot parts to go from 20 to 15 amps?!?) put a sub panel in the attic next to the quick disconnect, fed it off of the 20a 2 pole triplex breaker in the main panel. Than i can put a 15a 2 pole in the sub panel to feed the quick disconnect. This also has a benefit of i can also put a single pole breaker in the sub panel to power to the attic lights
Little background on current system-
20 amp 1 pole breaker feeding air handler/lights in attic
40 amp double pole breaker feeding condenser unit outside (breaker is a triplex 20-40/40-20). I plan to reuse this circuit for heat pump mounted outside