Lights flickering on another circuit.

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,129
Location
LI, NY
Had sparky out again and moved to an unused area. At this point I will be replacing the entire electrical panel.

Any idea what I’m looking out price wise ?

What is the best panel ?

Thanks IMG_1677.jpeg
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,043
Location
NJ
What's the history of the previous problem? What was "fixed"?

Pics of outside needed. How weathered is the meter pan and service entrance conductors?
Inspection? If yes, need an outside disco or metermain. What year was this service put in/upgraded? May need to upgrade grounding electrodes/bonding.

The fix may not be a new panel, but this one needs some attention at a minimum anyway.
How high is the centerline of the main cb above the floor in this pic?
I would put a 200amp 40 space, 60circuit panel. Clean up that birds nest. That leaves you with 16 circuits open.
Probably replace 1/2 the cbs. Some are old Murrays. Many look recently installed.

A sub-panel could remove some of this congestion. Not sure how practical now that may be.

Need to define the full scope of work before anyone could provide any $$. And of course, if not from LI, any costs you receive on GJ are mostly useless.
 
OP
J

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,129
Location
LI, NY
What's the history of the previous problem? What was "fixed"?

Pics of outside needed. How weathered is the meter pan and service entrance conductors?
Inspection? If yes, need an outside disco or metermain. What year was this service put in/upgraded? May need to upgrade grounding electrodes/bonding.

The fix may not be a new panel, but this one needs some attention at a minimum anyway.
How high is the centerline of the main cb above the floor in this pic?
I would put a 200amp 40 space, 60circuit panel. Clean up that birds nest. That leaves you with 16 circuits open.
Probably replace 1/2 the cbs. Some are old Murrays. Many look recently installed.

A sub-panel could remove some of this congestion. Not sure how practical now that may be.

Need to define the full scope of work before anyone could provide any $$. And of course, if not from LI, any costs you receive on GJ are mostly useless.
Thanks Very much. The outside meter box was replaced after hurricane sandy so about 2012. I got a new meter cabinet, and new piping up to the customer side of the turnbuckles.

What's the best brand of panel?

Not sure what the disco is or the metermain.

THe sparky said the buss bar in my panel was the issue both times. Previously the issue was similar but worse. Mt lights were pulsing as was the exhaust fan in the bathroom. This time is was lights flickering in the kitchen. First time you could hear a buzzing in the panel and see arcing. This time there was no noise but he said it was just not as bad but the same issue. He installed a split breaker above and it solved the issue.

After the first fix he said if it happens again I suggest a new panel.

Do you think that is wrong?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,997
Location
Central Iowa
Without seeing everything and knowing what is required by the AHJ, nobody is going to be able to tell you much. There is one place I can think of where in about a miles drive I can go through four jurisdictions, city, county, state, and another city and depending on where and which side of the road you are on, the job could go from $2000.00 for a panel swap up to $15000.00 for a service update if you are lucky enough to have a single story house with an unfinished basement. If not, the price will only go up.
 

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,837
Get that mess cleaned up before committing to a new panel.

There's no best brand. Square D and Siemens are the most common around here. You might be limited to what fits that space.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,400
Location
VT
Get that mess cleaned up before committing to a new panel.

Why would you pay an electrician to come in and tidy up you existing panel to turn around and pay him to rip it all out and re-install in a new panel?
 
OP
J

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,129
Location
LI, NY
Get that mess cleaned up before committing to a new panel.

There's no best brand. Square D and Siemens are the most common around here. You might be limited to what fits that space.
Clean up how ? What exactly?
 
OP
J

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,129
Location
LI, NY
What's the history of the previous problem? What was "fixed"?

Pics of outside needed. How weathered is the meter pan and service entrance conductors?
Inspection? If yes, need an outside disco or metermain. What year was this service put in/upgraded? May need to upgrade grounding electrodes/bonding.

The fix may not be a new panel, but this one needs some attention at a minimum anyway.
How high is the centerline of the main cb above the floor in this pic?
I would put a 200amp 40 space, 60circuit panel. Clean up that birds nest. That leaves you with 16 circuits open.
Probably replace 1/2 the cbs. Some are old Murrays. Many look recently installed.

A sub-panel could remove some of this congestion. Not sure how practical now that may be.

Need to define the full scope of work before anyone could provide any $$. And of course, if not from LI, any costs you receive on GJ are mostly useless.
Clean up the birds nest how? thanks
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,043
Location
NJ
Clean up the birds nest how? thanks
There is so much work involved to clean this up that a new and larger panel might as well be part of it and would make it easier. Best chance of a nice clean job when finished.
  • Many cables enter w/o connectors.
  • Many cables aren't stripped of jacket after entering panel.....not a code issue, but makes conductor routing a PIA.
  • Could put the new main cb on the bottom to eliminate 3 large conductors filling the gutters.
  • I would raise the new longer panel up several inches to gain cable/conductor length to aid in routing the conductors neatly inside the panel. The newer panel may also have a greater length to effectively accomplish this.

I would use a Siemens panel with copper buss. Inspect which existing cbs could be re-used and others discarded/replaced. Re-using old could be perfectly fine but, if any were damaged at the buss connection, you would be subjecting the new panel's buss to the same condition you have now.

Would this work be inspected? (Determines if any newer NEC requirements have to get done.)

1766156048981.png
1766156107220.png
 
OP
J

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,129
Location
LI, NY
There is so much work involved to clean this up that a new and larger panel might as well be part of it and would make it easier. Best chance of a nice clean job when finished.
  • Many cables enter w/o connectors.
  • Many cables aren't stripped of jacket after entering panel.....not a code issue, but makes conductor routing a PIA.
  • Could put the new main cb on the bottom to eliminate 3 large conductors filling the gutters.
  • I would raise the new longer panel up several inches to gain cable/conductor length to aid in routing the conductors neatly inside the panel. The newer panel may also have a greater length to effectively accomplish this.

I would use a Siemens panel with copper buss. Inspect which existing cbs could be re-used and others discarded/replaced. Re-using old could be perfectly fine but, if any were damaged at the buss connection, you would be subjecting the new panel's buss to the same condition you have now.

Would this work be inspected? (Determines if any newer NEC requirements have to get done.)

1766156048981.png
1766156107220.png
I was planning on using a licensed electrician and since replacing existing I did not plan on getting it inspected.

I will have the work done to the current code.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,651
Location
Long Island
...The outside meter box was replaced after hurricane sandy so about 2012. I got a new meter cabinet, and new piping up to the customer side of the turnbuckles...
Ok, so you have a bypass meter pan (current requirements for some time). Is there a disconnect or breaker outside by the meter?

mm0822 has the best plan of action. As for re-using breakers, the more I think about it, the less I like the idea. You have multiple bus positions that are failing, which means both your bus AND the breakers clamped onto it are corroding. And with the way that residential breakers hold onto the bus bars, there's just no good way to repair corrosion. The best the manufacturer will recommend is to replace parts and be careful not to wipe off the tiny dab of grease placed on the new breakers at the factory, because it's the magic that keeps things working.

Is your panel on an exterior unconditioned garage wall? Does it pick up condensation? I'm wondering if there's something about it's environment that's harsher than a typical panel's that led to its premature failure (since it isn't antique). If it were me replacing it, I'd stick a corrosion inhibitor in there before it's closed up.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,043
Location
NJ
I was planning on using a licensed electrician and since replacing existing I did not plan on getting it inspected.

I will have the work done to the current code.
Technically, a like for like replacement is a repair and shouldn't require an inspection. (I had an inspector tell this was wrong b/c it is a main panel. BS, I say! Only had it inspected b/c it was part of a house sale.)

Going to a larger space panel is trivial, IMO. However, the new panel won't have an inspection sticker on it. (That's how my customer's repair got flagged.) Not a big deal for now.

Replacing all of the cbs is the easiest way to establish a new baseline......leaves no doubts. Since they are all standard cbs (no electronic versions), cost is trivial.
 

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
603
Location
Boston 'burbs
Technically, a like for like replacement is a repair and shouldn't require an inspection. (I had an inspector tell this was wrong b/c it is a main panel. BS, I say! Only had it inspected b/c it was part of a house sale.)

Going to a larger space panel is trivial, IMO. However, the new panel won't have an inspection sticker on it. (That's how my customer's repair got flagged.) Not a big deal for now.

Replacing all of the cbs is the easiest way to establish a new baseline......leaves no doubts. Since they are all standard cbs (no electronic versions), cost is trivial.
Depends on your jurisdiction. If you replace a duplex receptacle or single pole switch or even a circuit breaker in MA, a permit is required. I have a friend who is an electrician and the State board is fining him $500 for replacing a circuit breaker without a permit....I don't really agree with this, but it's what we have....
 

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,837
Why would you pay an electrician to come in and tidy up you existing panel to turn around and pay him to rip it all out and re-install in a new panel?

Why replace a panel for no reason? Once they start digging past that mess of wires They'll be able to see what condition the panel is actually in and either continue cleaning it up or say yeah this is junk it needs to be replaced.
 

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,837
Clean up how ? What exactly?

Have a look at some of the other panel pictures people have posted in the forum. You don't have cables with their jackets on them going that far in, there's a bunch of marettes in there, wires that are way too long and should be cut back rather then bent back and forth to take up the length. If there are any circuits in there that are no longer used the wires should be pulled out etc.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,043
Location
NJ
Depends on your jurisdiction. If you replace a duplex receptacle or single pole switch or even a circuit breaker in MA, a permit is required. I have a friend who is an electrician and the State board is fining him $500 for replacing a circuit breaker without a permit....I don't really agree with this, but it's what we have....
Whatever the local requirements are, you need to live by or take on risk.
A permit required to replace a cb would easily triple the cost of a simple repair.

What great way to loose jobs. You know the next guy called won't pull a permit.

And how did the permit policia find out?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
Guessing it has an aluminum buss. They get corroded. Here we could replace that panel without adding an exterior disconnect.

Seeing that rat's nest would make me question every single connection in the panel. It screams of years of DIY.
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,043
Location
NJ
Guessing it has an aluminum buss. They get corroded. Here we could replace that panel without adding an exterior disconnect.

Seeing that rat's nest would make me question every single connection in the panel. It screams of years of DIY.
And everything else in the house.
 
OP
J

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,129
Location
LI, NY
Guessing it has an aluminum buss. They get corroded. Here we could replace that panel without adding an exterior disconnect.

Seeing that rat's nest would make me question every single connection in the panel. It screams of years of DIY.
I have been living here since 1991 and I have never had anyone but a licensed electrician work on the box or any electric in my home.
 

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,571
Location
Minneapolis, MN
Whatever the local requirements are, you need to live by or take on risk.
A permit required to replace a cb would easily triple the cost of a simple repair.
How much does an electrical permit cost in NJ? Here in Minnesota the minimum permit cost is $81 which would probably be the only cost for a permit to change a breaker. I don't know of any electrician that would change a breaker for a third of $81.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,043
Location
NJ
How much does an electrical permit cost in NJ? Here in Minnesota the minimum permit cost is $81 which would probably be the only cost for a permit to change a breaker. I don't know of any electrician that would change a breaker for a third of $81.
3x 81.....not 81/3.

Im talking about the extra time to fill it, drop it off, pay, schedule inspection.....vs just git it done and be done.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,997
Location
Central Iowa
I have been living here since 1991 and I have never had anyone but a licensed electrician work on the box or any electric in my home.
Licenses don't mean much other than in most cases, a test was passed. I would ask to see that license. There are plenty of people with a drivers license that can't drive, this is no different.
 
Last edited:

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,997
Location
Central Iowa
In town, we are supposed to get a permit for everything. Where the state has jurisdiction we are supposed to get a permit for anything that requires getting in the panel, but I doubt that would included changing a breaker. The only time I get a permit is when the POCO is involved and they won't turn the power on without an inspection and release. Permits and inspections are a pain in the ****
 

rmanrman

Well-known member
Joined
Nov 2, 2012
Messages
385
In Nj a new service has to be up to today standards. New panel will need afci breakers for every circuit. Outside needs a disconnect either with the meter pan or separately.
Cost is approximately $3000 to 3500.
Best panel In my experience is square D QO
Not homeline sold inbig box stores
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,651
Location
Long Island

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,043
Location
NJ
In Nj a new service has to be up to today standards. New panel will need afci breakers for every circuit. Outside needs a disconnect either with the meter pan or separately.
Cost is approximately $3000 to 3500.
Best panel In my experience is square D QO
Not homeline sold inbig box stores
A new service sure with surge suppressor and gfci recept near panel, too.

AFCIs not required on an upgrade if branch circuits not altered.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
In town, we are supposed to get a permit for everything. Where the state has jurisdiction we are supposed to get a permit for anything that requires getting in the panel, but I doubt that would included changing a breaker. The only time I get a permit is when the POCO is involved and they won't turn the power on without an inspection and release. Permits and inspections are a pain in the ****
Glad I'm not the only one!
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,997
Location
Central Iowa
A new service sure with surge suppressor and gfci recept near panel, too.

AFCIs not required on an upgrade if branch circuits not altered.
We have one city with a rouge AHJ that requires AFCI's for panel changes. I've never changed a panel there, so have no idea if it's an actual ordinance or some prickstick that doesn't know any better, but I've heard it from two people, one of which is a real electrical inspector from another jurisdiction that lives in the city in question. He found out first hand when he swapped out his own panel.
 
OP
J

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,129
Location
LI, NY

A new service sure with surge suppressor and gfci recept near panel, too.

AFCIs not required on an upgrade if branch circuits not altered.
Why a gfci receptacle near the panel ? I saw this somewhere and now you mention it. Whats the reason ?
 
OP
J

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,129
Location
LI, NY
How much work have you had done? If they're who created that mess.. yikes.
Lower level (slab is lowest) House was rewired after hurricane sandy. Had 4’ of water in the house. Previous renovated kitchen required significant power upgrades. That’s it.
 
OP
J

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,129
Location
LI, NY
So from what I am reading and AFCI breaker would have popped when there was arcing to protect from a potential fire ? Is there a down side from using all AFCI breakers ?
 
OP
J

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,129
Location
LI, NY
So this is what I should show the guy? Pic Found on line Looks like a ton of work to get from where I am to here. Other than it looks GJ pretty as long as it’s safe and functional to I need to burn $ to pretty up my panel ? IMG_1699.jpeg
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,043
Location
NJ
Why a gfci receptacle near the panel ? I saw this somewhere and now you mention it. Whats the reason ?
You dont/won't have a new service as in new construction, current codes, no grand-fathering of previous (lesser) requirements.

You will have a repair and at best, it will meet prior code requirements but not today's code.

Recept is part of recent code changes.
 