Hi all,
I'm wiring in my detached garage and may have put the cart before the horse a little. I've trenched and buried four 1/0 conductors to feed a 100 Amp panel (I realistically will probably only push out 50A max) inside the shop. The trench goes ~100 feet to the meter/main disconnect combo box on the side of my home. The main disconnect breaker, and the panel inside my home which it feeds, are also both 100A. Now that I'm nearly to the point of terminating my feeders, I've discovered that a new breaker for my box with lugs rated for dual conductors is either nonexistent or very hard to find. Here are my options as far as I can tell, please let me know if you have a better suggestion:
1. Find a breaker that fits my box with dual lugs-one set of feeders for the home panel and another for the shop's. This is my preferred route assuming one exists.
2. use something like this and/or Polaris taps and tap into the existing home panel feeders. Things would get pretty tight in that box but it could be done. more importantly, I believe this is still technically double tapping, though I'd be surprised if that main disconnect saw over 100 sustained amps even from the home and shop combined.
3. feed the shop via the home panel. No, the home panel isn't a feed-through, and I'm not sure the shop feeder lines would even reach it without being extended, but the shop's panel is the feed-through version of the home's panel (Homeline 24 slot) and it seems like the guts are interchangeable. This would obviously be very labor intensive, but at the end of the day would still be doable.
4. get a different meter combo box that's better set up for what I'm trying to do. This is the most straight forward but least preferable from a budgetary standpoint.
Thanks in advance for any suggestions. Here's a pic of my meter combo box for reference (The shop feeder lines would be coming in from the bottom):
I'm wiring in my detached garage and may have put the cart before the horse a little. I've trenched and buried four 1/0 conductors to feed a 100 Amp panel (I realistically will probably only push out 50A max) inside the shop. The trench goes ~100 feet to the meter/main disconnect combo box on the side of my home. The main disconnect breaker, and the panel inside my home which it feeds, are also both 100A. Now that I'm nearly to the point of terminating my feeders, I've discovered that a new breaker for my box with lugs rated for dual conductors is either nonexistent or very hard to find. Here are my options as far as I can tell, please let me know if you have a better suggestion:
1. Find a breaker that fits my box with dual lugs-one set of feeders for the home panel and another for the shop's. This is my preferred route assuming one exists.
2. use something like this and/or Polaris taps and tap into the existing home panel feeders. Things would get pretty tight in that box but it could be done. more importantly, I believe this is still technically double tapping, though I'd be surprised if that main disconnect saw over 100 sustained amps even from the home and shop combined.
3. feed the shop via the home panel. No, the home panel isn't a feed-through, and I'm not sure the shop feeder lines would even reach it without being extended, but the shop's panel is the feed-through version of the home's panel (Homeline 24 slot) and it seems like the guts are interchangeable. This would obviously be very labor intensive, but at the end of the day would still be doable.
4. get a different meter combo box that's better set up for what I'm trying to do. This is the most straight forward but least preferable from a budgetary standpoint.
Thanks in advance for any suggestions. Here's a pic of my meter combo box for reference (The shop feeder lines would be coming in from the bottom):