gagecalman
Well-known member
Sorry this is a long read but thanks for taking the time to read and teach me.
I'm helping a friend replace my gas furnace and AC here in Maryland. Furnace is in basement.
He has his own HVAC company but does mostly commercial work. He does do residential but he doesn't go looking for it. I've done most of the work because he's been very busy. I probably should have thought this out a little better but it's a learning experience! Feel like it's Groundhog day.
This is what we installed.
Furnace Goodman GR9S960603BN. 60k btu.
Condenser Goodman GLXS5BA3010. 2-1/2 ton.
Coil Goodman CAPTA3026B3. 2-1/2 ton. (Pressure drop at 950 cfm: DRY 0.20, WET 0.25).
Filter AprilAire 2410 MERV 13 16" x 25". (Pressure drop at 950 cfm: 0.14).
I posted already about the bushing that I installed in the gas line. I have since removed it and replaces the furnace wire that was in liquid tight with MC cable.
Plus the fitting that he put on top of the furnace wasn't a hit.
I have two questions. All reading are in wc.
The first is with my static pressures. I just want to know how they look. The total is on the high side at 0.53 but not sure what I can do.
I took 4 readings. Return side of filter (-.11), blower compartment (-.25), furnace below coil (.28), and above coil (.14). So a drop of .14 across filter and .14 across coil which is better than Goodman spec of .20.
The heat and ac blower speeds show the same readings and according to the charts they are 930cfm. I tried to increase the speed on the ac by 110cfm but the pressure went up to .65 which resulted in 1000cfm.
The second is with the coil condensate drain. The coil is under positive pressure. Should I install a trap and a safety switch? If so what's recommended. He mentioned an insulated trap? Not sure why. It will hook up to the PVC pipe sticking up on the right.
Thanks for any comments to help me understand.

I'm helping a friend replace my gas furnace and AC here in Maryland. Furnace is in basement.
He has his own HVAC company but does mostly commercial work. He does do residential but he doesn't go looking for it. I've done most of the work because he's been very busy. I probably should have thought this out a little better but it's a learning experience! Feel like it's Groundhog day.
This is what we installed.
Furnace Goodman GR9S960603BN. 60k btu.
Condenser Goodman GLXS5BA3010. 2-1/2 ton.
Coil Goodman CAPTA3026B3. 2-1/2 ton. (Pressure drop at 950 cfm: DRY 0.20, WET 0.25).
Filter AprilAire 2410 MERV 13 16" x 25". (Pressure drop at 950 cfm: 0.14).
I posted already about the bushing that I installed in the gas line. I have since removed it and replaces the furnace wire that was in liquid tight with MC cable.
Plus the fitting that he put on top of the furnace wasn't a hit.
I have two questions. All reading are in wc.
The first is with my static pressures. I just want to know how they look. The total is on the high side at 0.53 but not sure what I can do.
I took 4 readings. Return side of filter (-.11), blower compartment (-.25), furnace below coil (.28), and above coil (.14). So a drop of .14 across filter and .14 across coil which is better than Goodman spec of .20.
The heat and ac blower speeds show the same readings and according to the charts they are 930cfm. I tried to increase the speed on the ac by 110cfm but the pressure went up to .65 which resulted in 1000cfm.
The second is with the coil condensate drain. The coil is under positive pressure. Should I install a trap and a safety switch? If so what's recommended. He mentioned an insulated trap? Not sure why. It will hook up to the PVC pipe sticking up on the right.
Thanks for any comments to help me understand.