I have a newly built 26x26 detached garage in Henrico, VA and it's feeling like things have been planned out well enough. I had a local company come out to dig a trench and run a 2" pvc conduit for feed line to the garage and a 1" pvc conduit for internet. I'm feeling like I want to connect the subpanel myself just based on how some of this work was already done but based on the rough in it's not seeming that straight forward. I may call another electrician to see what they think.
My main panel is 200 amp. I'm planning on running a 125a subpanel with 1/0 AL wire with a 100 amp main breaker in case I do upgrade my main service.
The rough in at the subpanel location is coming out just in front of the wall. This is to left of the garage door. I'm planning on drywalling. There's also a stud right in the middle. I'll have to check with my builder on the stud spacing there.
Let's say I remove the stud and recess the panel I assume I can use a 45 to bring the conduit. under the subpanel. Otherwise I could build/extend a false wall to have it be recessed.
Now on the main panel side, things seem harder. They've come into a cinder block stem wall. The main panel is recessed in stud bays.
It's not clear me to what the best route to the main panel is here. Do i use another LB and then go back into stud? Then i have to have a junction box to go from THWN to SER?
Am i missing something here because i'm not an electrician or was the routing done in a way that makes life harder?
matt_i
SE Michigan
It looks like the 2" comes up fully proud of the stud wall. Can you slip a piece of drywall behind it(?). Its not the finest work, but if so, you can bend (flex) the conduit over several feet to glue into a male thread box adapter that will hit a knockout in the bottom of your subpanel.
Also...you could also core out what you have there, glue in new conduit stub(s) placed in a better spot, it's relatively easy to fit the pipes back to existing. (I think!). Underground you can flex quite a bit and nobody will care.
Surface mount deserves some thought about how the wiring will leave via the top side of the box and be secured if NM.
wyliesdiesels
Modesto, CA
not sure you will be able to safely remove studs on that garage wall. i would check with the GC first. it may be structural.
as to the main panel, I would have come in the back side of the main above or below the meter pan. as it is now, it will be a real pain to get into the panel with conduit. you could still reroute on the outside wall and thats what i would do
FYI- all that stuff you have in front of the panel violates the NEC required clearances. i would move the stuff
mm08822
Whomever trenched that didn't help you by making a hard 90. It could have been 2 45s or even arc'ed.
At the main panel you could put a horizontal LB flush with the block wall pointing left (to the panel). Run a few feet of conduit and add a 90 pointing upward. From the 90, add a female connector. Run sealtite into the bottom of the panel using a 45 degree connector. May need to notch the sillplate.
Back of the panel would have been much easier.
At the garage, it looks like you are stuck going with a surface mount panel. Otherwise reworking that conduit gets ugly!
Figure it out before you pull any wire.
Next time provide some space between conduits.
Someone with a heating blanket for conduit would be helpful to make offsets.
L
Landfall0158
Man, I thought I hired professionals. I had mentioned the placement of the subpanel to the electrician and asked if that made sense and they said it would be okay.
So I think building a false wall for the subpanel will make things easier on that side. At least one benefit of that is i won't have worry about going through a structural top plate.
For the main panel. It seems like i have a few options
1. Reroute on the outside with a sweeping elbow and then a LB right under the meter box in the small cavity between main panel and the bottom plate.
2. LB to the left -> sweeping 90 -> sealtite to 45. I'm having a hard time finding a short run of 2" sealtite on home depot or lowes? Is this something they sell by the foot in store? And in the 2" its really expensive for any length i am seeing.
3. Option 3 is the nuclear option where i just trench a new line to the right side of the garage.....
wyliesdiesels
Modesto, CA
i would not do option 2 on the main. option 1 is way better
option 3 for the garage, thats your call but youre most likely locked into surface mounted panel unless you move it
dscheidt
Panel location in the garage is fine, you just can't recess it in the wall. Surface mount it or build a wall in front of the studs.
As for getting to the main, since you've already got a penetration, I'd try to make it work.
How about a largish pull box on the wall. Conduit from outside enters in the lower right corner, conduit to the panel leaves on the top into the stud bay to the right of the panel, and enters from the side. Depending on the exact details it might be possible to bend a piece of conduit to fit, or you might need a unilet of some variety. I'm pretty sure I could make a piece of 1 1/4 EMT work, which would take copper big enough for your proposed loads. Splice to aluminum in the pull box.
mm08822
Better pull the panel cover off and see if there is room for option 1. Looks like the bottom of the meter panel is at same height as main panel bottom.
Option 2. Go to a supply house and get 3 ft and a 45 degree connector and a straight.
Whomever trenched this surely didn't think ahead for the main panel connection. It seems like every garage/pole barn, everybody has to hit the closest point of that structure which usually puts the sub-panel in a crappy place.
matt_i
SE Michigan
my guess....purely a guess....they were planning on putting a 2-1/2" holesaw thru the 3-1/2" side of the stud to access the panel sidewall knockout with a ******. Getting spindly there on framing but it basically fits with the work already shown. Use an LB from the ****** thru the stud to turn out on a 45 degree down, then a 45 degree ell to point straight down, then a 45 ell parallel to the wall plane fit to another LB on the stub going straight out.
Bad Habit
Chumstick WA
Why not extend the conduit straight up on the outside and penetrate higher than the panel. Then (assuming no or few obstructions) wrap it around the studs and then feed into the top?
kngelv
Detroit, MI
I have a few questions and I'm not trying to be a wiseguy. What are you planning to do in the garage? Is it a shop? A 125 Amp panel is overkill unless it's some kind of shop. The electrician is clearly clueless but your builder did you no favors by not having the ability to put the conduit throught the center of the floor plate or in front of it. He's in the middle of both. Two inch conduit inside a 2" x 4" stud is never a good idea. I have no idea why people don't spend a few extra dollars and do 2" x 6" walls. If you try and recess the panel you are going to have a hell of a time getting all your outlet wiring around that corner. Are you planning on running power across the ceiling for you main runs?
Using sealtite will look like ****. I'd just dig a new trench and do it right. If you want to keep the current run and there is room in the meter can box then I'd do two things:
1. Get rid of the LB's through the brick wall. Dig down and cut both of the conduits and put couplings on them. Patch the holes in the brick. Run the conduit straight up to the wood wall and use an LB straight in for the ethernet. Use an LR for the 2" and go straight into the meter box.
2. Your sort of stuck surface mounting the garage panel but it's in a shite location.
It looks like you got some bad advice and a bad build all together. I don't see any blocking on the sidewalls where the seams of the wall sheathing are and your ceiling design is going to be a ***** to insulate unless you use sprayfoam and then it's going to be a ***** to cover. It's hard to tell but your door header looks like it's sectional instaed of one long engineered piece. Good luck whatever you do.
James
larry4406
Northern Virginia
His brick has already been vandalized on his home. No repair will ever look proper again. So, I would retain the existing penetration of the power and communication via the existing LB's at his house garage and find a way to deal with it.
Or add a junction box on the outside to conceal the hole.
Me, I think I would run it on the interior of the structure with the panel.
The penetrations thru the block wall are centered on a stud bay. Chisel the block back so that LB's can install flush with the the block yet their covers are proud. Orient the in side LB's with ports up.
The block looks like 8" thick with a 2x8 sill and a 2x4 wall on top. This creates a shelf. Use the shelf to run left to to the panel while the comm goes in to the stud bay to be dealt with.
At the detached shop: Is the wing wall a shear wall - yes or no?
  • If no, then you can remove some studs and recess the panel there.
  • If yes, then you build a false wall to the interior and recess the panel in it, or surface mount it on the shear wall
wyliesdiesels
Modesto, CA
could just change it to a j box for comms and reroute the larger one to the panel on the outside.
its gonna be real fun trying to get that conduit into the panel since its recessed in the wall and there is a cinder block stem wall in the way. coming into the back of the main from the outside will be way easier and fewer bends to deal with
mm08822
not if the meter pan is back-back with the panel. OP never posted pics with cover off.
Dig Doug
Garage -
build a new wall in front of the existing wall run some future conduit for access later on, make it easy on your self
add a pull box for the low volt and add a future expansion conduit ( Spare ) up into the ceiling structure over to access panel area ( make it easy for later )
Drywall return back into existing wall 6-8 inches away from the garage door hardware
add some drywall backing in the inside corners
pretty easy !
jlv03
SE IA
It's always easy to armchair quarterback this with hindsight, but I think I would have explored swapping the meter pan out for a meter main and just run the detached garage to a breaker in that new meter main.
I like the false wall idea on the new detached garage, especially if you are going to insulate the space.
L
Landfall0158
125 amp is overkill but I want to have room to grow and to start I'm going to just do 100 amp breaker. Nothing too crazy in the garage. Mini split, lift, ev charger, pressure washer. I'll probably never reach the load capacity I have but i'm okay with that at this point.
I haven't pulled off the front cover of the main panel yet to confirm if meter pan is back to back with the main panel but it seems like it lines up pretty much 1 to 1 with the main panel and theres a lock on it.
The electrician come back out this pass Tuesday after i mentioned some disappointment and he was pretty much like we can't touch the meter box.
But the good news is I've made some decisions and a lot of progress. The electrician is coming out this upcoming Tuesday to finish the routing to the main panel for no additional money. His reasoning was that he assumed we would be continuing with the subpanel install as a separate engagement and it would be easier to run the wire and then slide the routing on, but he said could do it and leave it unglued for me.
I've decided to do the false wall pretty much exactly how Dig Doug just mentioned.
I got rockwool comfort batts and insulated the actual wall, built a false wall that goes all the way to the left and leaving just about 8 inches so i can fit in a liftmaster jackshaft 98022, added drywall blocking for the walls as well. Still need to figure out the ceiling but that will come later.
Figured out the subpanel height, cut the conduit and cemented the male fitting on to it.
Next step was wiring. I'm doing 1 awg copper thwn for the lines and neutral and 6 awg copper for the ground for the feeder wire.
I did the pull string with a plastic bag vacuum trick, then a paracord rope to pull the 4 lines through. It was actually super easy to pull through. We used a ladder and a 2x4 as a makeshift reel. My girlfriend held the ladders, my friend fed the wire, i was pulling and i didn't even feel any of the 90s. They simpull wire is advertised as lube free and i believe it.
So i got that through and I'll pull it back out the LB when the electrician gets here and then pull some more into the main panel room to have them finish that wiring while they're there. I already have the 100 amp breaker compatible with the main and some upsized lugs for the neutral / ground if needed.
Subpanel is about 1/2 in proud of the false wall. I ran 6 awg solid copper to the ufer ground that builder put on the other side of the 26 foot wall... with it not even fully in the wall... So that was more expensive than it needed to be and now I need to build a drywall box for that..
I've started running romex for a few things: utility sink water pump, future pressure washer, garage door opener, first general purpose outlet on my right wall.
I know I need at least one gfci 20 amp outlet (covered by the general purpose outlet) as well as an exterior and interior light that i'm getting some options for.
So if all goes to plan Tuesday I'll have things wired up! I'll upload pictures tomorrow when I'm on better wifi.
Also if anyone has any comments / advice about hanging lets off trusses, I would appreciate it. I understand they're engineered and are not supposed to have any holes or drilling but i'm just planning on some led prime lights so that has to be okay? I mean drywall has to go up. More research to come.
Appreciate everyone's comments. Make me feel better that these are reasonable concerns/questions about why it was done this way.
Skooterj
Indiana
Option 4??? Run a second line directly into a disconnect off your meter? I know not every POCO or AHJ allows this, and only some meter boxes have the capability, but that is what I did using the Milbanks K4977 meter box tap kit.
And Option 5? Build out your false wall just enough to cover the conduit and route the wire to a flush mounted box on the wall to the left of the door when looking out?
L
Landfall0158
Here are the pics.
Pulled the wire with my girlfriend and it went really smoothly. Followed this video
for prep. The simpull coating on the wire really helps. I didn't feel any of the 90's.
I did find what I thought was a lot of water in the conduit... Googling seems to show that these conduits are not waterproof, but I was't able to find examples of this much water. Keep in mind the garage end was capped with tape before it was roofed in.
While wiring i noticed the ufer ground is also starting on the outside of the wall and going in.. I didn't realize i could cut this at the bottom and just have the copper turn into the wall so now i'm going to have do a small drywall bump out as I connected the copper near the top and don't want to redo the ~50 feet run.
This is how he finished the rough in. Not great but was "free" as it was part of the previous work order.
Got my initial circuits wired up and passed rough in and final inspection with flying colors.
You can see here how i framed the false wall. I would have used 4 inch construction screws next time to go straight into the stud rather than the method i used here of connecting them with the cross bars.
I'm happy i can move on with my other electrical needs in the garage and get the final building inspection so that i can officially use it.
Also... thinking about 2 post lift positions. Originally was thinking just center left side so you could drive straight in but now im thinking about these orientations. Would keep my center space clear. the random floor colors, doing some swisstrax design.
Innovate1
They got it done but as has been noted there are lots of things that could have been done better. On the final steps if the low voltage LB had been tipped about 45 degrees the cable could have been routed around the large box easier. Could have flipped the subpanel over and had less large wire in the box to get in the way of other wire routing. I didn't see the rebar for ground in the pics of the sub panel - guessing it must be farther away?
Innovate1
On hanging lights from the trusses that should be no issue. No problem running screws or even small lag screws into the trusses (such as for mounting OHD track). Perhaps some locations get particular about that but I have never seen it. Just don't notch or drill holes for wires or anything bigger. Should be able to mount the fixtures or box so the wire connection misses the truss location.
L
Landfall0158
Yeah, i'll have to deal with the low voltage at some point. Also I realized the keyhole mounting slots were reversed on the bottom so that you could mount it upside down like you said. I didn't realize that was as an option until I had already run the wire and started circuits. Good to remember for next time. The rebar for the ground is on the other side of the building so I had to run a 50 feet ground to it.
Is there a splice in the jbox between LB and main panel?
Nope, just a loop in that space.
Thanks, the builder confirmed this as well.
I installed a Liftmaster jackshift door opener as well and realized my door tracks are slightly misaligned but are tearing up the rollers on the right side. They're coming out to address it next week.