Convert 3.5" round workbox to outlet

aragno

Member
Joined
Oct 31, 2021
Messages
23
I have a porcelain light bulb holder in my garage ceiling.
I wish to plug in 2 LED lights (65 watts each).
This light is on a single switch.
I want to plug in the 2 x LED lights I have and I'm happy to install an outlet for the sole purpose of these 2 lights.

I have taken this photo inside the workbox but unsure how to tackle this one.
As the box is shallow, I feel I should remove the workbox and install a new one that is deeper.
What workbox should I use?
What outlet and adapter plates/covers?
Any specific outlet I should select?
I am unsure of what to do with the 3 sets of wires + ground.
1 x red
2 x white (together on the light)
2 x black (capped together)
2 x ground

I'd like to the option to install the porcelain light when/if we move.
IMG_0750.jpeg

Once I have this wired in, can I install a GFCI switch like this next to the existing wall switch?
1788197884106.png
If so, i'll separately post about how to correctly wire this next to the switch.
 
To avoid these ads, REGISTER NOW!

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,963
You can get a listed receptacle and plate combination for a 4" box. (There are also covers available without the receptacle, but they're not code compliant, because code requires at least two screws. The listed assemblies use a rivet.) Either replace the box with a proper one, or get a round back 1900 extension box, depending on your tolerance for things looking like they're done by a hack, and put your receptacle in that.

You can use a dead front gfci like you show, but you'd have to make sure the neutral is in the switch box.
 

rust in the eye

Well-known member
Joined
Oct 2, 2017
Messages
2,892
Location
Chicagoland
Why a GFCI for a ceiling mounted fixture?
A lamp holder with a receptacle show in post #2 seems a fine choice from here. Good ones will come from an electrical supply house, the ones at big orange etc. are garbage. I'd imagine the ones you can't lay a hand on until you own them from the jungle to be as bad or worse.
 
OP
A

aragno

Member
Joined
Oct 31, 2021
Messages
23
I managed to install this in similar fashion as the light was wired (2 white on one side, red on another, and connected the ground wires (previously not in use with the light bulb holder).
The switch is working and the outlets are now working.
my round box was a 4" and I was able to accommodate this. I will add a 1/2" space ring to give a little more space, but for now, it's functional.



1788278353489.png
This circuit/breaker provides power to this former garage ceiling light, and 2 ceiling lights in nearby rooms.
This garage light was operated by a switch on the wall. Next I would like to install a GFCI near the switch in the garage since code requires a GFCI to be on the outlet circuits in a garage, regardless of location/position.
 
To avoid these ads, REGISTER NOW!

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,963
I may be missing something here but it seems like the key piece that's needed is a 3-1/2 inch round fixture cover punched for a duplex receptacle.
They don't exist. a 3.5 box isn't big enough, a 4" is. As I noted earlier, most of the outlet covers available are not code compliant, as code now requires the receptacle to be held by two screws. There are listed assemblies of a cover and an outlet.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,870
Location
East Bay SFO
Would it be kosher to use the existing screw holes to screw on a 4 inch square box? After that was up there, you could pull a Black, White, and Ground wire out through the middle punch out hole of the 4 inch box and from there wire in one or even two duplex receptacles.
Wire in a dead front GFCI in your switch box or even a GFCI duplex receptacle in that box. Then you’ll be good to go.
 
OP
A

aragno

Member
Joined
Oct 31, 2021
Messages
23
Would it be kosher to use the existing screw holes to screw on a 4 inch square box? After that was up there, you could pull a Black, White, and Ground wire out through the middle punch out hole of the 4 inch box and from there wire in one or even two duplex receptacles.
Wire in a dead front GFCI in your switch box or even a GFCI duplex receptacle in that box. Then you’ll be good to go.
I think the GFCI test and reset have to be accessible from the floor and no equipment requires to access it. That’s why I was thinking to install it next to the switch.

Based on the comment from @dscheidt it seems I need to open the switch and see if a neutral is present. I’m unsure what I’m looking for but I will snap a photo and see what I can learn.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,136
Location
Central Iowa
Can I install a blank-face GFCI next to the switch that controls that former light, which is now a switched outlet?
Yes, it's already been stated that a neutral is required. Cut it out to a two gang box, if it's already a two gand, make it a three gang and so forth.
I think the GFCI test and reset have to be accessible from the floor and no equipment requires to access it. That’s why I was thinking to install it next to the switch.
Correct.
Based on the comment from @dscheidt it seems I need to open the switch and see if a neutral is present. I’m unsure what I’m looking for but I will snap a photo and see what I can learn.
you are looking for two or more white wires connected together and not to anything else in the box.
 