Help with EMT
01Bullitt82
Hello Everyone, ive been looking through the journal and have learned alot. First time poster, though. I just had a 30x45x12 steel building built. I want to run EMT for my power. The problem im face is that the vertical columns on the 45' sides have double columns, and the horizontal braces are only signal. Also the front and rear 30' sides are single columan. What would be the best place to mount my boxes with the least amount of bends? while maximuming space. I currently have the boxes mounted with magnets, just to see what i was working with. If i put them on the horizontal brace, i feel like its a lot of bends to go around all the double columns. If I mount to the front of the double columans, the conduit is straight but then im losing 2.5-5" of space between the conduit and wall. I would preciate any advice from anyone who has dealt with this before. Picture for reference.
LXCam
Looks like you just need to get proficient at bending saddles. Or go vertical and into another box support in the ceiling space with a run paralleling your wall but you’d need to support that box as well.
Saddles aren’t that hard. Do you know the 30 degree rule for bending an offset?
matt_i
SE Michigan
There is also a tee (and LB and other related conduit bodies) which are made with a smooth bore for direct adaptation to EMT this no male thread adapter is needed. Not hanging out everywhere but would save some work and other parts if you are putting in quite a few tees.
The handbook which comes with the hand bender has everything you need although it takes a mild amount of study. There are 3 marks on the bender radius, notch, star and arrow to assist with lining up the various bending methods. When you lose the handbook you just look up the instructions online a few years from now.
JohnX14
Boston 'burbs
I would, and do, run the EMT high, right below the kicker braces from the wall to the ceiling. Set a box wherever you want a receptacle and run a conduit down the post to that box. It will take more conduit but be faster and look a whole lot better than having 500 offsets.
I like running the EMT high and dropping down for a number of reasons. That's how I'd do it too.
dscheidt
Bending saddles isn’t hard. Don’t let fear of them lead you to a layout that you don’t want. You will be living with it for a long time.
Figure out where you want boxes, then figure out how to pipe them up, using the least material.
Vertical drops will likely use more pipe, more boxes, and more wire. How much depends on the layout. It would take me longer if I was working off a ladder, but it might be faster for you.
01Bullitt82
All good suggestions, thank you. I did think about running it high and dropping down but that seemed like alot of conduit and wire. If I make bends thats about 8 columns to go around on each side. I guess I just need to decide on if I want to use more material and save time or use less and take more time.
matt_i
SE Michigan
The top "trunk line" is a fairly future proofed solution if you have enough diameter in the trunk. Yes this costs more now but you have the wireway 95% built for any future needs. Without sufficient diameter a person would have to start from the (sub) panel again running wireway. A building like that isn't very conducive to NM.
Dagny
Northern Wi.
If you put more than 3 current carrying conductors you have to derate them so don't get all excited about running everything in one pipe.
dscheidt
yes, but you derate them from table 310.16, which for most situations means THHN 10 awg and smaller carries what you expect it to be from 240 whatever.
WildBill
PNW
I also vote for running above and dropping down, that's what I did and it was fast, easy, and easy to add stuff afterwards. I also put boxes up for light receptacles and drop cords etc along the main trunk at every other roof truss. A duplex switched receptacle and a duplex always on in a double extra deep box at each location. I ran cords from them along the ceiling framing to LED strips and light fixtures, the LED strips are using one of the always on as they are app controlled. Has worked out really nice. If you look around you can buy bulk amounts of boxes for way less than Home Depot, I think I got mine from Ebay.
mm08822
7-9 CCC's requires derating to 70%. Using the 90C column for cu thhn derating let's #14 be ocp'd at 15a, #12 at 20a, #10 at 30a.
Above 9 CCC's is when it starts to impact ocp value.
I'd worry more about box fill.
mm08822
Ceiling recepts even for lighting requires gfci protection.
Ceiling outlets that get hard-wired to do not.
01Bullitt82
You guys are talking over my head now. Lol. I do have a electrician to help me with the technial stuff, but I was trying to get a head start on the lay out. The plan was to have 4 outlet on each side wall, three on the back wall and 3 in the middle of the trusses for the 6 high bay lights to plug into. I thought when a led light goes out it would easier to replace it by unplugging it and pluging a new one in.
cannuck
Rural SK
If you have enough room over the diagonal braces to me this is screaming for cable trays. Personally, I would have 120V 20A outlets on every column, plus 240s as needed.
dscheidt
Unless this is just storage building, you will want more outlets, or outlets in different locations. at the least, on every column, maybe more than that. Make a plan of where you put stuff, and where you'll be working, and place outlets accordingly. Again, you're probably going to be living with the decision for a long time, and if you have to use an extension cord for everything, you'll be mad about it.
In a garage, or similar occupancy, all receptacle outlets less than 50A are required to be GFCI protected. hardwired lighting outlets do not require gfci. So if you use plug connected lights, they'll need a gfci. the gfci device has to be readily accessible (which means no tools, no ladders, no moving ****), so you're either going to need a gfci breaker or a deadfront, because you don't want your lights going out because someone did something silly. In general, cord connected lights are ****, unless you're spending commercial fixture money. They're sold to people who can't or won't, for whatever reason, install a lighting outlet for a permanent fixture. Most of those reasons boil down to "they're cheap", so the fixtures match.
JohnX14
Boston 'burbs
The GFI's need to be readily accessible, and I'd put them in the panel, but 'readily accessible' does not mean not moving ladders, tools , etc. It means not moving any part of the building finish. But I do agree with the rest of your post, fwiw.
mm08822
including 50A.
MongoTA
CT
While it's always good to learn how to bend manually, once you get that down, if you have a lot of offsets semething like this Greenlee can make the installation go faster. This was a throw in at an auction lot.
Insert, press the lever, it bends the box offset perfect every time. It's so easy a Mongo can do it.
mm08822
Deep boxes are your friend
Of course. You should first have a conductor count/gauge(s) to know what size box to buy......4"sq x 2-1/8 deep or 4-11/16" sq x 2-1/8". That would also include how you plan to pull conductors into/through the box.
Plan it on paper before running a stitch of conduit or most boxes.
mm08822
Depending which code cycle they are on. IDK what FL follows. Here in MA we follow the current NEC, w/ MA amendments. Some states are 10-15 years prior.
Since OP doesn't have a location in profile or stated, he gets the current 2026 NEC version reqs. Local amendments is on the OP.
NEC jumped from requiring 15 & 20's on gfci to everything including 50A. So 30s were omitted in the above post, fwiw.
JohnX14
Boston 'burbs
Sounds good to me.
I wouldn't be putting 30 or 50 amp 240V receptacles in a workshop on GFCI's unless I had "no choice", realizing that they are required, and I have to do so for my customers, as a professional. We can't even get new Ranges and Dryers to run on a GFCI breaker. Fortunately we have a rule in MA that allowed us to document and remove the GFCI protection under certain circumstances. ("Rule 11" here in MA) It isn't 'as simple' as removing the GFCI breaker, but requires documentation. The guidelines of that rule have been bent on many occasions.
01Bullitt82
Im in Eastern North Carolina. Columns are only 5ft apart, I thought that would be to many outlets. The 4 on each side equals one about every 10ft on each wall. I was not tracking the gfi requirements, I thought only the first
receptacle in each circuit had to be protected with gfi. That makes the total cost of receptacles go up quite a bit. The shop will be used to store and work on cars.
NostraThpmas
You are correct. If you "daisy chain" the receptacles, each downstream receptacle is protected by the first receptacle on the circuit.
sparky 1971
Central Iowa
Every 10' is fine but make them quadplex receptacles if for no other reason than they look better. One device in a 4" square box looks dumb. The covers are within pennies of being the same price between duplex and quad, the only real expense would be the price of a duplex receptacle per box.
You're right, only the first receptacle is a GFCI as long as you connect the conductors properly. Just make sure it isn't in a place where you'll pile a bunch of **** in front of it and forget it's there. I'd keep it simple and make it one circuit per wall and be done with it. If you have a 120 air compressor or welder you might make those dedicated, but you could also make sure to not plug anything else into the same circuit when you're using them.
Shiftless
East Bay SFO
Getting one of those free is a GREAT deal. 🍻
dscheidt
Read your code book:
Accessible, Readily (Readily Accessible). Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to take actions such as using tools (other than keys), to climb over or under, to remove obstacles, or to resort to portable ladders, and so forth.
That’s the 2023 language. 26 removed ‘and so forth’. 210.8 requires GFCI to be installed in a readily accessible location. So, yes, having to move **** to reach the device makes it not readily accessible. And yes, everyone violates that all the time, because shops are full of stuff, and not blocking gfci access is pretty low on the list of priorities. But there’s no excuse to get it wrong from the get go, when a little planning gets you a much better setup.
nadogail
Coronado, CA
Jack Benfield wrote the definitive book on bending EMT. You should be able to find it at a technical book store. He also made a video tape demonstrating the process.
dscheidt
He also invented the bender everyone uses. The book is useful, if you know how to bend conduit. It's not going to teach you how to do that. No book is, it's not something you can learn by reading. Knowing the theory and the math is useful, if your brain works that way, but you learn to bend conduit by bending conduit.
Hands on instruction from a codgity old ******* whose been doing it since dinosaurs roamed the earth is the bast way, but failing that, watching some instructional videos (I don't remember if I liked the benfield one, or not, but YouTube has lots of stuff), getting a bender and some conduit, and just practicing will go a long way.
kngelv
Detroit, MI
What are you planning to do with the walls? Are you covering or insulating them? If you have never bent conduit before then you will likely struggle getting all your saddles the same. I would defintely go high as others have suggested. Once you figure your layout you can then pre-make all your vertical drops and horizontal runs. Then you can just assemble it all and save a ton of time.
James
dscheidt
Saddles aren't that hard. If you can use a tape measure and do some simple math to put the bends in the right place, you can figure out how to do it in an hour and three or four practice pieces. Each unnecessary vertical drop is going to cost you $20 or so, for the stick of conduit, extra box, and the wire, and at least two trips up a ladder.
Chuckster in NJ
Hunterdon County NJ
Whenever I hired a "greenie helper" (who had little to no experience bending EMT) I held bending class 101 after work, so after all the experienced guys (the ball breakers) left work I would give the kid some sticks of EMT and teach them how to bend saddles, dog legs with 90’s, offsets, etc. and by the end of the night they were pretty good and over the next week they would "hone" their bending skills on the job and impress their mechanics.
I am very good at bending all types of conduit with hand and hydraulic benders and I ran thousands of feet during my 55 years on the job.…….. I guess I am now that official "codgity old *******" ;)
LXCam
Back in the day when 1/2” was under a buck a stick it was no big deal to teach an apprentice. Now you’re making an investment to teach a newb.