Dayton G73 Wiring

ted13b

Member
Joined
Dec 19, 2008
Messages
19
I plan to wire up my new G73 heater this weekend, and I just wanted to run it by you guys first. My garage has 200 amp service and plenty of room in the subpanel. I'm going to install a 30 amp double breaker, then run 10-2 romex 20' to the heater, without conduit. Does this sound good?
 
To avoid these ads, REGISTER NOW!

bucs012

Well-known member
Joined
Aug 11, 2009
Messages
307
I plan to wire up my new G73 heater this weekend, and I just wanted to run it by you guys first. My garage has 200 amp service and plenty of room in the subpanel. I'm going to install a 30 amp double breaker, then run 10-2 romex 20' to the heater, without conduit. Does this sound good?

I did not do mine but my electician ran both of my g73's. He put them on a dual 40 amp breaker to be safe. Not sure the size of conduit. He then put a plug in (large like a dryer) in my ceiling and plugged the heaters in to their own plug in unit since they are located in different areas. If I ever need to replace one, all I have to do is change out the plug-in and plug it in and I am good to go. I also have 200 amp service.

Here is one of my units plugged in.
http://s104.photobucket.com/albums/m197/bucs012/Garage/?action=view&current=garage006-2.jpg
 
Last edited:

Keep

Well-known member
Joined
Jan 1, 2009
Messages
1,398
Location
Oshawa, Ontario
I ran a 30amp outlet, then bought some 10/3 cord so I can plug it in. If I need to move it I can move it up to 7 feet (that's how long the cord was) in any direction without having to rerun new wire.

You can sort of see the outlet here

23jan%20001.jpg
 
Last edited:

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Same here - 30A on #10, twist lock plug, a little 3/4" conduit and a couple of fittings. Bada-bing, packin' heat.
DaytonHeater.jpg
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I did not do mine but my electician ran both of my g73's. He put them on a dual 40 amp breaker to be safe.

He put two units on one 40 amp circuit or one unit each on a 40 amp circuit? Either way doesn't make sense really. If it draws 20 something amps why breaker two at 40 or even one at 40?:wtf:
 

jkeyser14

Well-known member
Joined
Dec 19, 2008
Messages
1,819
Location
(rural) Maryland
You either need a disconnect switch at the unit, a plug, or a lockout on your service panel if it's not in sight for it to meet code. That way if someone is "servicing it" power is removed and can't be restored by someone else accidentally.
 

bucs012

Well-known member
Joined
Aug 11, 2009
Messages
307
He put two units on one 40 amp circuit or one unit each on a 40 amp circuit? Either way doesn't make sense really. If it draws 20 something amps why breaker two at 40 or even one at 40?:wtf:

Each one on their own 40. Over kill? Maybe, but I have never blown a breaker. Who knows, I may want to go with a larger heater in the future. Plan ahead and do it once.
 

bucs012

Well-known member
Joined
Aug 11, 2009
Messages
307
Same here - 30A on #10, twist lock plug, a little 3/4" conduit and a couple of fittings. Bada-bing, packin' heat.
DaytonHeater.jpg



Mine is mounted pretty much like yours. See my latest power bill post under the heater section. 130 kph at 6.5 cents is dirt cheap!
 

mrbreezeet1

Banned
Joined
Dec 6, 2010
Messages
3,694
Location
Moundsville, WV, 15 miles South Of Wheeling WV
I know this is an older thread, but so you guys think this would be OK with the plug?
There were a few threads on another group cautioning to to use a plug, one guys caught on fire, but it turns out he used a 110v RV plug. The amps were OK,though, and another fellow thought the 110V part was not an issue, and was due to improper installation.
Myself, now, I would get a proper 220V 30 amp plug/outlet.
To me this seems easier than wiring 10/2 MC into the heater.
I am thinking about NEMA 6-30 plug or a twist loc plug wired onto 10/2 stranded cable, with the proper matching Outlet.
See the NewAir G73 just gives you 3 stranded wires to tie into, think there about a 12 AWG.
I wish they would just provide a terminal block like the Dayton, or like you would see on a dryer.
Thanks, Tony
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
I know this is an older thread, but so you guys think this would be OK with the plug?
There were a few threads on another group cautioning to to use a plug, one guys caught on fire, but it turns out he used a 110v RV plug. The amps were OK,though, and another fellow thought the 110V part was not an issue, and was due to improper installation.
Myself, now, I would get a proper 220V 30 amp plug/outlet.
To me this seems easier than wiring 10/2 MC into the heater.
I am thinking about NEMA 6-30 plug or a twist loc plug wired onto 10/2 stranded cable, with the proper matching Outlet.
See the NewAir G73 just gives you 3 stranded wires to tie into, think there about a 12 AWG.
I wish they would just provide a terminal block like the Dayton, or like you would see on a dryer.
Thanks, Tony

Of course, why wouldn't a properly rated plug be ok? That's the route I would take.

However, if I was you I would NOT install a flat-blade receptacle like a 6-30 up there just in case it slowly vibrates out over time; given gravity, I would use an L6-30 or similar rated for what you need... a twist-lock.

Do NOT install a 40a breaker on #10 wire as a previous OP suggested. bucs012's install looks great.
 

mrbreezeet1

Banned
Joined
Dec 6, 2010
Messages
3,694
Location
Moundsville, WV, 15 miles South Of Wheeling WV
Of course, why wouldn't a properly rated plug be ok? That's the route I would take.

However, if I was you I would NOT install a flat-blade receptacle like a 6-30 up there just in case it slowly vibrates out over time; given gravity, I would use an L6-30 or similar rated for what you need... a twist-lock.

Do NOT install a 40a breaker on #10 wire as a previous OP suggested. bucs012's install looks great.

OK Thanks, The one above, I think that's Falcon67's heater.
No I got a 30 Amp breaker.
I'll let you all know what I come up with.
Thanks, Tony
 

mrbreezeet1

Banned
Joined
Dec 6, 2010
Messages
3,694
Location
Moundsville, WV, 15 miles South Of Wheeling WV
No one local had the L6-30 or similar twist loc, maybe lowes will carry it I have to check tomorrow. Went to busy beaver, ACE and Tractor Supply.
Ace, IIRC had the twist Loc plug, but no outlet.
So is a L6-30 plug and outlet what I need?
If I go with the MC out of a box, I don't like the box clamp's shown, was looking
for the kind that screw on to the cable, but the ones ACE had looked too big, although I did not have the MC cable with me.
Guess I can use the ones I have too.
Was also looking for the little "Red-Head" Anti-Short bushings that go in the end of the MC, but no one local had those either.
I guess NEC says there not required for MC, but there Nice to use. They ARE required for AC cable.
Of course no one had the wire either, was looking for 10/2 with ground stranded cable.
Wonder if I could just use the 10/2 with ground MC on the twist loc plug, if I can find a plug and outlet locally. :headscrat
Thanks for reading.
Tony
 

Attachments

  • MC 007 2.jpg
    MC 007 2.jpg
    40.9 KB · Views: 19

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
No one local had the L6-30 or similar twist loc, maybe lowes will carry it I have to check tomorrow. Went to busy beaver, ACE and Tractor Supply.
Ace, IIRC had the twist Loc plug, but no outlet.
So is a L6-30 plug and outlet what I need?
If I go with the MC out of a box, I don't like the box clamp's shown, was looking
for the kind that screw on to the cable, but the ones ACE had looked too big, although I did not have the MC cable with me.
Guess I can use the ones I have too.
Was also looking for the little "Red-Head" Anti-Short bushings that go in the end of the MC, but no one local had those either.
I guess NEC says there not required for MC, but there Nice to use. They ARE required for AC cable.
Of course no one had the wire either, was looking for 10/2 with ground stranded cable.
Wonder if I could just use the 10/2 with ground MC on the twist loc plug, if I can find a plug and outlet locally. :headscrat
Thanks for reading.
Tony

Sign up for Amazon Prime and get your $3.99/item one-day shipping and get it all there then :)

Receptacle: http://www.amazon.com/dp/B00002NAT9/?tag=atomicindus08-20

Plug: http://www.amazon.com/dp/B00002NARX/?tag=atomicindus08-20

Cheapest way to wire would be to buy an acceptable "range cordset" designed for a home range (stove), and then cut both ends off. IE: http://www.amazon.com/dp/B000VU1KC6/?tag=atomicindus08-20

You could also buy 25' of 10/3 cable but this will be 2-3X more expensive.
 
To avoid these ads, REGISTER NOW!

aandpdan

Well-known member
Joined
Nov 12, 2009
Messages
849
Location
In between MA and PA
Just a suggestion...

Try an electrical supply store for the L6-30 and the cable. They should have all of it. The prices are often better than HD or Lowes.
 

mrbreezeet1

Banned
Joined
Dec 6, 2010
Messages
3,694
Location
Moundsville, WV, 15 miles South Of Wheeling WV
electrical supply store was out of the 10/3 cord, wanted about $45.50 for the plug and outlet, Lowes wanted about $35.50 for the plug and outlet and about $7.00 for the cord.
Got some screw in box connectors for the MC like this in case I still decide to hard wire it.
Thanks, Tony
Halex-90440-rw-162426-240117.jpg
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Fine strand wire cord, like that used in extension cords, is not permitted on the electrical code to be used on appliance connectors that are not specifically designed and designated for such. NEC 422.16(A). While this is a heater, and not a kitchen appliance (stove, oven, dishwasher, etc) is still should be good practice to know if the connector accepts fine stranded cord.

Whatever you use for a disconnecting means, plug, switch, etc, must be rated at a minimum of 125% of the total heater load (including blower, thermostat transformer, etc). Since fixed electric space heaters are considered continuous load items, the entire branch circuit supplying it also has to be rated at a minimum of 125% of the total load of the unit (wire, breakers, etc).

NEC 424 covers fixed electric heating and should be used as the minimum guide for installation of such systems.

Pay special attention to whether the manufacturer requires conductors rated at more than 60C and if so, what the minimum temperature rating is.

Charles
 
Last edited:

mrbreezeet1

Banned
Joined
Dec 6, 2010
Messages
3,694
Location
Moundsville, WV, 15 miles South Of Wheeling WV
Well I know the heater pulls max 20.8 amps so 21 X 125% is 26.25, so I am using a 30 Amp breaker and # 10 wire.
That part should be OK then.
The manual with the heater does not specify if requires conductors rated at more than 60C
But you are are connecting into the heater wiring to 2 stranded wires that appear to be thinner than # 10.
So my guess is that the #10 stranded is OK.
Just looked on the cord and it says 300V -30 to 90C.
Thanks, Tony
 

timgr

Well-known member
Joined
Dec 19, 2006
Messages
544
Location
Medford, MA USA
A plug, socket and cord is expensive and unnecessary for a permanent installation. You can use a 10-2 whip from Home Depot (about $10) like I did:

daytonHeater.jpg
 

mrbreezeet1

Banned
Joined
Dec 6, 2010
Messages
3,694
Location
Moundsville, WV, 15 miles South Of Wheeling WV
Re Those whips, I was looking at those the other day, and didn't get it. (Had 1 left)
Went back Saturday, and was going to get it, and you guessed it, it was gone, No more in stock.
So I decided to just go with the twist loc's and the 10/3 cord.
That's a clean looking set up timgr.
What is the red NM coming out of the J box for, a line T-stat?

harvero, did you "tin" the cord wires with solder, or just leave them bare, where they clamp down into the plug connector's?
thanks, Tony

Edit,
The directions that came with the plug said Do NOT TIN wires.
 
Last edited:

timgr

Well-known member
Joined
Dec 19, 2006
Messages
544
Location
Medford, MA USA
...
That's a clean looking set up timgr.
What is the red NM coming out of the J box for, a line T-stat?

Thanks - there's a speaker wire detouring around the bottom of the box. Is that what you're seeing?

Otherwise it's the 10-2 for the heater (orange) and yellow 12-2 going to the drop on the right.
 

timgr

Well-known member
Joined
Dec 19, 2006
Messages
544
Location
Medford, MA USA
No It was the orange 10/2. I see, that's your line in, and the EMT must run down to the shut off switch.
Thanks, Tony

Yes there is a switch at the bottom of the EMT. The power shut-off switch isn't strictly proper for that heater. Proper external control would intercept the thermostat instead of the power feed. But it works fine as long as the fan is off when I switch off.
 

harvero

Well-known member
Joined
Nov 16, 2009
Messages
233
Location
Flemington, NJ
Fine strand wire cord, like that used in extension cords, is not permitted on the electrical code to be used on appliance connectors that are not specifically designed and designated for such. NEC 422.16(A). While this is a heater, and not a kitchen appliance (stove, oven, dishwasher, etc) is still should be good practice to know if the connector accepts fine stranded cord.

Whatever you use for a disconnecting means, plug, switch, etc, must be rated at a minimum of 125% of the total heater load (including blower, thermostat transformer, etc). Since fixed electric space heaters are considered continuous load items, the entire branch circuit supplying it also has to be rated at a minimum of 125% of the total load of the unit (wire, breakers, etc).

NEC 424 covers fixed electric heating and should be used as the minimum guide for installation of such systems.

Pay special attention to whether the manufacturer requires conductors rated at more than 60C and if so, what the minimum temperature rating is.

Charles

If an appliance is connected by cord, then does NEC apply to it? Would not UL take precedent since the device is not hard wired?

I copied this from another forum:

UL Standard UL-749
UL 749
Household Dishwashers

7.3 Installation instructions

7.3.1A Where the installation instructions for a built-in dishwasher specifies
that the appliance is able to be connected by means of a power-supply cord
not already attached to the appliance by the manufacturer, the instructions
shall specify that a power-supply cord kit marked for use with dishwashers
shall be used. The cord kit shall comply wi th Clause 25.2A. The part or model
number of the power-supply cord kit shall be included in the appliance
installation instructions.
7.3.2 The installation instructions provided with a cord-connected undercounter appliance shall include
the following instructions or equivalent information:
a) the power-supply receptacle for the appliance shall be installed in a cabinet or on a wall
adjacent to the undercounter space in which the appliance is to be installed;
b) there shall be an opening through the partition between the compartments specified in (a) that
is large enough for the attachment plug to pass through. The longest dimension of the opening
shall not be more than 38 mm;
c) the edges of the opening specified in (b) shall, if the partition is wood, be smooth and rounded,
or, if the partition is metal, be covered with an edge protector provided for this purpose b y the
manufacturer; and
d) care shall be exercised, when the appliance is installed or removed, to reduce the likelihood of
damage to the power-supply cord.

25.2 Cord-connected appliances
25.2.1 The power-supply cord of an appliance provided with a means for grounding shall include an
equipment-bonding conductor and shall terminate in a grounding-type attachment plug.

25.2.4 For a cord-connected built-in appliance:
a) the flexible cord shall be Type S, SJT, SPT-3, or the equivalent; and
b) the length of the flexible cord shall be 0.9 – 1.2 m, measured from the face of the
attachment plug to the plane of the rear of the appliance.

25.2.5 The power-supply cord shall be attached permanently to the
appliance or shall be in the form of a separate cord supplied as part of a
power-supply cord kit with means for connection to the appliance. The
power-supply cord kit shall comply with Clause 25.2A.
25.2.6 The ampacity of the cord and the current rating of the fittings shall not be less than the current
rating of the appliance.
For an appliance rated more than 15 A, the current rating of the attachment plug shall not be less than
125% of the current rating of the appliance.
A 20 A plug shall be acceptable for an appliance rated not more than 4000 W at 240 V. The attachment
plug shall be acceptable for use at a voltage equal to the rated voltage of the appliance.
.

25.2A Power-supply cord kits for use with undercounter or built-in
dishwashers
25.2A.1 A power-supply cord kit intended for the installation of an
undercounter or built-in dishwasher shall include the following:
a) power-supp ly cord, strain-relief means, and push-back relief that complies
with Clause 25.2;
b) a part or model number marked on the power-supply cord kit package, or
in the kit installation instructions;
c) installation instructions; and
d) grounding instructions in accordance with Clause 7.2.2.4(a).
 

awdriven

New member
Joined
Feb 16, 2012
Messages
3
Hi guys, what's the trick to making this work with an L14-30 connector from a generator? I'm not ready to set up a 240 circuit to my shop, but it's easy for me to hook up my 6500 watt generator temporarily. Bucs012, your setup looks much like what I would want to do, but in lieu of the receptacle box, I'd look for some way to support the whip and bring it over to the wall, where I could hook up my generator cord.
 

racerboy

Well-known member
Joined
Nov 7, 2005
Messages
458
Location
New Jersey
I know this is an old thread but thought it best to continue rather than start a new one.

I had a NewAir G73 in my last garage. When I moved, I took it with me, but that was almost two years ago and I do not remember how the electrician had it wired in my last garage. Following the advice on this forum, I bought a double-pole 30A breaker last night. I was also going to make a power cord (never did that before) by purchasing a twist-lock plug/receptacle and some 10/3 power cord. But in looking at the wiring that is currently attached to the G73, and is 12 AWG, not 10. Also, it has three wires, Red, White, Black. There is no copper bare wire. All of the wires are in a metallic sheath. In the previous install, the electrician ran that sheath down the wall and wired it directly to my breaker box. I had no on/off switch and he told me to simply turn the breaker on/off for power (which I've since learned is not the best advice).


If I wanted to hard-wire the existing wiring to a two-pole receptacle, where does the Black, Red, and White wire go?

Is the wiring he used too small? Should this be 10g?

My plan was to run orange romex (10/2) to a twist-lock receptacle, and then create a power cord that plug in from the G73 to the receptacle (the way some other folks here have done it), but the use of the 12 AWG wire has me confused since it seems everyone here is using a 10/3 power cord.

And the last, most basic question. How come the Romex cable is called 10/2, even though it has three wires, put the power cord is called 10/3, but also only has three wires?
 

racerboy

Well-known member
Joined
Nov 7, 2005
Messages
458
Location
New Jersey
Here are a couple of pics of the wire:

12 AWG wires:

11ac81e5beef3c3b9bc699421c0838c7.jpg


Metallic sheath coming out of heater:

47c30ef75f1408ffa70d8023e3fe1e92.jpg



Sent from my iPhone using Tapatalk
 

Attachments

  • 11ac81e5beef3c3b9bc699421c0838c7.jpg
    11ac81e5beef3c3b9bc699421c0838c7.jpg
    292.9 KB · Views: 0
  • 47c30ef75f1408ffa70d8023e3fe1e92.jpg
    47c30ef75f1408ffa70d8023e3fe1e92.jpg
    337 KB · Views: 0

DeltaWye

Well-known member
Joined
Sep 26, 2016
Messages
114
Location
Toronto, Canada
If I wanted to hard-wire the existing wiring to a two-pole receptacle, where does the Black, Red, and White wire go?

You'd need to open up the unit and see where the wires connect or use a multimeter and see which one is bonded to the chassis. That wire is supposed to be green or bare, he probably used what he had laying around.

Is the wiring he used too small? Should this be 10g?

Sounds like it based on the other posts in this thread. Cheating on wire colour is one thing, cheating on wire ampacity is an absolute no-no. Post the specs or check what the manufacturer recommends.

And the last, most basic question. How come the Romex cable is called 10/2, even though it has three wires, put the power cord is called 10/3, but also only has three wires?

Just convention, probably intended to trip up the beginners.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,728
Location
SE Michigan
I would agree with that advice. I don't think it comes brand new with that metallic "whip" on there. Take pictures of where the wires are landed and that will give you (or the forum) more information on what to land where.
 