Big Maxx 45KBTU LP Heater

drez77

Member
Joined
Dec 30, 2007
Messages
17
I have the 45kBTU heater installed in my garage running off a 100# propane tank with this regulator http://www.northerntool.com/shop/tools/product_23995_23995 I am getting next to nothing out of it for heat. My garage is 24*26 with R13 insulation. This weekend it went from 39* to 42* in one hour. I expected a lot more heat out of the unit. Everything on the unit appears to be functioning correctly so I am thinking it may be the regulator. Can anyone with this heater comment if the regulator I have is okay or suggest a replacement.
 
To avoid these ads, REGISTER NOW!

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
Drez there is a similar thread in this forum and I am pretty sure the overall consensus was that a 100# tank wasnt big enough to support the heater properly with propane flow.


Rick
 

romoman

Well-known member
Joined
Feb 11, 2010
Messages
61
Location
Bedford, NH
The tank is big enough. I have a 74k btu unit runing on a 100 pound propane tank with no problems. Something isn't working right. I'm not a HVAC expert, but go through all the steps. Make sure the LED on the board is not showing any codes, the unit is firing correctly, etc.
 

Jay41

Active member
Joined
Feb 26, 2011
Messages
42
Location
Grundy co. IL
I have the 45kBTU heater installed in my garage running off a 100# propane tank with this regulator http://www.northerntool.com/shop/tools/product_23995_23995 I am getting next to nothing out of it for heat. My garage is 24*26 with R13 insulation. This weekend it went from 39* to 42* in one hour. I expected a lot more heat out of the unit. Everything on the unit appears to be functioning correctly so I am thinking it may be the regulator. Can anyone with this heater comment if the regulator I have is okay or suggest a replacement.

That one says, "for use with 20 lb. tank".

Is your gas pressure set right at the unit?
 

Big Larry

Member
Joined
Jan 3, 2011
Messages
8
Location
WI
for what its worth I was running 75K LP on a 100 LB tank With brand new reg. 2 stage reg verry little heat gas suppler came out. had to turn REG up 3 turns had lots of heat
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
I run a 200K heater on a 100 lb tank with no problems... But, just for the record, that's about the maximum for a 100 lb tank. Like others, I suspect the regulator isn't supplying enough gas to the heater.
 
To avoid these ads, REGISTER NOW!

fishheds

Well-known member
Joined
Apr 30, 2010
Messages
164
Location
Outer Banks,NC
That regulator is fixed and cannot be adjusted.The twin stage regulator previously mentioned may work better.You need to be getting 11" -13" WC to the gas valve.
Look at the pilot when the main burner kicks on.It should remain the same size except for maybe a very small fluctuation when the main valve first opens.If it gets smaller or begins to flutter you're not getting enough pressure.
Even though this may earn me a :yikes:,if you don't have a pressure gauge,think about your breathing.11-13" is about what you'd use to use to blow out birthday candles,but not enough to blow up a balloon.Don't try this with propane haha
I initially thought the tanks ACME service valve(the ones with the big coarse external threads) may be the culprit,but 100# cylinders shouldn't have this type valve.
Also,look inside the tank service valve to make sure dirt daubers haven't got in there and clogged it up.
I spent 18 years doing propane service work and here's a little off topic tidbit.If you ever approach a tank and see flies all over it,you can bet the farm that tank or hardware has a leak somewhere.They love LP for some reason.
I flipped the lid open on an underground tank once and dead green flies were piled 3" deep inside the dome. Thousands of em.
Anyway,a 100# cylinder will have plenty of vaporization to run that heater and a full tank should last about 48-50 hours.
 
OP
D

drez77

Member
Joined
Dec 30, 2007
Messages
17
I did ask Mr. Heater what they recommended for a regulator and here is their response:
"Any low pressure (11-14"WC) regulator will work. The 11-14"WC regulator is common household LP pressure. The regulators can be found at most home improvement and hardware stores as well has HVAC supply houses."

I still think I will look at a different regulator.
 

Jay41

Active member
Joined
Feb 26, 2011
Messages
42
Location
Grundy co. IL
I did ask Mr. Heater what they recommended for a regulator and here is their response:
"Any low pressure (11-14"WC) regulator will work. The 11-14"WC regulator is common household LP pressure. The regulators can be found at most home improvement and hardware stores as well has HVAC supply houses."

I still think I will look at a different regulator.

But what is your gas valve pressure set at, at the unit?
 

crazy wheel

Well-known member
Joined
Feb 26, 2011
Messages
197
I have the 45kBTU heater installed in my garage running off a 100# propane tank with this regulator http://www.northerntool.com/shop/tools/product_23995_23995 I am getting next to nothing out of it for heat. My garage is 24*26 with R13 insulation. This weekend it went from 39* to 42* in one hour. I expected a lot more heat out of the unit. Everything on the unit appears to be functioning correctly so I am thinking it may be the regulator. Can anyone with this heater comment if the regulator I have is okay or suggest a replacement.

That one says, "for use with 20 lb. tank".

Is your gas pressure set right at the unit?

But what is your gas valve pressure set at, at the unit?

I'm not sure how many BTU that regulator is rated at, or how many BTU that hose will carry (ID of that hose looks kinda small).

Like Jay41 says, You need to know what the inlet pressure and the manifold pressure is while the unit is running.

I would recommend calling a qualified service technician and have things checked out.

Then you will know what is wrong and what needs to be done for a safe and proper repair.

It will most likely save you money in the long run.
 

Big Larry

Member
Joined
Jan 3, 2011
Messages
8
Location
WI
Had the same problem with 75k lp the brand new reg. had to B turned up 3 turnes got heat now.
 