So I have a older miller tig machine, it has a 75ft power cord on it. WAAAAAAY more than i need to get around the shop. However, I do need a larger gauge wire to run to my welders outlet. Would it be possible to use this as outlet wiring? as in, from the breaker to a 50amp socket.

Its only 3 wire, so there wouldn't be an actual ground in there, but my 240v outlet doesn't have a ground hook up. Just the 2 hot and common. Is this possible, or should i just go buy some 6/3 romex? Btw, I don't know the exact gauge of this wire, but I know its bigger than 6/3 romex. In my welders manual it says that it can be wired directly to the breaker or with a plug. This is why i'm wondering if I can run part of this cable from the breaker to the plug.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If you are talking about using the welder cord as wire that will run in side of a wall from the breaker box to a wall outlet the answer is no. You need to use romex. Also the 240v outlet for the welder should be two hots and a ground not two hots and a common.
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
If you are talking about using the welder cord as wire that will run in side of a wall from the breaker box to a wall outlet the answer is no. You need to use romex. Also the 240v outlet for the welder should be two hots and a ground not two hots and a common.

If it's temporary, I'd say its fine... however, if you plan on installing it in a wall/conduit/etc. definitely no. Make sure the breaker screw and receptacle screws are torqued properly, but not so tight they cut the fine strands.

Finely stranded cord is thicker then the same gauge solid, know what it is before you do anything.
 
OP
N

nismomans13

Well-known member
Joined
May 1, 2008
Messages
438
Location
Pittsburgh, PA
it will not be inside a wall. I think i'll just get some 6/3 romex and be to code. I did read more about wiring and it should have the ground not the neutral wire. Thats how it was when i opened the socket up but i'll fix it tomorrow and make sure its hooked up right
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You want to get 6/2 (black,white + bare ground). The ground is not counted in the numbering. 6/3 will be 3 wires (red,black,white + bare ground).

When you say it's not in a wall, you shouldn't use romex as a cord if that's what you are planning. Sorry, I'm a little confused as to what you are doing. Romex should be used within a wall or where it is protected from damage.
 
Last edited:
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
cord is cord and cant be used as a substiute for building wiring. You can put a plug on one end and a connector on the other and use it as an extension cord if you want....

Also, realize in cord the ground is counted in romex its not. So a 6/3 cord and a 6/2 romex will both have 2 wires plus a ground.
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
concrete block garage, it will be ran through conduit on the outside of the wall.

Install the outlet near the box, cut the cord off and put 50A ends on it, and a 50A end on each welder. That way, you have the luxury of the long cord for whatever you need, and the outlet wiring will be cheap yet legal. :)
 
OP
N

nismomans13

Well-known member
Joined
May 1, 2008
Messages
438
Location
Pittsburgh, PA
Install the outlet near the box, cut the cord off and put 50A ends on it, and a 50A end on each welder. That way, you have the luxury of the long cord for whatever you need, and the outlet wiring will be cheap yet legal. :)


I like your thinking, 3ft of 6/2 is and a couple 50amp receptacles is a lot cheaper than 20ft of 6/2
 