After looking at other sub panels on the forum I tried my best to make it look neat but more importantly make sure I am meeting all codes. I think am about ready for final inspection. Let me know if I should change anything before final inspection.
I can't speak to code, not a pro, but that is one of the neatest instals I have seen. I am not sure why some pros feel the need to just toss panels together.
Looks nice and tidy. That will make life a lot better for the next person that has to work in there!
Correct me if I'm seeing this wrong. But are all three entry cables black? Shouldn't the neutral be white, and perhaps a red wire is needed too?
Is the white tape enough on the neutral?
Gotta say, I hate that panel. Nothing to do with your quality of work, it looks great... but I hate having to dig under a bunch of hots to get to my neutrals/grounds.
looks like the gr bus is connected to the nuet bus by flat bar going behind busbar assembly, if so, thats not good if thats a subpanal
Correct me if I'm seeing this wrong. But are all three entry cables black? Shouldn't the neutral be white, and perhaps a red wire is needed too?
Is the white tape enough on the neutral?
Chris, you are correct. They are two separate structures. I drove an 8 footer in the ground.
I will split up the romex in the knockouts. Not a problem.