Flourescent Lights and Compressor

To avoid these ads, REGISTER NOW!

Jim Johnstone

Well-known member
Joined
Apr 11, 2011
Messages
1,841
Location
Brantford, Ontario
Have enough power coming into your garage that the start up load of the compressor doesn't starve the lights.

What is your electrical setup like in your garage?
 
OP
G

GMCAMARO

Well-known member
Joined
Jul 29, 2007
Messages
120
Location
Near Worcester, MA
There is 60 Amps coming into the garage. The compressor is wired for 240.
There is plenty of current available as the circuit breakers has never tripped.
We are talking 18 double 4 foot lamps.
The compressor is 7.5HP 90 Gallons ingersoll rand.
 

pro machine Engineering

Well-known member
Joined
Sep 29, 2011
Messages
317
Location
kansas
60 amp service. I dont think your going to stop the lights from flickering when the compresser starts up. There is a pretty good amount of amp draw when a compressor motor starts
 

Jim Johnstone

Well-known member
Joined
Apr 11, 2011
Messages
1,841
Location
Brantford, Ontario
60 amp service. I dont think your going to stop the lights from flickering when the compresser starts up. There is a pretty good amount of amp draw when a compressor motor starts

I agree, a true 7.5hp compressor draws right around 34 or so amps at full load. Start up load on most electric motors is 2 to 3 times higher. So figure 70 to 100 amps on start up. The breakers don't trip because it is a split second start up load, and the breakers are slightly time delayed for that reason.
 
To avoid these ads, REGISTER NOW!

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
I agree, a true 7.5hp compressor draws right around 34 or so amps at full load. Start up load on most electric motors is 2 to 3 times higher. So figure 70 to 100 amps on start up. The breakers don't trip because it is a split second start up load, and the breakers are slightly time delayed for that reason.


I think this is a good assessment of the problem. Larger service coming in would overcome the voltage sag from the motor startup current.
 

Provincial

Well-known member
Joined
Sep 21, 2011
Messages
6,872
Location
Near Salem, OR
Unless you bring in a bigger service feed to the garage, your only hope is to reduce the starting load of the compressor. Some sort of "soft start" setup is necessary. I am not aware of any Soft Starts for single phase motors, but there may be such a thing. Before solid state electronic motor controls became available, it was pretty common to set up banks of capacitors to aid motor starting. It takes someone with experince to design one of these setups. Perhaps someone on the Board knows more?
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,353
Location
Beautiful Southern Maryland
GM.
Put a voltmeter on one of the lines going to the lights, or probably just into a wall outlet will do the trick. Watch it while someone else turns the compressor on. You WILL see the voltage drop because your service is not big enough. That is why the lights are dimming, period. Only way to fix it is to upgrade the service so that there is not a voltage drop when the compressor starts. By the way, it might not be the actual service, maybe just the feed cables if they are not large enough.
 

StaggeringGoat

Well-known member
Joined
Jul 1, 2011
Messages
758
Location
Oregon
If you have magnetic ballasts new electronic ballasts may solve the problem. I've had the same issue with a regular 20A circuit and a smaller compressor and some lights plugged in. The lights with magnetic ballast flicker when the compressor kicks on but the electronic ballasts do not.
 