How do you prevent the lights from restarting(flickering) when the compressor comes on?
60 amp service. I dont think your going to stop the lights from flickering when the compresser starts up. There is a pretty good amount of amp draw when a compressor motor starts
I agree, a true 7.5hp compressor draws right around 34 or so amps at full load. Start up load on most electric motors is 2 to 3 times higher. So figure 70 to 100 amps on start up. The breakers don't trip because it is a split second start up load, and the breakers are slightly time delayed for that reason.