Copper wire Question

To avoid these ads, REGISTER NOW!

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
Almost certainly. 100 amp is generally #2 or #3 wire so #1 is just one size up. Breakers seem to take several sizes up from code sizing to handle volt drop and probably other reasons, like yours.

My only issue would be "single strand" wire. I would investigate that. The large wire I have seen is always multistranded.
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,082
Location
Amarillo,TX and Stinnett,TX
Almost certainly. 100 amp is generally #2 or #3 wire so #1 is just one size up. Breakers seem to take several sizes up from code sizing to handle volt drop and probably other reasons, like yours.

My only issue would be "single strand" wire. I would investigate that. The large wire I have seen is always multistranded.

I was wondering about that also, thanks.
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
Well, now your breaker most likely will not take that. Make sure not stolen, there are a lot of copper thieves these days.
 
To avoid these ads, REGISTER NOW!

superdel

Active member
Joined
May 3, 2012
Messages
38
I would suspect it is stolen. The scrap price on that would be $600+ if you burned the insulation off. That is service cable or for hard wiring welding packs. It is good for 200 amps. The likelyhood of you using 450 ft if you are not in industry is slim. The roll is quite big and probably over 200 pounds. If you can use it, it is a great deal. If you can scrap it with no trouble it is a great deal also. Your call.
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,082
Location
Amarillo,TX and Stinnett,TX
I would suspect it is stolen. The scrap price on that would be $600+ if you burned the insulation off. That is service cable or for hard wiring welding packs. It is good for 200 amps. The likelyhood of you using 450 ft if you are not in industry is slim. The roll is quite big and probably over 200 pounds. If you can use it, it is a great deal. If you can scrap it with no trouble it is a great deal also. Your call.

My use for some of it, would be to wire a single 100 amp circuit for a rotary phase converter.
 

jeff000

Well-known member
Joined
May 6, 2012
Messages
437
I would suspect it is stolen. The scrap price on that would be $600+ if you burned the insulation off. That is service cable or for hard wiring welding packs. It is good for 200 amps. The likelyhood of you using 450 ft if you are not in industry is slim. The roll is quite big and probably over 200 pounds. If you can use it, it is a great deal. If you can scrap it with no trouble it is a great deal also. Your call.

Never just burn off the insulation. The scrap yards give you the same price as if you just left the insulation on it. Sometimes less even. You can strip 450' in 30 minutes. Roll it out, put one end under a car tire or something and run a knife up the wire like you were debarking a tree.

A 450' roll of 2/0 is worth somewhere around 1400 bucks from a wholesaler depending on the type of insulation.

And stripped and recycled is worth 500+. Something smells fishy.

An electrical contractor would not sell it.


As for fitting, Residential breaker or commercial? Commercial you may be able to change the lug out. I don't use GE though so could't tell you for sure.
 