I found some 1ga single strand copper wire on CL for $1 per foot. Any idea if this will fit into a 100 amp GE circuit breaker?
Almost certainly. 100 amp is generally #2 or #3 wire so #1 is just one size up. Breakers seem to take several sizes up from code sizing to handle volt drop and probably other reasons, like yours.
My only issue would be "single strand" wire. I would investigate that. The large wire I have seen is always multistranded.
Are you saying you found some #1 AWG solid wire insulated?
I would suspect it is stolen. The scrap price on that would be $600+ if you burned the insulation off. That is service cable or for hard wiring welding packs. It is good for 200 amps. The likelyhood of you using 450 ft if you are not in industry is slim. The roll is quite big and probably over 200 pounds. If you can use it, it is a great deal. If you can scrap it with no trouble it is a great deal also. Your call.
I found some 1ga single strand copper wire on CL for $1 per foot. Any idea if this will fit into a 100 amp GE circuit breaker?
A 100amp breaker at least the one I use 1/0 will fit. R u sure it's not 1/0?
I would suspect it is stolen. The scrap price on that would be $600+ if you burned the insulation off. That is service cable or for hard wiring welding packs. It is good for 200 amps. The likelyhood of you using 450 ft if you are not in industry is slim. The roll is quite big and probably over 200 pounds. If you can use it, it is a great deal. If you can scrap it with no trouble it is a great deal also. Your call.