wire size

To avoid these ads, REGISTER NOW!

IONH

Well-known member
Joined
Feb 12, 2010
Messages
2,043
Location
Central Massachusetts
Dave, I assume you are running this wire in conduit underground. If so, you should consider Mobile Home Feeder. The sizes are limited and 2/0-2/0-2/0-1 or 2/0-2/0-1-4 is what I think you could get to handle the full 100A. The 2/0 will give you up to 135A if needed and it should fit in a 100A breaker.
See this on MHF...

http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet15


*

Wow, 500ft package. Where would someone get a bundle like that in shorter lengths? What would the home/garage interior "in wall" alternate be for the 2/0-2/0-2/0-1 be since the wire you linked I believe is for outside use?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
MHF can be run inside to a panel if in conduit. Supply houses and big box stores will sell it by the foot. The alternate would be to switch to SER cable inside which can be run without having to use conduit.

This is SE cable...
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet273
*
Wow, 500ft package. Where would someone get a bundle like that in shorter lengths? What would the home/garage interior "in wall" alternate be for the 2/0-2/0-2/0-1 be since the wire you linked I believe is for outside use?
 
Last edited:

IONH

Well-known member
Joined
Feb 12, 2010
Messages
2,043
Location
Central Massachusetts
MHF can be run inside to a panel if in conduit. Supply houses and big box stores will sell it by the foot. The alternate would be to switch to SER cable inside which can be run without having to use conduit.

What gauge SER cable would be the equivalent sizing to the 2/2/2/1 cable?

Which would you recommend? Not to hijack, but my span is probably only 20 feet exterior to a building and another 80 or so interior (total within both buildings from panel to panel).
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The sizes are the same between the two cables. Are you wanting #2 or #2/0? What's the amp rating you need? The reason I ask is 2-2-2 comes with a #4 ground not #1. 2/0-2/0-2/0 comes with #1 ground.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I would only use aluminum for large and long feeds. The aluminum alloy in wire has been improved greatly over the aluminum in wire from years ago. Aluminum wire is certainly not outdated.
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
OP
D

Dave Maxwell

Well-known member
Joined
Sep 21, 2011
Messages
865
Location
Kickapoo illinois
I'm sorry, but your question is not real clear. Does 2 2 2 4 mean 2/0, 2/0, 2/0 & #4 ground? Does it mean #2, #2, #2, #4 awg wire size? Without knowing what your load is on your existing panel and the size of your existing panel and what size your existing service wires are, it is not possible for me to answer your question. You will need to have your electrician come to your house, calculate your existing loads and check against your existing service feeders to determine if your wire size is of sufficient size to handle the added loads that will be applied to your old panel from the new storage shed loads. Your electrician will need to calculate the loads your anticipating from the storage shed also.

I'm sorry this is the best I can do fo

That is the response I got about the mobile home feed from county on legality. How do I calculate that stuff.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I don't know about the UL rating of only being 60 degrees, but my Cutler Hammer panels have listed on the sticker 60/75.

This thread here seems to state that the enclosure is the bottleneck and that when you mount these dual marked 60/75 breakers together that you must default to the 60 degree rating

http://forums.mikeholt.com/showthread.php?t=81811

This is consistent with what PHR posted here.

I believe you would need #2 copper, not 3 as has been posted.

http://database.ul.com/cgi-bin/XYV/...n=versionless&parent_id=1073985569&sequence=1

Suprising that no one other than PHR has ever mentioned this.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Too much to explain here. You'll need to do a search on the web for "How to calculate electrical loads", and do a lot of reading.


I'm sorry, but your question is not real clear.
Does 2 2 2 4 mean 2/0, 2/0, 2/0 & #4 ground? Does it mean #2, #2, #2, #4 awg wire size? Without knowing what your load is on your existing panel and the size of your existing panel and what size your existing service wires are, it is not possible for me to answer your question. You will need to have your electrician come to your house, calculate your existing loads and check against your existing service feeders to determine if your wire size is of sufficient size to handle the added loads that will be applied to your old panel from the new storage shed loads. Your electrician will need to calculate the loads your anticipating from the storage shed also.

I'm sorry this is the best I can do fo

That is the response I got about the mobile home feed from county on legality. How do I calculate that stuff.
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
I don't know about the UL rating of only being 60 degrees, but my Cutler Hammer panels have listed on the sticker 60/75.


I'll have to look at mine too but for most people who are going to have at least one older panel they are looking at 60 degrees.
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I don't know about the UL rating of only being 60 degrees, but my Cutler Hammer panels have listed on the sticker 60/75.

Pattenp, straight from UL, taken from here:

http://www.ul.com/global/documents/...l/newsletters/MoldedCaseCircuitBreakersMG.pdf

20. 60/75°C Wire — All circuit breakers rated 125 A or less are marked for use with 60° C,
60/75°C or 75°C only wire. This marking indicates the proper wire size for termination in
accordance with Table 310.15(B)(16) of the NEC . It is acceptable to use wire with a higher
insulation rating if the ampacity is based on the wire temperature rating marked on the breaker. For
breakers rated more than 125 A, the proper wire temperature rating is 75°C and it is optional for the
breaker to bear this marking.
 

johno

Well-known member
Joined
Oct 16, 2009
Messages
2,418
Location
Southern Ont.
One thing you need to do with aluminum is coat the wire ends/connections with an antioxidant, whatever size you end up with.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Bunk..., just plain bunk. I recommend to run the aluminum in conduit, but it's not necessary if installed direct bury and the trench is clear of stone. The poco uses direct bury aluminum all the time to service structures.

Was told by local electrician that aluminum shouldn't be used underground. Copper is going to cost me close to 5,000 just in wire
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
There is no heat issue with aluminum if sized properly. 1/0 copper and 3/0 aluminum are about the same amp cap. At 60C 125A for Cu vs 130A for Al

Said there was a heat issue. What size of aluminum is same as 1/0 copper. Or do they carry the same loads
 
Last edited:

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
What amp is the 4/0 4/0 2/0 aluminum good for at 200 foot run
If it is for the main service to the house then 200A.

Typically the secondary side of the service (120/240v) can be run approximately 250' before you need to worry about upsizing. This is usually the POCO's call.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Dave, You need to clarify your inquiry about the wire sizes. Is the feed to your shop going to be a new service coming off a meter, or are you planning to feed your shop as an auxiliary building off your existing main panel? This makes a difference in the number of conductors and size to the allowable amps.
 
OP
D

Dave Maxwell

Well-known member
Joined
Sep 21, 2011
Messages
865
Location
Kickapoo illinois
If I can by code I would.like to come straight off the meter base. That would be 200 amp. If I have to go off a breaker in main house panel then it will be 100 amp
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
If I can by code I would.like to come straight off the meter base. That would be 200 amp. If I have to go off a breaker in main house panel then it will be 100 amp
If it is a typical residential meter pan or even a meter/main then you CANNOT come right off of it. You need to come from a panel.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You can't get an additional 200a feed off of a 200a service. You need to have the service increased to 400a and install a 400a meter socket.

Edit: 400a service technically can use a 320A meter socket even though I said 400A.

If I have a 200. Amp service at house, can I put a 200 amp feed off it. Or do they make a breaker that size
 
Last edited:

fastjohnny

Well-known member
Joined
Sep 3, 2011
Messages
261
Location
SW Michigan
You can't get an additional 200a feed off of a 200a service. You need to have the service increased to 400a and install a 400a meter socket.

Edit: 400a service technically can use a 320A meter socket even though I said 400A.

Can't you use a 200A feed-through panel going to a 200A panel?:dunno:
 
OP
D

Dave Maxwell

Well-known member
Joined
Sep 21, 2011
Messages
865
Location
Kickapoo illinois
Finally at the point. Hope I can fit the wire in a 100 amp breaker in my feeder panel. Looks small. The main breaker on the shop box should be fine.
 