Wondered about that. Saw it on Menards site
Dave, I assume you are running this wire in conduit underground. If so, you should consider Mobile Home Feeder. The sizes are limited and 2/0-2/0-2/0-1 or 2/0-2/0-1-4 is what I think you could get to handle the full 100A. The 2/0 will give you up to 135A if needed and it should fit in a 100A breaker.
See this on MHF...
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet15
*
I assume since it says 2 2 2 4 it has 3 main leads and one ground. Why is it only $1 something per foot and single 2 copper is 3 per foot
Wow, 500ft package. Where would someone get a bundle like that in shorter lengths? What would the home/garage interior "in wall" alternate be for the 2/0-2/0-2/0-1 be since the wire you linked I believe is for outside use?
MHF can be run inside to a panel if in conduit. Supply houses and big box stores will sell it by the foot. The alternate would be to switch to SER cable inside which can be run without having to use conduit.
This thread here seems to state that the enclosure is the bottleneck and that when you mount these dual marked 60/75 breakers together that you must default to the 60 degree rating
http://forums.mikeholt.com/showthread.php?t=81811
This is consistent with what PHR posted here.
I believe you would need #2 copper, not 3 as has been posted.
http://database.ul.com/cgi-bin/XYV/...n=versionless&parent_id=1073985569&sequence=1
Suprising that no one other than PHR has ever mentioned this.
I'm sorry, but your question is not real clear.
Does 2 2 2 4 mean 2/0, 2/0, 2/0 & #4 ground? Does it mean #2, #2, #2, #4 awg wire size? Without knowing what your load is on your existing panel and the size of your existing panel and what size your existing service wires are, it is not possible for me to answer your question. You will need to have your electrician come to your house, calculate your existing loads and check against your existing service feeders to determine if your wire size is of sufficient size to handle the added loads that will be applied to your old panel from the new storage shed loads. Your electrician will need to calculate the loads your anticipating from the storage shed also.
I'm sorry this is the best I can do fo
That is the response I got about the mobile home feed from county on legality. How do I calculate that stuff.
I don't know about the UL rating of only being 60 degrees, but my Cutler Hammer panels have listed on the sticker 60/75.
I don't know about the UL rating of only being 60 degrees, but my Cutler Hammer panels have listed on the sticker 60/75.
Was told by local electrician that aluminum shouldn't be used underground. Copper is going to cost me close to 5,000 just in wire
Said there was a heat issue. What size of aluminum is same as 1/0 copper. Or do they carry the same loads
If it is for the main service to the house then 200A.What amp is the 4/0 4/0 2/0 aluminum good for at 200 foot run
If it is a typical residential meter pan or even a meter/main then you CANNOT come right off of it. You need to come from a panel.If I can by code I would.like to come straight off the meter base. That would be 200 amp. If I have to go off a breaker in main house panel then it will be 100 amp
If I have a 200. Amp service at house, can I put a 200 amp feed off it. Or do they make a breaker that size
You can't get an additional 200a feed off of a 200a service. You need to have the service increased to 400a and install a 400a meter socket.
Edit: 400a service technically can use a 320A meter socket even though I said 400A.