Bare wire in pulling lubricant
justinae
I have already pulled my (3) #2 wires in conduit. I now need to pull my ground wire. I used Ideal Yellow 77 to pull my wires so do I have to use a coated wire for the ground or can I use bare wire?
Aluminum ok?
Thanks!
J
justinae
Yep, probably should have done them at once. I had a triplex and the ground is separate. Regardless, I need to run it separately. It's 1 1/4" conduit.
rabidsquirrel
SE Pennsylvania
Most pulling lube is conductive, is usually says on the bottle to wait until it dries to turn the power on. That being said, I've never had a problem using it in a hot conduit.
pattenp
Virginia - USA
justinae, in your other post about this you said you purchased a single #4 Al to go with the #2 Triplex. Why are you not using the #4 for the equipment ground?
Norcal
Triplex is usually 2 insulated conductors wrapped around a bare AL conductor, it is not recognized as a wiring method by the NEC & is not allowed in conduit, either above or underground, the bare AL will turn to a toothpaste like substance underground, BTW.
Triplex is used by PoCo's for overhead service drops.
pattenp
Virginia - USA
The Triplex he got was UD for direct bury.
nehog
Jaffrey, NH
Why would there be a problem with a bare ground wire? It would be the same as steel conduit, wouldn't it?
:beer:
Gerry
Do not put bare conductors/ground in a steel conduit in moist (buried) conditions! The conductor and the conduit will form an electrolytic reaction, resulting in the failure of both. However, the first to fail will be the conduit (steel is sacrificial to aluminum!) and once the conduit fails, then the conductor will quickly deteriorate.
You could perhaps use plastic conduit, but I would not recommend it, as it will be almost impossible to keep it dry, which will result in deterioration of the bare conductor. :)
J
justinae
PVC conduit.
Pattenp I'm a bit embarrased to say, but the original #4 was a couple feet short. I was able to successfully fish it through after I fished the triplex, so in effect I can use the too short #4 as pull string.
My length is about 15 feet with 2 90 degree elbows.
I'll get the same kind of wire I had, but is it possible to use #6 instead of #4?
thanks
mossy66
Lake Villa, Illinois
I didn't see where it was installed under ground.
dirtydogintex
inner looper-3rd Div Houston w & n
If he pulled aerial style triplex cable (2 insulated conductors wrapped around a bare AL conductor), the neutral is uninsulated for 240vac 1ph service.
Last I checked it's not kosher to have an uninsulated neutral and an uninsulated ground in the same conduit.... just like not using aerial style triplex cable in conduit.
pattenp
Virginia - USA
He pulled Triplex UD. It is for direct bury or can be put in conduit in wet locations. He has another whole post as to what he is using. All is speculation as to what he's doing is just confusing things.
pattenp
Virginia - USA
PVC conduit.
thanks
Yes you can use a #6 Al or #8 Cu for the equipment ground. What ever you get make sure it has either THHN/THWN or RHH/RHW-2 rating.
Edit: Since you used AL SER in the house you should stick with AL for the rest of the equipment ground to the garage.
J
justinae
Got it. I'll stick with aluminum but if i can use #6 it wheel be easier to fish than #4.
I apologize if the two threads was confusing. I thought it would be better to separate.
alfredeneuman
Fullerton, CA
PVC conduit.
You can use a #8 THWN (green) insulated copper conductor for the ground.
If the run is 15' of conduit, the wire length can't be much more than 25'.
Cost should around $20 or so.