Triplex? What construction?Yep, probably should have done them at once. I had a triplex and the ground is separate. Regardless, I need to run it separately. It's 1 1/4" conduit.
Triplex is usually 2 insulated conductors wrapped around a bare AL conductor, it is not recognized as a wiring method by the NEC & is not allowed in conduit, either above or underground, the bare AL will turn to a toothpaste like substance underground, BTW.
Triplex is used by PoCo's for overhead service drops.
Why would there be a problem with a bare ground wire? It would be the same as steel conduit, wouldn't it?
Gerry
Do not put bare conductors/ground in a steel conduit in moist (buried) conditions! The conductor and the conduit will form an electrolytic reaction, resulting in the failure of both. However, the first to fail will be the conduit (steel is sacrificial to aluminum!) and once the conduit fails, then the conductor will quickly deteriorate.
You could perhaps use plastic conduit, but I would not recommend it, as it will be almost impossible to keep it dry, which will result in deterioration of the bare conductor.![]()
I didn't see where it was installed under ground.
If he pulled aerial style triplex cable (2 insulated conductors wrapped around a bare AL conductor), the neutral is uninsulated for 240vac 1ph service.
Last I checked it's not kosher to have an uninsulated neutral and an uninsulated ground in the same conduit.... just like not using aerial style triplex cable in conduit.
PVC conduit.
Pattenp I'm a bit embarrased to say, but the original #4 was a couple feet short. I was able to successfully fish it through after I fished the triplex, so in effect I can use the too short #4 as pull string.
My length is about 15 feet with 2 90 degree elbows.
I'll get the same kind of wire I had, but is it possible to use #6 instead of #4?
thanks
look into codes cause i am not sure if a ground needs to be insulated if in pvc
PVC conduit.
I'll get the same kind of wire I had, but is it possible to use #6 instead of #4?
agreedHe pulled Triplex UD. It is for direct bury or can be put in conduit in wet locations. He has another whole post as to what he is using. All is speculation as to what he's doing is just confusing things.