Bare wire in pulling lubricant

justinae

Well-known member
Joined
Aug 6, 2012
Messages
56
I have already pulled my (3) #2 wires in conduit. I now need to pull my ground wire. I used Ideal Yellow 77 to pull my wires so do I have to use a coated wire for the ground or can I use bare wire?

Aluminum ok?

Thanks!
 
To avoid these ads, REGISTER NOW!
OP
J

justinae

Well-known member
Joined
Aug 6, 2012
Messages
56
Yep, probably should have done them at once. I had a triplex and the ground is separate. Regardless, I need to run it separately. It's 1 1/4" conduit.
 

rabidsquirrel

Well-known member
Joined
Jul 17, 2010
Messages
397
Location
SE Pennsylvania
Most pulling lube is conductive, is usually says on the bottle to wait until it dries to turn the power on. That being said, I've never had a problem using it in a hot conduit.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
justinae, in your other post about this you said you purchased a single #4 Al to go with the #2 Triplex. Why are you not using the #4 for the equipment ground?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
Triplex is usually 2 insulated conductors wrapped around a bare AL conductor, it is not recognized as a wiring method by the NEC & is not allowed in conduit, either above or underground, the bare AL will turn to a toothpaste like substance underground, BTW.

Triplex is used by PoCo's for overhead service drops.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Triplex is usually 2 insulated conductors wrapped around a bare AL conductor, it is not recognized as a wiring method by the NEC & is not allowed in conduit, either above or underground, the bare AL will turn to a toothpaste like substance underground, BTW.

Triplex is used by PoCo's for overhead service drops.

The Triplex he got was UD for direct bury.
 
Last edited:
To avoid these ads, REGISTER NOW!

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
Why would there be a problem with a bare ground wire? It would be the same as steel conduit, wouldn't it?
:beer:
Gerry

Do not put bare conductors/ground in a steel conduit in moist (buried) conditions! The conductor and the conduit will form an electrolytic reaction, resulting in the failure of both. However, the first to fail will be the conduit (steel is sacrificial to aluminum!) and once the conduit fails, then the conductor will quickly deteriorate.

You could perhaps use plastic conduit, but I would not recommend it, as it will be almost impossible to keep it dry, which will result in deterioration of the bare conductor. :)
 
OP
J

justinae

Well-known member
Joined
Aug 6, 2012
Messages
56
PVC conduit.

Pattenp I'm a bit embarrased to say, but the original #4 was a couple feet short. I was able to successfully fish it through after I fished the triplex, so in effect I can use the too short #4 as pull string.

My length is about 15 feet with 2 90 degree elbows.

I'll get the same kind of wire I had, but is it possible to use #6 instead of #4?

thanks
 

mossy66

Active member
Joined
Dec 22, 2010
Messages
32
Location
Lake Villa, Illinois
Do not put bare conductors/ground in a steel conduit in moist (buried) conditions! The conductor and the conduit will form an electrolytic reaction, resulting in the failure of both. However, the first to fail will be the conduit (steel is sacrificial to aluminum!) and once the conduit fails, then the conductor will quickly deteriorate.

You could perhaps use plastic conduit, but I would not recommend it, as it will be almost impossible to keep it dry, which will result in deterioration of the bare conductor. :)

I didn't see where it was installed under ground.
 

dirtydogintex

Well-known member
Joined
Sep 28, 2012
Messages
927
Location
inner looper-3rd Div Houston w & n
If he pulled aerial style triplex cable (2 insulated conductors wrapped around a bare AL conductor), the neutral is uninsulated for 240vac 1ph service.
Last I checked it's not kosher to have an uninsulated neutral and an uninsulated ground in the same conduit.... just like not using aerial style triplex cable in conduit.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If he pulled aerial style triplex cable (2 insulated conductors wrapped around a bare AL conductor), the neutral is uninsulated for 240vac 1ph service.
Last I checked it's not kosher to have an uninsulated neutral and an uninsulated ground in the same conduit.... just like not using aerial style triplex cable in conduit.

He pulled Triplex UD. It is for direct bury or can be put in conduit in wet locations. He has another whole post as to what he is using. All is speculation as to what he's doing is just confusing things.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
PVC conduit.

Pattenp I'm a bit embarrased to say, but the original #4 was a couple feet short. I was able to successfully fish it through after I fished the triplex, so in effect I can use the too short #4 as pull string.

My length is about 15 feet with 2 90 degree elbows.

I'll get the same kind of wire I had, but is it possible to use #6 instead of #4?

thanks

Yes you can use a #6 Al or #8 Cu for the equipment ground. What ever you get make sure it has either THHN/THWN or RHH/RHW-2 rating.

Edit: Since you used AL SER in the house you should stick with AL for the rest of the equipment ground to the garage.
 
Last edited:
OP
J

justinae

Well-known member
Joined
Aug 6, 2012
Messages
56
Got it. I'll stick with aluminum but if i can use #6 it wheel be easier to fish than #4.

I apologize if the two threads was confusing. I thought it would be better to separate.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
PVC conduit.
I'll get the same kind of wire I had, but is it possible to use #6 instead of #4?

You can use a #8 THWN (green) insulated copper conductor for the ground.

If the run is 15' of conduit, the wire length can't be much more than 25'.
Cost should around $20 or so.
 