Meter socket options for new shop build

Blk88GT

Well-known member
Joined
Mar 16, 2009
Messages
1,076
Location
Manitoba
I'm going to be building a shop next month and will require a 200 amp service.

My current meter is a Thomas-Betts (Microelectric) CO2-200G.

I need to retain the 200amp disconnect on the meter because of the way the service is fed to my panel in the home.

Ideally, I would have a JS4 (dual lug) with a 200 amp disconnect for the house side. Unfortunately, the current meter is cut into some decorative stone on the side of the house.

Is it possible to take the "guts" of another meter and change them out with the existing meter, retaining the cabinet?

I have the Hydro coming out on the 27th for a cable locate but would like to know a little bit before they get here.

Thanks!
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Don't take this as gospel, but I think even if you could take the guts from one meter cabinet and get it to fit in into another it would void the certification of the unit. Devices are tested and certified as manufactured.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,618
Location
Long Island
Don't take this as gospel, but I think even if you could take the guts from one meter cabinet and get it to fit in into another it would void the certification of the unit. Devices are tested and certified as manufactured.

Yep. Even more important though, is that the meter must meet the exact specifications of the power company. Expect this to be much more specific than just what's stated in the code.
 

sickjuice

Well-known member
Joined
Jun 12, 2012
Messages
143
Location
welfare provence
The T&B JS4 series is for 400 amps

A) No chance of switching the guts
B) A homeowner cannot do a 400a service in Manitoba

If you are mistaken on the part number and actually want a 200a meter with a main and a splitter, they do make such an animal but the enclosure is much bigger (CO2-M series)
 

oltruckag

Well-known member
Joined
Aug 10, 2007
Messages
171
Location
*******, GA
Don't take this as gospel, but I think even if you could take the guts from one meter cabinet and get it to fit in into another it would void the certification of the unit. Devices are tested and certified as manufactured.

Yep - it will void the UL listing (and I'm sure the Canadian equivalent)
 
OP
B

Blk88GT

Well-known member
Joined
Mar 16, 2009
Messages
1,076
Location
Manitoba
Don't take this as gospel, but I think even if you could take the guts from one meter cabinet and get it to fit in into another it would void the certification of the unit. Devices are tested and certified as manufactured.

That was my belief as well. Thank you for clarifying.

Sickjuice, I do require a 400amp meter base. 200 for the house, 200 for the shop. The house side would require a disconnect.

What should I be looking at?
 

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
That was my belief as well. Thank you for clarifying.

Sickjuice, I do require a 400amp meter base. 200 for the house, 200 for the shop. The house side would require a disconnect.

What should I be looking at?


what is going into this shop that needs 200 amps?
How big is the house?
 

sickjuice

Well-known member
Joined
Jun 12, 2012
Messages
143
Location
welfare provence
That was my belief as well. Thank you for clarifying.

Sickjuice, I do require a 400amp meter base. 200 for the house, 200 for the shop. The house side would require a disconnect.

What should I be looking at?

Before you waste anymore time, have you gotten a price from MB hydro for a 400a service upgrade? Chances are you will drop the idea when you get the price. If your not adding any big loads like electric heat for the shop (i.e if their not going to make anymore money off you) then they charge you the full cost of upgrading their equipment to support the new service (transformer, wire, ect) Last one I did was 8k just on hydros end (plus the cost of the customers 400a installation)

T&B dosent make any 400a metering cabinets with built in disconnects.
I know their made by others but I've never used one cause their not cheap.

If your rural and have the space best way to do it is have a CT cabinet out in the yard and re-feed the house and new shop from there

But ya in Manitoba you will need an electrician anyways to do a 400a service so he will be able to go over your options with you
 
Last edited:
OP
B

Blk88GT

Well-known member
Joined
Mar 16, 2009
Messages
1,076
Location
Manitoba
what is going into this shop that needs 200 amps?
How big is the house?

It's 40x50, in floor heat, hoist, welder, compressor. The essentials. :bounce:

Sickjuice, if it's 8k to get me 400amp service, I'll have to bite the bullet. Hydro will be out soon to survey the situation. I have an electrician doing the work but wanted to educate myself before hand.

I think the easiest scenario would be to put a new meter socket on the pole, retain the feed to the house as-is and supply a new underground service to the shop. We'll see what they think about that.
 

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
It's 40x50, in floor heat, hoist, welder, compressor. The essentials. :bounce:

Sickjuice, if it's 8k to get me 400amp service, I'll have to bite the bullet. Hydro will be out soon to survey the situation. I have an electrician doing the work but wanted to educate myself before hand.

I think the easiest scenario would be to put a new meter socket on the pole, retain the feed to the house as-is and supply a new underground service to the shop. We'll see what they think about that.

Gas boiler?

what is all electric in the house? what is the house Sq. Ft.?
 

Angelfire

Well-known member
Joined
Mar 22, 2012
Messages
1,367
Location
New Mexico and Ireland
Have you done load calcs to validate you truly need that size service? That seems awfully big unless you are running multiple high amperage tools at once. If this is a one man shop, consider what you'll be running simultaneously and do your load calcs. Keeping in mind some items can be derated depending on what they are.
 

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
Everything is electric, there is no gas service available. The house is 2300sqft.



400A service will be a waste of money(unless you've got a large grow operation:pimpflash), and most(not all) utilities will require proof of need for the large service.

If you'd like i could walk you through doing a load calc to see what size service you actually need.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
400A service will be a waste of money(unless you've got a large grow operation:pimpflash), and most(not all) utilities will require proof of need for the large service.

If you'd like i could walk you through doing a load calc to see what size service you actually need.

I bet he will need 400 amp service, ALL electric heat in house and shop will eat up a lot of power, add in stove, dryer, water heater etc in house and I bet on a cold day with the wife cooking and doing laundry a 200 amp service won't cut it.

I don't know where in Manitoba he lives but I did a quick check in my heat load calc program and the design temps in the cites listed went from -23 to -37 degrees, that's going to take a bit of power to heat with either straight electric or geothermal.
 

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
I bet he will need 400 amp service, ALL electric heat in house and shop will eat up a lot of power, add in stove, dryer, water heater etc in house and I bet on a cold day with the wife cooking and doing laundry a 200 amp service won't cut it.

I don't know where in Manitoba he lives but I did a quick check in my heat load calc program and the design temps in the cites listed went from -23 to -37 degrees, that's going to take a bit of power to heat with either straight electric or geothermal.

Geo or a heat pump would draw very little compared to resistive heating, heating a 2300 sq ft home with pure resistive heat would cost an insane amount.

I've done many new homes with all electric(heat pumps and geo) and i've never had a calc call for anything more than 200 amps

Like i said, i'd be happy to help the OP with doing a proper load calc for the home. and shop.
 
Last edited:

awdblazer

Well-known member
Joined
Oct 17, 2011
Messages
1,100
Location
winnipeg, manitoba, canada
honestly talk to hydro, they will probably guide you in the way to go as you are probably outside the city, and well hydro does the inspections so better get it from them
 
OP
B

Blk88GT

Well-known member
Joined
Mar 16, 2009
Messages
1,076
Location
Manitoba
Gooch, a heat pump or geothermal is not an option.

I have an electric forced air furnace in the house and will have an electric boiler in the shop. We can see temperatures in the -25 to -40c range during the winter months and the last thing I want is an undersized electrical service powering my furnace and boiler.

The draw for the boiler alone is roughly 85amps. I can't see why I would go with anything smaller than a 200 amp service for the shop by the time you add in outlets, lighting, compressor, welder, hoist etc.

Let me know what you need for a load calculation.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,029
Location
Modesto, CA
Is propane an option so u don't have to use electric heat. I'm sure it would be far cheaper than what must be a HUGE future electric bill! U could even switch your water heater to gas!
 
To avoid these ads, REGISTER NOW!
OP
B

Blk88GT

Well-known member
Joined
Mar 16, 2009
Messages
1,076
Location
Manitoba
You guys worried about the electricity bill have to remember that we pay a fraction of what you guys do for power. We pay 6.94¢/kwh right now.

I submitted my paperwork to hydro this morning, I'll see what they say about my proposed solution.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,029
Location
Modesto, CA
You guys worried about the electricity bill have to remember that we pay a fraction of what you guys do for power. We pay 6.94¢/kwh right now.

I submitted my paperwork to hydro this morning, I'll see what they say about my proposed solution.

Wow! Almost 7 cents? Out here in Modesto, we pay .165/KwH for the first 500KwH and .1808/KwH over 500KwH!

Just out of curiosity, would propane or electricity be cheaper?
 
OP
B

Blk88GT

Well-known member
Joined
Mar 16, 2009
Messages
1,076
Location
Manitoba
I have no idea. Propane heat is not very popular here. We are mainly electric or natural gas.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
We pay .116 kWh on the co-op here and propane is not cost effective enough to warrant a retro fit of our existing resistance heat unit. Our design temps aren't anywhere near Manitoba though, either! We'd be money ahead with a heat pump, but there is no cash for that right now and at 56 I'd be stupid to borrow against any equity. We're all electric, 1600 sq/ft and run just under $200/mth for the entire year average. We'd be in hog heaven to pay only .07/kWh.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,029
Location
Modesto, CA
Why would they disallow a higher amperage service entry? Aren't they in the business of selling power?

The reason higher residential service loads are usually not offered is because amperages over 400a require CTs, a CT meter, and a very large transformer which will cause losses costing the utility revenue. This is just the reason u see underated transformers on the pole. Residential loads will rarely draw enough to balance out the losses of an overrated transformer.
 
Last edited:
OP
B

Blk88GT

Well-known member
Joined
Mar 16, 2009
Messages
1,076
Location
Manitoba
Each lot in my area has a 25KVA transformer dedicated to it, so luckily that's not one of the issues I'm facing.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,029
Location
Modesto, CA
Each lot in my area has a 25KVA transformer dedicated to it, so luckily that's not one of the issues I'm facing.

25Kva? Do u know how much that's rated for? That's good for just over 100a. So I'd say that WILL be an issue and they will be upgrading the transformer. U should ask if u will have to pay for that! Depending on what your calculated continuos load is they'll probably put in a 37.5-50Kva transformer!
 

socapots

Well-known member
Joined
Jan 3, 2011
Messages
544
Location
Canada
Each lot in my area has a 25KVA transformer dedicated to it, so luckily that's not one of the issues I'm facing.

may be mistaken on this.

Like above said that is rated for just about 100amps. Be putting alot on it with an all electric house.

Im in a similar boat as you. I have all electric (its the only service available) and 2100sqft (old drafty house too).
and now i want to build a shop ontop of that. that will need power for a heated slab.
What did you end up doing?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,029
Location
Modesto, CA
And I didn't mention the fact that its not good to put a continuous load on a transformer that's more than 80% of its rated capacity for more than a short period of time. Otherwise, the transformer can start to suffer from saturation, @ which point it will start putting out dirty power!
 
OP
B

Blk88GT

Well-known member
Joined
Mar 16, 2009
Messages
1,076
Location
Manitoba
may be mistaken on this.

Like above said that is rated for just about 100amps. Be putting alot on it with an all electric house.

Im in a similar boat as you. I have all electric (its the only service available) and 2100sqft (old drafty house too).
and now i want to build a shop ontop of that. that will need power for a heated slab.
What did you end up doing?

I had a second 200amp service installed for the shop. So I've got 200 for the shop, 200 for the house, both fed off a 25kva transformer on two separate ~210ft underground runs.

I can't comment on the transformer thing, other than to say I am not interested in a debate. Everything has been designed and OK'd by my power company's sizing engineers and inspectors. I can't imagine they would OK something as bad as you are making it out to be. Let's move on.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,029
Location
Modesto, CA
Maybe the transformer feeding you're services is larger than u think. Are u sure its only 25Kva? Or maybe they upgraded it when u weren't home. Another possibility is your calculated continuous load isn't more than the transformer's rated capacity! You didn't give all the details other than a small transformer.....
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I wouldn't even worry about the transformer. It's not your deal.

Wire the shop up, if you notice power issues, extreme voltage sags, etc that's when you call the power company.
 
OP
B

Blk88GT

Well-known member
Joined
Mar 16, 2009
Messages
1,076
Location
Manitoba
Thanks Aceman, that's exactly my thinking. I was starting to think I wasn't being clear enough. ;)
 

awdblazer

Well-known member
Joined
Oct 17, 2011
Messages
1,100
Location
winnipeg, manitoba, canada
blk88gt i work for the local authority and these guys are right the transformer rating is not your problem
if you overload it, you will blow the primary fuse
so dont worry
 

Higgins

Well-known member
Joined
Dec 25, 2009
Messages
1,936
Location
Shepheardsville, KY
I'm not sure what the problem is upgrading a service feed beyond 200 Amps is. 12 yrs ago, when I built the 2nd garage I wanted to add 100 amps to the garage, there wasn't enough room in the existing panel in the house to do a sub-panel, and the local power co wouldn't allow us to install a larger pedestal for a 400 Amp feed. Se we trenched in conduit and cable to the 2nd garage and had a second meter installed to support the 135 Amp panel. The wiring is large enough to support a 200 Amp panel if we need to upgrade it!

Now the interesting point in all this is, there are several mega-mansions in the area with 400 Amp services. One mansion is so big, they have their own transformer and two electric meters. (don't know what that is about!!!)
 