I'm going to be building a shop next month and will require a 200 amp service.
My current meter is a Thomas-Betts (Microelectric) CO2-200G.
I need to retain the 200amp disconnect on the meter because of the way the service is fed to my panel in the home.
Ideally, I would have a JS4 (dual lug) with a 200 amp disconnect for the house side. Unfortunately, the current meter is cut into some decorative stone on the side of the house.
Is it possible to take the "guts" of another meter and change them out with the existing meter, retaining the cabinet?
I have the Hydro coming out on the 27th for a cable locate but would like to know a little bit before they get here.
Thanks!
My current meter is a Thomas-Betts (Microelectric) CO2-200G.
I need to retain the 200amp disconnect on the meter because of the way the service is fed to my panel in the home.
Ideally, I would have a JS4 (dual lug) with a 200 amp disconnect for the house side. Unfortunately, the current meter is cut into some decorative stone on the side of the house.
Is it possible to take the "guts" of another meter and change them out with the existing meter, retaining the cabinet?
I have the Hydro coming out on the 27th for a cable locate but would like to know a little bit before they get here.
Thanks!

), and most(not all) utilities will require proof of need for the large service.