Allen Bradley 440 to 220 Conversion

To avoid these ads, REGISTER NOW!

A_Pmech

Well-known member
Joined
May 8, 2007
Messages
8,002
Location
IL
You'll need to re-tap the control transformer for 240V input and change the motor lead configuration to the 240V connection.
 

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,117
Location
Amarillo,TX and Stinnett,TX
Could you elaborate please? I'm pretty much an idiot when it comes to electrical. My first post was just repeating what I was told. I can post up a picture if it would help.

Sounds like you need to rewire the control transformer to operate on 240V, also the motor will need to be reconnected to the lower 240V.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,795
This is assuming there is a control transformer. If the OP would post photos it would be helpful.
 
OP
R

Richard D

Well-known member
Joined
Jan 19, 2007
Messages
1,925
Location
Texas City, between Houston and Galveston
AllenBradley01.jpg

I believe the part with #69A288 on it needs to be changed for 220 operation.
AllenBradley02.jpg
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,258
Location
Modesto, CA
Take a pic of the motor nameplate and post here...how many wires are in the motor j box? And the part youre referring to is called a coil which is part of the starter and yes it will need to be swapped out with a 240v coil!

Also, if the motor IS multi-volt, the heaters/overloads will need to be swapped out since your FLC will approx. double because of the supply voltage being halved!

You'll need to re-tap the control transformer for 240V input and change the motor lead configuration to the 240V connection.

Sounds like you need to rewire the control transformer to operate on 240V, also the motor will need to be reconnected to the lower 240V.

Theres no control transformer! Controls operate on 480v....
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,258
Location
Modesto, CA
Unfortunately, thats a 480v only motor. Either get a transformer(expensive unless a good deal can be found) or replace the motor with either a 240v 3 phase motor or ditch the phase converter and buy a single phase motor and youll be set!
 
Last edited:

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
we use Marathon motors alot. Harbor frieght sells motors also. If you can find a "184 frame" it should drop right in. You may have to fab a motor mount. It also appears that it is a two speed motor, 1750 rpm / 850 rpm - that may or may not be important to you. Measure the shaft and get the same horse power. I would go 220v if possible.
 

jerryd68

Well-known member
Joined
May 3, 2013
Messages
274
Location
Idaho
We use Baldor or Leeson motors a lot, I would contact your local motor/pump repair shop and see if they have any used motors. It would make your set up much simpler to eliminate the phase converter and go with the single phase motor, I would recommend 220 also, the higher voltage will reduce the current draw. You will also need to re-do the control circuit.
 