30 amp 220 breaker without a connecting bar?

STINEY

Well-known member
Joined
Jan 23, 2009
Messages
279
Location
Bucyrus Ohio
I saw this picture on another post and I borrowed it for illustration purposes.

See the bottom left twin 30 amp breaker?

We recently bought a HUD house as-is and found a similar breaker in its' box. I assumed that the PO simply removed the connecting bar and used it as 2 - 30s.

But seeing this, I am wondering if these are actually made?

And if so, for what purpose?



null_zps7cd9315a.jpg
 
To avoid these ads, REGISTER NOW!

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
OP
S

STINEY

Well-known member
Joined
Jan 23, 2009
Messages
279
Location
Bucyrus Ohio
The picture may just look that way, but in my instance it is actually a Tandem breaker with no connecting bar.

I assume it is a PO hack-job, but I'm always open to learning something new.
 

djjsr

Well-known member
Joined
Sep 4, 2006
Messages
4,796
Location
In the cornfields
I'm not an electrician, so I have 2 (probably stupid) questions about that photo.

Is it possible that there are two separate circuits that are 30 amp, 120 volts? I think 30 amp circuits are unusual for 120 volts but I've seen receptacles for them so they must exist somewhere.

Is it ok to have that plain unmarked white wire connected to a breaker?
 
Last edited:

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,198
Location
SE MI
We recently bought a HUD house as-is and found a similar breaker in its' box. I assumed that the PO simply removed the connecting bar and used it as 2 - 30s.
It is illegal either way. No connecting bar on a 240V breaker is illegal. White for hot on a 120V circuit is illegal

If the 2 wires coming off are back and white, it is likely a 240V circuit (water heater, stove, dryer). The white wire should be colored red with permanent marker of red tape at BOTH ends !

Most breaker manufacturers make/sell connecting bars which would make it legal.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,029
Location
Modesto, CA
What does this circuit feed? Are the breakers riveted together or are they 2 individual breakers? What is the m/n of the breaker?

If this (or these) breakers are feeding a 240v circuit and theyre 2 individual breakers, then they should be swapped for a common trip breaker!

If instead the circuit is a MWBC, then it needs a handle tie to be code compliant.

And just for sh*ts and giggles, that panel is NOT code complaint as it has different brands of breakers.
 
Last edited:
To avoid these ads, REGISTER NOW!

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
Is that a 20A GFCI breaker in the panel and is it missing a black wire out to a circuit? All I see is the coiled white wire to the bus bar, and as I'm surely NOT an expert and I've never used such a thing, I'm assuming that MIGHT be OK???
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
Is that a 20A GFCI breaker in the panel and is it missing a black wire out to a circuit? All I see is the coiled white wire to the bus bar, and as I'm surely NOT an expert and I've never used such a thing, I'm assuming that MIGHT be OK???

Or AFCI, not familiar with GEs. Either way it is not in use as it has nothing attached to it :)

Also looks like the wire is awful small for a 30 amp circuit. Should be #10 I think. Looks like the same size as the one on the 20 Amp GFCI

Depends on the load too, for example an AC might require only #12 with a 30-amp breaker.
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,329
Location
Beautiful Southern Maryland
stiney,
I just read your original post again and realized that we are not looking at your actual panel but a picture of a similar one. How about a picture of your panel ?? The only way you will know for certain is to turn the breaker off and see what happens ?? I think they make tie bars for certain brands of breakers, but if it is indeed a 220 circuit then I would probably replace it with a true 2 pole breaker.
 
OP
S

STINEY

Well-known member
Joined
Jan 23, 2009
Messages
279
Location
Bucyrus Ohio
I am not questioning what the circuits are.

Was just curious if there were tandem (riveted) 30 amp breakers manufactured with no tie bar, or if the PO removed the tie bar.

I have a couple of extra tie bars from some bad breakers, I'm just going to tie this one together and use it for a water heater circuit.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Eaton doesn't have a tandem 30A breaker like that. Those in the picture are two full size breakers and if they are riveted together then it's a double pole that is missing the handle tie.

I am not questioning what the circuits are.

Was just curious if there were tandem (riveted) 30 amp breakers manufactured with no tie bar, or if the PO removed the tie bar.

I have a couple of extra tie bars from some bad breakers, I'm just going to tie this one together and use it for a water heater circuit.
 