I have a compressor I'm going to wire up within the next week or two. I just want to make sure I understand the wiring concept. I've wired my garage with your standard outlets, so I think I'm going in the right direction.
So the compressor motor is a USA made Century from back in the 80's. I think the tank was stamped 1983. The motor is rated at 3hp, 15 amps, and 230 volts continuous. The plug is NEMA 6-20P. I'll have to buy the 6-20R outlet.
Will a 20a double pole breaker and 12-2 wire be sufficient for this compressor? The main thing I'm worried about is the start up, but do I really need to bump up to 30a breaker and 10-2 wire? The run on wire will be less than 10 feet total.
I've done a lot of reading to cover my bases, so I hope I'm on the right track.