Yeah, I know I sound a little over cautious. It comes from having a "Type A" personality & over 30 years of HVAC/Facilities Maintenance Management. You should have seen how much of a meticulous zealot I was when I was the crew chief for our race car.
I'm completely on board with the idea of giving the compressor a second life. I absolutely love getting old things back into operating condition, even if I don't completely restore them. I just really like the way things were made back then. Heck, my lawn sprinkler is a 60's Craftsman tractor style traveling sprinkler I rescued from a garbage can at a swap meet. I use it all summer.
Also, I realize you aren't doing anything that is electrically unsafe, but just FYI, by code the breaker is not allowed to be used as a disconnect. There has to be a manually operated switch other than the breaker.
Tommy
I really thought you could. It does list it in the NEC and it is within line of sight and less then 50 feet.
The disconnecting means for the motor controller and/or the motor must be a [430.109(A)]:
A listed horsepower-rated motor-circuit switch.
A listed molded-case circuit breaker.
A listed molded-case switch.
Listed manual motor controllers marked “Suitable as Motor Disconnect.”