Something to consider when running a load calculation.

Mike007

Well-known member
Joined
Dec 4, 2010
Messages
2,617
When I sized the heater for my garage I sized it based on my years of HVAC experience. I installed a 20K net BTU heater. During the recent cold snap I was able to see the ultimate performance. It was 7* out and it ran continuously to maintain 62* inside.

I just got around to filing a permit. The building department wanted a manual J. Out of curiosity I punched the design conditions in 62* inside temp with a 7* outside temp. Since I insulated and finished the garage, I knew all the other variables were accurate. The program spit out a heat loss of 81,000 BTU's under those conditions. :headscrat Obviously 80K would be a major oversize.

When I looked at where the BTU's were going, the program has 60,500 BTU loss for the 2 garage doors. I called the company who puts out the program. The guy I spoke with was aware of this and told me any program based on Manual J (most are) will spit out ridiculous numbers for insulated garage doors. He suggests putting insulated garage doors in the program as a wall.

So if you are running a manual J you may want to take a look at what the heat loss for the doors looks like.
 
Last edited:
To avoid these ads, REGISTER NOW!

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
When I sized the heater for my garage I sized it based on my years of HVAC experience. I installed a 20K net BTU heater. During the recent cold snap I was able to see the ultimate performance. It was 7* out and it ran continuously to maintain 62* inside.

I just got around to filing a permit. The building department wanted a manual J. Out of curiosity I punched the design conditions in 62* inside temp with a 7* outside temp. Since I insulated and finished the garage, I knew all the other variables were accurate. The program spit out a heat loss of 81,000 BTU's under those conditions. :headscrat Obviously 80K would be a major oversize.

When I looked at where the BTU's were going, the program has 60,500 BTU loss for the 2 garage doors. I called the company who puts out the program. The guy I spoke with was aware of this and told me any program based on Manual J (most are) will spit out ridiculous numbers for insulated garage doors. He suggests putting insulated garage doors in the program as a wall.

So if you are running a manual J you may want to take a look at what the heat loss for the doors looks like.

I quit using J a long time ago.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
What software program?

Got specs on the garage? I'll punch it in mine and see what it comes up with.
 
To avoid these ads, REGISTER NOW!

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,411
Location
N CA
Manual J also builds in an 18% adder for duct leakage. Worth considering when you use something that is "net to the space".
 

meathooker

Well-known member
Joined
Dec 10, 2013
Messages
254
Location
Iowa
Op, what program are you using?


In idaho some cities are requiring manual J on all jobs. Such a waste on a lot of projects. As a member or ASHRAE I'm annoyed at all things acca.
 
OP
M

Mike007

Well-known member
Joined
Dec 4, 2010
Messages
2,617
What software program?

Got specs on the garage? I'll punch it in mine and see what it comes up with.

Good idea. It doesn't need to be exact, just punch in four 24' walls, a ceiling, floor, and two 8 x 8 insulated garge doors. Same conditions I used, 7* out 62* in and post what the door heat loss comes up as. Thanks.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
My program doesn't have a specific entry for garage doors that I know of, it gives a choice of door materiel and construction so I used metal with polystyrene core.

24x24 with 9' ceilings with average construction( I used a building from my file and just adjusted size slightly), two 8x8 doors and 1 3x7 man door and I came up with 19k and change.

I simply removed the doors so it made them wall and it dropped about 2000 btu.

This is with Elite Rhvac.
 