When I sized the heater for my garage I sized it based on my years of HVAC experience. I installed a 20K net BTU heater. During the recent cold snap I was able to see the ultimate performance. It was 7* out and it ran continuously to maintain 62* inside.
I just got around to filing a permit. The building department wanted a manual J. Out of curiosity I punched the design conditions in 62* inside temp with a 7* outside temp. Since I insulated and finished the garage, I knew all the other variables were accurate. The program spit out a heat loss of 81,000 BTU's under those conditions.
Obviously 80K would be a major oversize.
When I looked at where the BTU's were going, the program has 60,500 BTU loss for the 2 garage doors. I called the company who puts out the program. The guy I spoke with was aware of this and told me any program based on Manual J (most are) will spit out ridiculous numbers for insulated garage doors. He suggests putting insulated garage doors in the program as a wall.
So if you are running a manual J you may want to take a look at what the heat loss for the doors looks like.
I just got around to filing a permit. The building department wanted a manual J. Out of curiosity I punched the design conditions in 62* inside temp with a 7* outside temp. Since I insulated and finished the garage, I knew all the other variables were accurate. The program spit out a heat loss of 81,000 BTU's under those conditions.
Obviously 80K would be a major oversize.When I looked at where the BTU's were going, the program has 60,500 BTU loss for the 2 garage doors. I called the company who puts out the program. The guy I spoke with was aware of this and told me any program based on Manual J (most are) will spit out ridiculous numbers for insulated garage doors. He suggests putting insulated garage doors in the program as a wall.
So if you are running a manual J you may want to take a look at what the heat loss for the doors looks like.