I am in the early stages of having a house built in a new subdivision. Long story short I got the builder to price my two outlets of 240 volts 60 amps each with disconnects. One is for my Air compressor which draws about 25 amps.
First, there was just recently a major knock-down, drag-out thread regarding the PROPER sizing of branch circuits feeding compressor loads (
http://www.garagejournal.com/forum/showthread.php?t=232403). I suggest you carefully review that before carving anything into granite. The upshot is, the circuit needs to be sized based on the nominal HORSEPOWER of the motor driving the compressor; and because of this it may well need to be rated for more than the nominal 25 Amps you figure your compressor draws.
I want another outlet for a future tig/stick welder. Something like the Miller Syncrowave 210. They plan on using #4 aluminium wire and the house will have a 200 amp service.
Personally, I'm not a fan of aluminum wiring for this sort of application. Yes, I've heard all the claims about how "today's" AL wiring is not the same stuff that became notorious for burning down houses 30-50 years ago; but still.
Further, it simply isn't necessary in this case. Worse-case, if your compressor has a 5HP motor, you'll need some 8-2 NM-B or AWG 10 THHN (if run in conduit); neither of these is so expensive (
well under $1.00/foot even at retail) as to reasonably drive you to AL wire for cost reasons.
The welder is even easier. According to the spec sheet for the model you cited, it draws less than 12A @ 240V when running at rated output. Dedicated welder circuits are (at least sometimes) allowed to use undersized wire, due to the presumed low duty cycle; but even if we were to ignore that (which may be a good idea for other reasons), AND presume a 20A circuit, that would still only need 12-2 NM-B (w/g), which is more like half a buck per foot. (That said, I might be tempted to upsize this a bit, in case you change your mind about what welder to buy.)
my question is what is the best way to do this? Two separate outlets or a sub panel?
I gather that this is an ATTACHED garage. If so, you can legally do without the sub-panel.
BUT... Given that you're already planning on a "substantial" compressor AND a welder, the odds are overwhelming that you WILL also want a considerable amount of other "stuff" in that garage by the time your done. So I would HIGHLY recommend the sub-panel, as opposed to individual branch circuits run from the home's main service panel. This not only makes for the "better" (neater, simpler, more efficient) installation, it helps keep your options open for the future.
One feed to the garage with a 6 space sub panel. Have them use #2 AL and a 90A breaker in the main. It might even be cheaper because you won't need the disconnects.
I would go with a MUCH larger panel than this. He'll use four of those six "slots" just for the compressor and the welder. That doesn't leave much (read: "enough", in my book anyway) left over for general-purpose 120V outlet circuits, lighting circuits, GDO circuits, dedicated circuits for other power tools & equipment, etc. Something like this:
http://www.homedepot.com/p/Square-D...ver-QO120M100C/100195842?N=5yc1vZbm2wZ1z0x9jp
is certainly inexpensive enough to be considered a "no brainer", in the context of a whole new home build.
The #2 AL (or #3 CU) feeder cable and a 90-100A (depending) breaker is near-certainly fine.
If the garage is going to be drywalled by the builder, do NOT have a flush mount box installed. With a surface mount box, you will have to use conduit for branch circuits, but plastic conduit is easy to install.
I am somewhat of two minds on this. Yes, a surface-mount box would make it easier to run conduit in the future. But personally, I just don't like that "look"; and the OP may not either. I'd rather repair/re-do drywall ONCE than put up with the "cluttered" look and dust-catcher aspects of surface mount conduit forever more.
I emailed the builder for a price on upgrading to a 300 amp service. Either way I will have a sub panel installed and I will just have them put in one 50 amp outlet in for my compressor and if i get a welder i can add a circuit later on.
First, forget that so-called "50 amp outlet" for the compressor. Any compressor larger than 3 HP (which can be served nicely, with capacity to spare, from a 30A circuit) will REQUIRE hardwiring. There are NO affordable plugs/receptacles which are rated for more than 3HP/single-phase.
Second, given the way you seem to be floundering around on this (no doubt exacerbated by relaying all the conversations through the builder, to his electrical sub, and then back again -- think "Whisper Down The Lane"), you might well be better off having the builder install a suitable sub-panel (which meets your specs in terms of capacity, slot count, feeder cable, etc.) and ONE 120V "test" outlet immediately adjacent, and let it go at that. Then plan out EVERYTHING you're going to want in that garage in terms of electrical circuits and such, and hire your own guy to install it.
No need to upgrade the main panel, even with a 90A feed to the garage,
Probably right, unless the "normal" house loads are already pushing the limits of that 200A service, which it probably isn't.